Cooling systems in thermal power stations

  • Thread starter Thread starter Gruxg
  • Start date Start date
  • Tags Tags
    Steam turbine
AI Thread Summary
Thermal power stations generally require effective cooling systems, often situated near large water sources or equipped with cooling towers. Concentrated solar power (CSP) stations, however, utilize smaller dry cooling systems due to their typical locations in arid regions with limited water resources. These systems are less efficient than traditional wet cooling but are sufficient for the lower capacity of CSP plants. Additionally, the design of CSP plants often incorporates forced ventilation, making large cooling towers unnecessary. Overall, CSP plants adapt their cooling methods to environmental constraints while still meeting operational needs.
Gruxg
Messages
43
Reaction score
2
I thought any type of thermal power sation required a powerful cooling system and therefore had to be located near a large water mass (river, sea) or have big cooling towers: I have seen this in nuclear, gas or biomass stations. However, I haven't seen it in concentrated solar power stations despite they use steam turbines like any other termal station (if I am not mistaken). Once the heat is produced by any means, I suppose the thermodynamics should not be very different: why (thermal) solar stations do not need such big cooling towers nor large water supply like the other stations?
 
Engineering news on Phys.org
second link said:
Normally, steam engine power plants utilize the water-intensive wet cooling technique to disperse the waste heat that has been generated. But such processes have the ability to lose huge amounts of water as a result of the evaporation and, thus demand a constant water supply.

This poses a severe threat as the majority of the CSP plants are set up in hot and dry regions with restricted water resources.

I don't think I say "severe threat," rather, "design constraint."
 
  • Like
Likes russ_watters
Gruxg said:
I thought any type of thermal power sation required a powerful cooling system and therefore had to be located near a large water mass (river, sea) or have big cooling towers:
You are right, they do need cooling the same way as any other thermal power station.

Gruxg said:
why (thermal) solar stations do not need such big cooling towers

As far as I know there are multiple reasons.
- since there is usually no water nearby at all, they prefer dry towers with forced ventilation. And those are lot smaller.
- usually these CSP stations are at lower capacity than those big power plants => less cooling is needed.
- the sheer size of the plant is lot bigger, and cooling is just harder to notice.
- also, those iconic natural draft towers are associated with 'bad power', so if it's just matter of choice then it'll be something else.

'Bookport CSP plant' is 50MW and all the cooling it needs is that three shaft white-ish block with the green piping on the right side of the block of machinery. The perspective is tricky that thing is still big from up close.
-parabolic-trough-collector-technology-%C2%AESENER.jpg


You can find some more here, for example.
1736235067296.png
 
  • Like
  • Informative
Likes Gruxg, gmax137, jack action and 1 other person
Dry coolers are fine, they just have lower performance/efficiency than evaporative coolers if you have water available and have a choice. Evaporative towers approach the wet bulb temperature whereas dry towers approach the dry bulb. For my area that means a wet tower provides 85F condenser water on a on 98F day (78F wet bulb) vs 105F condenser water for a dry cooler.

Other considerations:
-Wet towers are air cleaners. All the dirt/dust in the air flowing through the tower ends up in the water.
-For cold water/ambient operation, you may need anti-freeze and that dictates a dry tower.
-Legionella. Not a concern in a dry cooler.
 
  • Like
  • Informative
Likes harborsparrow, Gruxg and berkeman
Hi all, I have a question. So from the derivation of the Isentropic process relationship PV^gamma = constant, there is a step dW = PdV, which can only be said for quasi-equilibrium (or reversible) processes. As such I believe PV^gamma = constant (and the family of equations) should not be applicable to just adiabatic processes? Ie, it should be applicable only for adiabatic + reversible = isentropic processes? However, I've seen couple of online notes/books, and...
Thread 'How can I find the cleanout for my building drain?'
I am a long distance truck driver, but I recently completed a plumbing program with Stratford Career Institute. In the chapter of my textbook Repairing DWV Systems, the author says that if there is a clog in the building drain, one can clear out the clog by using a snake augur or maybe some other type of tool into the cleanout for the building drain. The author said that the cleanout for the building drain is usually near the stack. I live in a duplex townhouse. Just out of curiosity, I...
I have an engine that uses a dry sump oiling system. The oil collection pan has three AN fittings to use for scavenging. Two of the fittings are approximately on the same level, the third is about 1/2 to 3/4 inch higher than the other two. The system ran for years with no problem using a three stage pump (one pressure and two scavenge stages). The two scavenge stages were connected at times to any two of the three AN fittings on the tank. Recently I tried an upgrade to a four stage pump...
Back
Top