Delta-Delta 3 phase transformer HNC help

Join the discussion
Ask a follow-up here, or get your own question answered by working scientists, mathematicians and engineers — people, not an autocomplete.
Real named experts · corrections over time · the nuance an AI answer skips
8 replies · 3K views
craig clarke
Messages
4
Reaction score
0
<< Thread moved from the technical engineering forums to HH >>[/color]

I'm currently studying for a HNC in electrical engineering and am currently stuck on a question on one of my assignments. The question is:

A Delta-delta, 3 phase transformer steps down the system line voltage of 132kV to a local power distribution level of 11kV. The total connected load is 21 MW at 0.86 pf lagging. Calculate:

a) The apparent power taken by the load
b) The current in the HV lines
c) The current in the LV lines
d) The currents in the primary and secondary windings of the transformer
e) The load carried by each phase winding of the transformer

a) Apparent power = 21MW/cos(0.86 = 32MW

b) Current in HV line = 32MW/√3x132kV = 139.9A
c) Current in the LV line = 32MW/√3x11kV = 1679.5A
d) Current in primary winding = Primary current/√3 = 80.25A
Current in secondary winding = Secondary current/ √3 = 969A

Could someone please check these answers for me and I'm not sure how to calculate the load carried by each phase winding but am I correct in thinking that each winding have the same answer?
 
Last edited by a moderator:
on Phys.org
Delta-Delta 3 phase transformer HNC help

Hi craig clarke. http://img96.imageshack.us/img96/5725/red5e5etimes5e5e45e5e25.gif

If you'd like some answers checked then you need to include your working. That's the requirement when seeking homework help at Physics Forms. Otherwise, helpers would have to work the problem themselves in its entirety.

Where the load is balanced, phase currents and voltages are all identical.
 
Last edited by a moderator:
  • Like
Likes   Reactions: craig clarke
I have included my calculations and answers of a,b,c and d I'm stuck on quest e. I'm not sure on what formula to use. I want to know what formula to use for calculating the load carried by each phase winding and if I've answered the other questions correctly.

Thanks
 
craig clarke said:
a) Apparent power = 21MW/cos(0.86 = 32MW
Isn't 0.86 already cos(Φ)? Why take the cos of a cos?
 
PF=cos(φ

where φ is the phase angle between the voltage and current, the power factor is 0.86 lagging, so φ=0.86

The PF is the cosine of the phase angle which is 0.86?
 
NascentOxygen said:
In (e) the intended answer might be kVA.

Will the equation for this calculation be

Has it is a delta transformer and will be balanced?

kilovolt-amps = 3 × amps × volts / 1000
 
craig clarke said:
PF=cos(φ

where φ is the phase angle between the voltage and current, the power factor is 0.86 lagging, so φ=0.86

The PF is the cosine of the phase angle which is 0.86?
The power factor is indeed the cosine of the phase angle. Here it's given to you as PF = 0.86. So 0.86 = cos(φ).
That would make φ = cos-1(0.86). Or if you prefer, φ = arccos(0.86).
 
  • Like
Likes   Reactions: craig clarke