Design pressure & max working pressure

Click For Summary
SUMMARY

The discussion clarifies the distinction between Maximum Allowable Working Pressure (MAWP) and Design Pressure in boiler design, emphasizing adherence to ASME Boiler and Pressure Vessel Codes. MAWP is defined as the maximum pressure permissible at the top of the vessel under specified conditions, while Design Pressure represents the most severe expected operational conditions. Relief devices must be set at or below the MAWP, typically 10% above the operating pressure. The conversation also touches on the pressure ratings of fittings, referencing ASME B16.5 and B16.9 standards for standard fittings and the complexities involved in calculating pressure ratings for bent pipes.

PREREQUISITES
  • Understanding of ASME Boiler and Pressure Vessel Codes
  • Familiarity with Maximum Allowable Working Pressure (MAWP) and Design Pressure concepts
  • Knowledge of pressure ratings for piping fittings per ASME B16.5 and B16.9
  • Basic principles of pipe bending and its effects on pressure ratings
NEXT STEPS
  • Research the ASME Boiler and Pressure Vessel Code (2007) for detailed guidelines on boiler design
  • Study the implications of relief valve settings on operational safety and compliance
  • Learn about pressure rating calculations for bent pipes and tubes
  • Explore the differences between various ASME standards for piping fittings
USEFUL FOR

Engineers, boiler designers, and piping design professionals seeking to understand the regulatory framework and technical specifications for safe boiler operation and design.

wendyv007
Messages
7
Reaction score
0
hello!
Can anyone tell me what is the difference between max working pressure and design pressure of a boiler. how do we chose the max working pressure and design pressure if a boiler need to be designed.
thank you in advance
 
Engineering news on Phys.org
Depending on where you live, there will be design codes governing the allowables in boiler design. In the US that ASME's Boiler and Pressure Vessel codes. For any application, these codes must be followed.
 
In short, Boiler and Pressre Vessel (BPV) code defines the Maximum Allowable Working Pressure (MAWP) of a vessel to be the pressure that will create stresses in the shell that equal the allowable stresses given in the material section of the code. The piping code has similar criteria, but they call this the "Design Pressure".

The codes also require that relief devices be set no higher than the MAWP except for fire cases. It gets fairly complicated, but basically you need to have a relief valve set at the MAWP of the vessel. The pressure you operate this vessel at is then dictated by this relief valve setting. Most vessels are operated such that this relief valve is set no less than 10% above the operating pressure.

For example, if you need a vessel for a process that will operate at 100 psig, you shouldn't have a relief valve set at less than 110 psig which means you will need a pressure vessel with an MAWP of at least 110 psig.
 
The design pressure is essentially the most severe condition of coincident pressure and temperature expected in normal operation.

The maximum allowable working pressure for a vessel is the maximum pressure permissible at the top of the vessel in its normal operating position at the designated coincident temperature specified for that pressure.

Source: 2007 ASME Boiler and Pressure Vessel Code (Division 1).
 
how do we chose the max working pressure and design pressure if a boiler need to be designed.

You design the boiler based on the conditions you need it to operate. The material and design is based on whatever the desired pressure and temperature is for each case you are analyzing.
 
as per indian boiler regulation the max. w.p. of boiler is the design pressure. the inspecting authority can restrict the use of boiler to a pressure(which will be called max. w.p. of that boiler) less than design pressure.
 
i am working in piping design. i design one pipe and submit the detailes to my manager. i am using 90 degree elbow 1.25*D. my manager asked that derivation for elbow calculations. is there any of them know it give me the details for me. and then suggest any book also. veryyy urgent.
 
Hi pr andandh,
Regarding the pressure rating of elbows and similar fittings;
- If you’re using standard fittings (purchased, off the shelf) then they should be manufactured to a given standard. In the US for example, pipe fittings (including elbows) are fabricated per ASME B16.5 and B16.9. Wrought copper fittings are per ASME B16.22. Other specifications exist for other types of fittings.

All specifications for fittings will provide guidance on pressure ratings. So if you are using standard fittings, you can find the pressure ratings of them using those standards.

- If you’re simply bending a piece of pipe or tube, there are two different ways I’ve seen used to evaluate this. The issue with bending a tube or pipe is that the conduit wall is stretching on the outside radius and compressing on the inner radius of the bend. The result is a thinning on the outer radius and thickening on the inner radius of the bend. Because of this thinning, there should be a decrease in working pressure at the bend. But because of cold working and the resulting toroidal shape, the working pressure should increase at the bend. Depending on how you interpret different codes and how conservative you want to be, there are two distinct view points I’ve seen:

1. Disregard the thinning because of the benefits, and rate the bend at the same pressure as the rest of the pipe or tube. Pressure testing I’ve seen has largely confirms this affect, but this particular view isn’t conservative.
2. Rate the bent tube or pipe at the pressure rating an equivalent piece of straight tube or pipe would have given the reduction in wall thickness. You can determine the reduction in wall thickness simply by doing a geometric analysis of the bend, remembering that the conduit is bending around it’s neutral axis. If you really can’t derive this wall thinning yourself, I’ll provide, but you should be able to do this without too much effort.
 

Similar threads

  • · Replies 8 ·
Replies
8
Views
4K
  • · Replies 3 ·
Replies
3
Views
3K
  • · Replies 15 ·
Replies
15
Views
5K
  • · Replies 8 ·
Replies
8
Views
3K
  • · Replies 5 ·
Replies
5
Views
5K
Replies
2
Views
2K
  • · Replies 6 ·
Replies
6
Views
3K
  • · Replies 9 ·
Replies
9
Views
2K
  • · Replies 99 ·
4
Replies
99
Views
11K
Replies
1
Views
7K