Capacitor to be connected to increase power factor

Click For Summary
SUMMARY

The discussion focuses on calculating the required capacitance to improve the power factor of an RL circuit connected to a 240V, 50Hz supply. The initial calculations led to an incorrect capacitance value of 28.4uF, as the user misapplied the formula for current using apparent power instead of real power. The correct approach involves calculating the impedance and using the relationship between reactance and capacitance to achieve a unity power factor, emphasizing that power factor correction (PFC) is typically done with parallel capacitors rather than series configurations.

PREREQUISITES
  • Understanding of RL circuit behavior and power factor concepts
  • Familiarity with impedance calculations in AC circuits
  • Knowledge of reactance and its relationship to capacitance
  • Proficiency in using formulas such as P=VI and XC=1/2πfC
NEXT STEPS
  • Study the calculation of impedance in RL circuits
  • Learn about the differences between series and parallel power factor correction
  • Explore the implications of power factor correction on circuit performance
  • Investigate the effects of reactive components on total power in AC circuits
USEFUL FOR

Electrical engineers, students studying circuit theory, and professionals involved in power factor correction and AC circuit design will benefit from this discussion.

Nax13
Messages
4
Reaction score
0
A resistance 'R' ohm and inductance of 'L' henry are connected across 240V, 50Hz supply. Power distributed in the circuit is 300W, and the voltage across R is 100V. In order to improve the power factor to unity, the capacitor to be connected in series should have a value of __.
a) 43.7 uF b) 4.37 uF c) 437 uF d) 0.437 uF

Step 1) Using P=V/I, got I=1.25A
Step 2) Using R=VR/I, got R=80 ohm
Step 3) Now since total voltage is 240V, VL is 240-100=140V
Step 4) Using XL=VL/I, got XL=112 ohm.
Step 5) For power factor to be unity, XL=XC, which means that XC should also be equal to 112 ohm, which leads me to the answer that C is 28.4uF. (since XC=1/2πfC)

Where did I go wrong? Any help would be appreciated. :wink:
 
Last edited:
Physics news on Phys.org
Where did I go wrong?

First line (ignoring the typo. P=V/I), you used P=VI to find I. This is incorrect, VI is the apparent power if you use the total voltage. If however you just use the voltage across the resistor ...
 
BTW. It is a poor exercise to refer to this a merely "power factor correction". Series resonating out a reactive element like this does a lot more than merely correcting power factor. In this case for example it increases the total power by a multiple of about 6. If the load was designed to run at 300W then it would likely be destroyed.

This is why PFC is normally done with a parallel capacitor.
 
Why is it necessary to calculate the impedance?
Btw, are all my other steps right?
 
Nax13 said:
Why is it necessary to calculate the impedance?

Because you want to find the reactance "X". So find the resistance "R", find the impedance magnitude |Z| and use R^2 + X^2 = |Z|^2 to solve for X.
 
Thanks for your help, uart and tim! :)
 

Similar threads

  • · Replies 9 ·
Replies
9
Views
2K
  • · Replies 20 ·
Replies
20
Views
5K
Replies
1
Views
2K
Replies
2
Views
4K
  • · Replies 3 ·
Replies
3
Views
3K
  • · Replies 3 ·
Replies
3
Views
14K
  • · Replies 4 ·
Replies
4
Views
2K
Replies
2
Views
3K
  • · Replies 2 ·
Replies
2
Views
9K
  • · Replies 7 ·
Replies
7
Views
8K