Correcting power factor without affecting active power.......

Click For Summary
SUMMARY

Correcting power factor (PF) without affecting active power involves adjusting reactive power through the addition of capacitance or inductance, which indirectly changes the phase angle. The active power remains constant while the current magnitude adjusts to maintain the relationship defined by the equation Active Power = Vrms * Irms * cos(theta). In practical applications, such as PC power supplies, power factor correction (PFC) reduces the current drawn from 2.5A to 2A while keeping the active power at 460W, effectively modifying the power factor from 0.8 to 1. Modern PFC in PC power supplies utilizes electronic methods rather than traditional transformers or passive components.

PREREQUISITES
  • Understanding of AC power concepts, including active and reactive power
  • Familiarity with power factor and its implications in electrical systems
  • Knowledge of the relationship between voltage, current, and phase angle in AC circuits
  • Basic principles of power factor correction techniques
NEXT STEPS
  • Study the principles of power factor correction in detail
  • Learn about the operation and design of electronic power factor correction circuits
  • Explore the impact of reactive power on electrical systems and efficiency
  • Investigate the differences between passive and active power factor correction methods
USEFUL FOR

Electrical engineers, power system designers, and anyone involved in optimizing power factor in electrical systems, particularly in consumer electronics like PC power supplies.

Voltageisntreal
Messages
18
Reaction score
5
When correcting power factor without affecting active power, wouldn't the current and voltage of the system have to change due to

Active power =VrmsIrmscos(theta), where cos(theta) is the power factor?
 
Engineering news on Phys.org
Most cases the voltage can be considered as given, so what changes is the current.
 
  • Like
Likes Voltageisntreal
  • Like
Likes Voltageisntreal
anorlunda said:
@Rive is right considering voltage magnitude, but the phase angle might change.

@Voltageisntreal , welcome to PF.

You might understand better after reading these two PF Insights articles.
https://www.physicsforums.com/insights/ac-power-analysis-part-1-basics/
https://www.physicsforums.com/insights/ac-power-analysis-part-2-network-analysis/

Hello to you too and thanks :D.

I'm not sure if I understand better now or not :p.

Steinmetz said, if I percieve correctly from the article, that z=A+jB, where jB is the phase shift. I've always just seen imaginary power as a phase shift between voltage and current in AC, where j is 90 degrees. Essentially, voltage is applied and then electromagnetic energy lags or leads it depending on whether the imaginary power is positive or negative which comes down to how capacitors and inductors act in AC.

My issue was that with a transformer in which I want to correct the power factor , but I want to keep active power the same, then you change reactive/imaginary power to get the result- yes. You do that by changing the phase angle indirectly by adding a capacitance or inductance.

I thought then, however, would that not result in a change in the current (as Rive said) in terms of it's magnitude to balance the formula: VIcos(theta)= Active Power?

I now feel, from the article, that because of this shift due to the change in reactive power-- V and I do change at instantaneous points because of the shift--- however, the rms remains the same and the average active power is therefore the same?

If so that does make more sense and thank you for you help :).
 
Let's take a simple example. If the PSU in your PC draws 460W, that would mean 2A at 230V.
Of course, PC power supplies has power factor correction these days. Without correction that PSU would draw 575VA (not W, but VA!), in case the power factor // cos(theta) is 0.8.
Since the voltage is the same 230V, it would mean 2.5A current.

So, we can say that in this case the PFC reduced the current to 2A from 2.5A, with the effective power remaining 460W. The very meaning of the PFC is that you modify the cos(theta) from 0.8 to 1 (so theta will change).

PS.: In PC PSUs the correction is done with electronics these days, not with transformers or simple additional inductive/capacitive elements.
 
  • Like
Likes Voltageisntreal
Rive said:
Let's take a simple example. If the PSU in your PC draws 460W, that would mean 2A at 230V.
Of course, PC power supplies has power factor correction these days. Without correction that PSU would draw 575VA (not W, but VA!), in case the power factor // cos(theta) is 0.8.
Since the voltage is the same 230V, it would mean 2.5A current.

So, we can say that in this case the PFC reduced the current to 2A from 2.5A, with the effective power remaining 460W. The very meaning of the PFC is that you modify the cos(theta) from 0.8 to 1 (so theta will change).

PS.: In PC PSUs the correction is done with electronics these days, not with transformers or simple additional inductive/capacitive elements.

I see, I had gotten confused :o! Tyvm :3 :D, I understand now. It does reduce the current, which it would have to because rms is average anyway so the shift wouldn't have affected it.<3.
 
Most likely this can only be answered by an "old timer". I am making measurements on an uA709 op amp (metal can). I would like to calculate the frequency rolloff curves (I can measure them). I assume the compensation is via the miller effect. To do the calculations I would need to know the gain of the transistors and the effective resistance seen at the compensation terminals, not including the values I put there. Anyone know those values?

Similar threads

  • · Replies 2 ·
Replies
2
Views
1K
  • · Replies 8 ·
Replies
8
Views
2K
  • · Replies 6 ·
Replies
6
Views
2K
  • · Replies 10 ·
Replies
10
Views
2K
  • · Replies 8 ·
Replies
8
Views
3K
Replies
2
Views
984
Replies
12
Views
3K
  • · Replies 4 ·
Replies
4
Views
1K
Replies
11
Views
2K
  • · Replies 7 ·
Replies
7
Views
6K