I had great difficulty editing this post to fix arithmetic and grammar errors .
System for a while refused to acknowledge "insert quotes" or even "edit" buttons... at one point i had two versions of it up ...
it looks okay now, but if you notice anything's changed , well, it probably has.
...........................
tim9000 said:
Do you mean no flux would travel through the leg with a shorted coil around it? This is an interesting notion, do you think you could draw a crude picture, what was your idea behind how it would be used as a welder?
I just spent an hour with Paint trying to draw. As usual Microsoft drove me to my knees.
It looked just about like this before i cut off the windings. Weighed probably three hundred pounds.
I was left with a three legged core. I then wound about sixty turns on center leg.
So use this schematic but the only winding present is P2, say 60 turns on center leg.
Flux enough to make 2 volts per turn flows ( let us say )UP throuh center leg (of course it's alternating but we need a mental image).
It splits , dividing between the outer legs and returns through them. It'll divide between those legs in inverse proportion to their respective reluctances, of course, which were balanced close as i could measure, i saw 1 volt per turn in each leg.
[So i just now tried in paint to draw 3 arrows representing that , the outer ones pointing down half as big as the center one pointing up. Apologies for my awkwardness]
Next i took a couple feet of of big wire and wrapped it around the right hand leg, touched the ends together rather expecting a big spark but got only a miniscule one.
The shorted turn made a MMF that opposed changing flux, and quite successfully. That's because the flux could return through the left leg.
In a normal transformer there'd be no alternate return path for flux , so the shorted turn would cancel center leg's MMF allowing my variac to push in more amps ... that's how transformers work when you think aboout it. MMF's oppose but the flux is constrained to the core so MMF primary equals very nearly MMF secondary, meaning NIprimary = NIsecondary and that's why current ratio follows turns ratio.
But my core was very happy to allow a really small current in that shorted turn to push all the flux over to the other leg.
Aha ! How interesting !
If i could cause flux to divide unequally between the legs i'd have a "variable" transformer ... put a big secondary on left leg and do something to make flux divide between the legs as i wanted.
I never finished the project, sadly - a move interrupted it and the core had to go (as Ben Franklin said "3 moves are as good as a fire.)
Here was the plan:
For a welder you want open circuit voltage to be high so it'll strike an arc
but when current starts to flow you want it to drop off quickly to the 20-30 volts required to maintain that arc.
Observe that the magnetic circuit is a source of MMF in the center leg, with left and right legs in parallel with it.
Left and right legs have equal reluctance.
So i planned to saw an air gap in the right leg raising its reluctance so that flux would shift to the left leg, and wind a 90 volt secondary there.
That would do the same thing as my shorted turn, make the flux move to left leg because it takes a lot of MMF to push flux through air.
Reluctance of right leg would be high because of air gap.As soon as current starts to flow in the left leg's winding , a MMF appears there.
That MMF is impressed across right leg because they're in magnetic parallel. So it begins to push flux through air gap in right leg, reducing left leg flux hence induced voltage.
That's the characteristic i needed, very poor voltage regulation.
By wrapping my welding lead around the right leg i'd be able to help or hinder that diversion of flux, providing current adjustment.
Back of the envelope calculations said about 1/4 inch airgap should do .
Sadly it was overtaken by events and never finished it.
Point of this digression is to get your brain thinking about pushing flux around through iron and air
because for me that's what i have to do - work it in my head, and make that process agree with the textbook equations.
As i said earlier that was ~1974 and i apologize for the lack of calculations in the presentation, details are just not sharp anymore.
I guess that exercise though was good - it erally planted in my brain the concept of MMF's in a transformer. My 1901 textbook describes Tesla's exuberance at figuring it out, "It is a marvelous self regulating system".
.................
tim9000 said:
So which Flux do I go with? There must be some simple inconcistancy I'm making but not realising.
I think i see your dilemma...
You see that these two equations are the same
tim9000 said:
B = u*N*I / len = 1.2*100*10 / 1 = 1200 <---------> Φ = u*N*I*A / len = 120
because the second one is just the first one with both sides multiplied by A.
Here's the disconnect:
You specified an inductor with ten volts per turn which at 60hz means.
10 = * w* Φcos(wt) ::: that's just familiar old n dphi/dt
10/377 = Φcos wt
Φ = .0265, which in your 0.1 meter^2 core is the B you calculated. That's the total flux(not flux density) to make 10 volts per turn, or 1000 volts per 100 turns at 60 hz.
Now - what current will make that flux?
You said you'll have 10 amps through that inductor. Well not at Φ = .0265 you won't. At 10 amps you'll get the other flux that you calculated.
B = u*N*I / len = 1.2*100*10 / 1 = 1200 , 1200sin(wt) for 60hz AC
And your volts at that flux will be what ?
V = ndΦ/dt , which = 120pi * 120
0cos(wt) =
452400 45240 volts/turn
which is an impossible result - so what happened?
Aha - u is
relative permeability, and must be multiplied by μ
0 which is 4pi X 10-7
and your value of 1.2 for u is almost air... a 100 turn
air core inductor won't make much flux
so multiply by μ
0
45240
0 X 4piX10^-7 =
.57 0.057 volts per turn , way more reasonable.
had trouble editing jh
Try to go back to the concept i had cemented into my alleged brain with my transformer core experiment,
volts per turn at given frequency is a direct measure of flux Φ, not fluxdensity B.
Flux is ∑amp turns X area/length, X physical constants μ
0 and u ,
Flux density B and MMF per unit length H are convenience terms that let you have equations not involving geometry so they work great for writing textbooks and printing datasheets.
How was temperature having such a huge effect on the permiability of your reactor? (I thought you were going to say there was a breakdown of lamination insulation and that was causing such large eddy currents or something) Why was it not forseen? What did you do about it?
Lastly - those iron rod drive shafts were not laminated at all. I can only think it was an oversight to operate them at line frequency.
We spoke to the designers and they'd never tried other frequencies or waveshapes, and seemed delighted with what we'd found.
I never did find in any literature a discussion of eddy current effects versus temperature in solenoid cores.
Somebody argued there could be other effects - Bozorth speaks of time effects in magnetizing iron , and the shaft gets strongly magnetized by the action of lifting the rods(it uses DC electromagnets) so that we're not quite centered on its B-H curve, and there's a lot of Gamma rays up there...
But i heated a shaft to ~ 200 degF and observed its behavior enough to convince myself we'd hit the nail on its head.
Eddy currents cancel flux making the inductance go down, but as the iron heats up eddy currents decrease, less flux is cancelled, so you get more flux per ampere
and inductance IS flux per ampere
so a warmer core looked like it had better u. As i said , i calculated apparent u around 25 versus the few hundred expected for stainless steel..
Apparent u is a function of both frequency and temperature, and it's not in textbook equations.
But it shows up in datasheets as different values for permeability at DC, 60 hz, 50 hz, and sometimes 400 hz. That's why you have different lamination thickness for different frequencies, and powder for radio frequencies. But i never saw a curve for temperature other than the one we empirically measured on our warehouse floor..
What did we do about it?
We learned to live with the temperature sensitivity... and improved our calibration technique.
There's a market for perhaps a dozen systems that'd get around it. As much fun as it would be, it's almost impossible to change anything in a Nuke plant.