Electrical heating transmission wires

Click For Summary
SUMMARY

The discussion centers on the principles of electrical heating transmission and power loss calculations. It clarifies that while high voltage (V) can suggest increased heating effects through the equation P = V^2 / R, the actual power loss in transmission lines is better understood using P = I^2 R. The key takeaway is that higher voltage results in lower current, which reduces power losses in the transmission line. This is because the voltage drop across the transmission line is a fraction of the total voltage supplied to the load, making the I^2 R formula more applicable for calculating losses.

PREREQUISITES
  • Understanding of Ohm's Law and power equations (P = I^2 R and P = V^2 / R)
  • Familiarity with electrical transmission concepts and transformer operations
  • Basic knowledge of circuit diagrams and voltage drop calculations
  • Experience with power loss analysis in electrical systems
NEXT STEPS
  • Study the impact of transmission line resistance on power loss calculations
  • Learn about the operation and efficiency of step-up transformers in electrical systems
  • Explore advanced circuit analysis techniques for understanding voltage drops
  • Investigate real-world applications of high-voltage transmission in reducing energy losses
USEFUL FOR

Electrical engineers, power system analysts, and students studying electrical transmission systems will benefit from this discussion, particularly those focused on optimizing power delivery and minimizing losses in electrical networks.

Glenn G
Messages
113
Reaction score
12
Hello community.
I have a question about electrical heating. I am familiar with the fact that textbooks explain how power losses are reduced by transmitting at high V and low I since P = I^2 X R (equation from Ohm's law and P=I X V)

But if you use a different sub for P = I V then you get P = V^2 / R ... So this would suggest high V gives a high heating effect. How would you describe the apparent contradiction here? My take is that the power output is fixed because it depends on the input and as such you will, with a step up transformer get a low I and high V and therefore lower I^2 R, but I don't get why we are precluded from using P=V^2/R for explaining power losses as this clearly gives the opposite conclusion.

Kind regards,
Glenn
 
Physics news on Phys.org
It doesn't give a different conclusion ...I think the best way to grasp this is to calculate the losses in a given situation ...

First imagine you have a power line of 1ohm resistance then calculate the losses in the powerline when (a) transmitting 1kw of power at 10V ...(b) ...transmitting 1kw of power at 100V ... whichever equations you use the answer will come out the same , and at higher voltages the loss is less for same power delivered
 
  • Like
Likes   Reactions: Glenn G
Glenn G said:
My take is that the power output is fixed because it depends on the input and as such you will, with a step up transformer get a low I and high V and therefore lower I^2 R
Right.
Glenn G said:
but I don't get why we are precluded from using P=V^2/R for explaining power losses as this clearly gives the opposite conclusion.
It doesn't.
Draw a simple circuit diagram with a high voltage source V, a transmission line with resistance R and a connected load. What is the voltage across the transmission line resistance? What do you understand from this?
 
  • Like
Likes   Reactions: Glenn G
Glenn G said:
Hello community.
I have a question about electrical heating. I am familiar with the fact that textbooks explain how power losses are reduced by transmitting at high V and low I since P = I^2 X R (equation from Ohm's law and P=I X V)

But if you use a different sub for P = I V then you get P = V^2 / R ... So this would suggest high V gives a high heating effect. How would you describe the apparent contradiction here? My take is that the power output is fixed because it depends on the input and as such you will, with a step up transformer get a low I and high V and therefore lower I^2 R, but I don't get why we are precluded from using P=V^2/R for explaining power losses as this clearly gives the opposite conclusion.

Kind regards,
Glenn
This would be true if the transmission lines were the only load, but they are not. They are in series with the destination load. Doubling the line voltage cuts the current delivered in half. Since the line resistance is constant, you will actually drop less voltage across the transmission lines.
 
  • Like
Likes   Reactions: Glenn G
For the loss in the transmission line the V in P = V^2 / R is NOT the voltage of the transmission line. V is the voltage DROP across the length of the transmission line. You don't know what that V is. You could figure it out by V = I R, but that puts you right back at P = I^2 R. Lower current gives less loss in the transmission line. To deliver the same power to the load at lower current you need higher voltage.
 
  • Like
Likes   Reactions: NTL2009 and Glenn G
Thanks for your help, I see now where I was getting confused of course the voltage drop across the cables are only a proportion of the output voltage with the rest going to the load whereas the same current is going through the cables and the load, hence I suppose the ease of using I^2 X R to find the energy losses in just the transmission cables
 

Similar threads

  • · Replies 3 ·
Replies
3
Views
1K
  • · Replies 4 ·
Replies
4
Views
2K
  • · Replies 2 ·
Replies
2
Views
2K
  • · Replies 10 ·
Replies
10
Views
1K
  • · Replies 3 ·
Replies
3
Views
2K
  • · Replies 16 ·
Replies
16
Views
3K
  • · Replies 2 ·
Replies
2
Views
1K
  • · Replies 4 ·
Replies
4
Views
1K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 12 ·
Replies
12
Views
7K