COP in vapor compression refrigeration analysis

Click For Summary
SUMMARY

The discussion centers on the operation of heat pump compressors within vapor compression refrigeration cycles, specifically addressing the coefficient of performance (COP) calculations under varying outdoor temperatures. It is established that the compressor operates with a fixed compression ratio but does not maintain a fixed pressure; instead, pressure varies with outdoor temperature changes. The COP decreases when outdoor temperatures rise, complicating calculations that involve the saturation states of fluids. Participants suggest using the Carnot efficiency equation and t-s diagrams for accurate analysis.

PREREQUISITES
  • Understanding of vapor compression refrigeration cycles
  • Knowledge of heat pump operation and thermodynamic principles
  • Familiarity with the Carnot efficiency equation
  • Ability to interpret t-s diagrams for thermodynamic cycles
NEXT STEPS
  • Research the calculation of COP in vapor compression refrigeration systems
  • Study the effects of outdoor temperature variations on heat pump performance
  • Learn to plot and analyze t-s diagrams for refrigeration cycles
  • Investigate typical COP values for vapor compression and absorption chillers
USEFUL FOR

Engineers, HVAC professionals, and students studying thermodynamics or refrigeration systems will benefit from this discussion, particularly those focused on optimizing heat pump performance and understanding COP calculations.

bearcharge
Messages
26
Reaction score
0
Hi, has anybody worked with heat pumps? I'm recently confused about how the heat pump compressor operates. Does it have a fixed pressure or it actually adjust its pressure automatically to outdoor temperature variation? All my confusion originate from the following problem:

Now we have a heat pump that employs vapor compression refrigeration cycle for cooling. Suppose indoor temperature is 55 F(12.7 C) and outdoor temperature is 95 F(35 C), try to determine the parameters that compressor should be operating so that COP of 6 can be achieved. Then use the determined parameters to calculate COP when outdoor temperature is raised to 105 F and indoor temperature stays the same. For the sake of simplicity, assume saturated fluid in the condenser and saturated vapor in the entrance of compressor.

Any suggestion will be much appreciated. Thanks.
 
Science news on Phys.org
A heat pump compressor is fixed compression ratio, but not fixed pressure. If the temperature outside drops (in heating mode), the pressure in the entire system will drop...and the COP will drop. Similarly, if the temperature outside rises when in cooling mode, the COP will drop.
 
thanks for the reply! so in the cooling mode, when the outdoor temperature is raised, the compression ratio stays the same, but the system pressure drops or rises? and can we calculate this pressure drop or rise based on the assumption of saturation liquid and saturation vapor? and from that we calculate the COP in this case? Thanks.
russ_watters said:
A heat pump compressor is fixed compression ratio, but not fixed pressure. If the temperature outside drops (in heating mode), the pressure in the entire system will drop...and the COP will drop. Similarly, if the temperature outside rises when in cooling mode, the COP will drop.
 
In air conditioning mode, if the temperature outside rises, the pressure rises.

Well...it depends on what other information you are given and how you are expected to use it. You can probably plot the cycle on a t-s diagram and work from there. Or maybe they just want you to use the carnot efficiency equation? Part of the difficulty in a calculation, though, is the CoP drop is related to the difficulty with dissipating heat at the heat exchanger when the temperature outside rises.
 
Thank you very much, Russ Watters! you've been very helpful.
Is it appropriate to assume this pressure is a function of temperature, considering it's saturated at the entrance of the condenser, and this pressure is equal to the pressure at the exit of the compressor? then by using the equation
COP = \frac{h_1-h_4}{h_2-h_1},
where 1:entrance of compressor
2:exit of compressor
3:entrance of condenser
4:exit of condenser
but it seems that even with the pressure calculated, we still need to know the temperature at point 2 to determin h2. Can I just assume a temperature at point 2?
by the way, I tried to use carnot cycle efficiency for calculation, but this method was denied...

russ_watters said:
In air conditioning mode, if the temperature outside rises, the pressure rises.

Well...it depends on what other information you are given and how you are expected to use it. You can probably plot the cycle on a t-s diagram and work from there. Or maybe they just want you to use the carnot efficiency equation? Part of the difficulty in a calculation, though, is the CoP drop is related to the difficulty with dissipating heat at the heat exchanger when the temperature outside rises.
 
What are the typical cop of vapor compression chiller and absorption chiller
 

Similar threads

  • · Replies 10 ·
Replies
10
Views
3K
  • · Replies 20 ·
Replies
20
Views
2K
Replies
1
Views
791
  • · Replies 8 ·
Replies
8
Views
5K
  • · Replies 3 ·
Replies
3
Views
5K
  • · Replies 23 ·
Replies
23
Views
4K
  • · Replies 6 ·
Replies
6
Views
7K
Replies
3
Views
3K
  • · Replies 13 ·
Replies
13
Views
4K
  • · Replies 6 ·
Replies
6
Views
4K