DC Distribution System -- Minimum Voltage across the line

5 replies · 1K views · last reply
jaus tail
Messages
613
Reaction score
48

Homework Statement


Diagram of a DC distribution line fed at 220 V, with branch loads of 10, 20 and 50 amperes at successive junctions and conductor resistances of 0.1, 0.08 and 0.06 ohms per segment.


Homework Equations


V = IR
And R becomes 2(r of one conductor) because of return path.

The Attempt at a Solution


V minimum is at third junction. At VD
Using KVL we get:
Single-line diagram of a DC distribution feeder with nodes A to D, segment resistances 0.1, 0.08 and 0.06, loads 10, 20 and 50 tapped off, and source Vsc = 220V at A.
[/B]
Drop at AB = (10 + 20 + 50) * 2 * 0.1 = 16 V
Drop at BC = (20 + 50) * 2 * 0.08 = 11.2
Drop at CD = (50)*(2 * 0.06) = 6
Total Drop = 33.2 V
VD = 220 - 33.2 = 186.8V
Why have they not included the 2 factor in their calculation?
In solved examples they have used factor of 2.

Textbook page: Example 13.1 on a 2-wire d.c. distributor AB with tapped currents, and the solution's resistance and current calculations for sections AC, CD, DE and EB.

Aren't all dc distribution 2 wire as the return path cannot be ground for DC? So shouldn't the factor of 2 be there in the equation?
 
Attachments
  • Diagram of a DC distribution line fed at 220 V, with branch loads of 10, 20 and 50 amperes at successive junctions and conductor resistances of 0.1, 0.08 and 0.06 ohms per segment.
    upload_2018-1-28_9-47-36.png
    11.4 KB · Views: 873
  • Single-line diagram of a DC distribution feeder with nodes A to D, segment resistances 0.1, 0.08 and 0.06, loads 10, 20 and 50 tapped off, and source Vsc = 220V at A.
    upload_2018-1-28_9-49-46.png
    2.7 KB · Views: 424
  • Textbook page: Example 13.1 on a 2-wire d.c. distributor AB with tapped currents, and the solution's resistance and current calculations for sections AC, CD, DE and EB.
    upload_2018-1-28_9-58-51.png
    65.1 KB · Views: 437
jaus tail said:
So shouldn't the factor of 2 be there in the equation?
No. You should be concerned with only point D here. Out of the four load points, D has the minimum voltage.
 
But in solved example they have used factor of 2
Should I use factor of 2 if they say 2-wire dc system and not use factor of 2 if they don't mention 2 wire dc system?
 
jaus tail said:
But in solved example they have used factor of 2
Should I use factor of 2 if they say 2-wire dc system and not use factor of 2 if they don't mention 2 wire dc system?
It is also possible that they have added the return path's resistance in the forward path's resistance (since they are in series) and have replaced the return path with an ideal wire.

Even if you consider the return wire's resistance here, it will not affect the voltages at given points A, B, C and D since the currents of the loads are given.
 
The currents are given in solved example also and still they've included the factor of 2. I've marked it red in the picture. Is there some reason when to use 2 and when to not use 2?
 
jaus tail said:
The currents are given in solved example also and still they've included the factor of 2. I've marked it red in the picture. Is there some reason when to use 2 and when to not use 2?
When you have to compute the resistances of individual conductor segments, you need to use the factor of 2 since you need to calculate the resistance of the entire two-wire system first. Here, you have already been given the resistances of the segments of one conductor and you are asked to find the potentials at the tapping points on that conductor. So you need not worry about the return conductor here.

You should consider the voltage drop in the return conducor if they are asking for 'load voltage'. Here, it seems they are asking for 'potential at point D', which is not same as the load voltage at D if you include the resistance of the return conductor.
 
  • Like
Likes   Reactions: jaus tail