Electricity in transmission lines (Simple V^2/R =P)

Click For Summary
SUMMARY

The discussion focuses on calculating the resistance of high-voltage transmission lines using the formula V^2/R = P. Given a transmission line delivering 800 MW at 132 kV, the resistance is determined to be 0.2 ohms, accounting for a 1% power loss as heat. The participants clarify that the actual power generated must exceed 800 MW to compensate for this loss, emphasizing the importance of understanding current flow and ohmic losses in transmission lines.

PREREQUISITES
  • Understanding of electrical power formulas, specifically V^2/R = P and P = V*I.
  • Knowledge of power loss calculations in transmission lines, including I^2*R losses.
  • Familiarity with high-voltage transmission concepts and their implications on power delivery.
  • Basic grasp of electrical resistance and its role in energy dissipation.
NEXT STEPS
  • Study the derivation and application of the formula P = I^2*R in electrical systems.
  • Learn about the impact of transmission line resistance on overall power efficiency.
  • Explore methods for calculating current in electrical circuits using P = V*I.
  • Investigate the effects of voltage drop in high-voltage transmission systems.
USEFUL FOR

Electrical engineers, power system analysts, and students studying electrical engineering who are interested in transmission line efficiency and power loss calculations.

bonbon22
Messages
92
Reaction score
5
Homework Statement
The National Grid uses high-voltage transmission lines to carry electrical power
around the UK. A particular transmission line delivers 800 MW of power at
132 kV to the user. It loses 1% of the transmitted power as heat.
What is the resistance of the transmission line?
[1 mark]
A 0.2 Ω
B 6 Ω
C 20 Ω
D 2000 Ω
Relevant Equations
V^2/R = P
I understand how to get the answer but i don't understand how the answer 0.2 ohms is equal to the resistance of the transmission lines
If V^2/P = R then (132kV)^2/800MW = the resistance of the transmission lines, why is the 1% tansmitted as heat relevant at all as this is just one form of energy released from the resistance ?
 
Physics news on Phys.org
bonbon22 said:
Problem Statement: The National Grid uses high-voltage transmission lines to carry electrical power
around the UK. A particular transmission line delivers 800 MW of power at
132 kV to the user. It loses 1% of the transmitted power as heat.
What is the resistance of the transmission line?
[1 mark]
A 0.2 Ω
B 6 Ω
C 20 Ω
D 2000 Ω
Relevant Equations: V^2/R = P

If V^2/P = R then (132kV)^2/800MW = the resistance of the transmission lines, why is the 1% tansmitted as heat relevant at all as this is just one form of energy released from the resistance ?
The transmission line is not the load connected to the end of the transmission line. Clearly, if all 132 kV were dropped across the transmission line then no power would be available for the actual load.

If 800 MW is actually delivered to the load, then there must be both voltage and current involved. That current is what leads to ohmic losses in the resistance of the transmission line.
 
  • Like
Likes   Reactions: bonbon22
why is the 1% tansmitted as heat relevant at all as this is just one form of energy released from the resistance ?
Remember that the transmission lines deliver 800 MW of power to the user. What is lost as heat is lost. The 800 MW delivered is 99% of the power that the generating plant put into the transmission line. Another relevant equation for power is P = V*I. The power lost as heat is I^2*R.
 
  • Like
Likes   Reactions: bonbon22
sojsail said:
Remember that the transmission lines deliver 800 MW of power to the user. What is lost as heat is lost. The 800 MW delivered is 99% of the power that the generating plant put into the transmission line. Another relevant equation for power is P = V*I. The power lost as heat is I^2*R.
sojsail said:
Remember that the transmission lines deliver 800 MW of power to the user. What is lost as heat is lost. The 800 MW delivered is 99% of the power that the generating plant put into the transmission line. Another relevant equation for power is P = V*I. The power lost as heat is I^2*R.
ok. I think i understand it a bit better, when doing the calculation for resistance i got a value of 21.78ohms what does this value represent the answer was 0.01 percent of this value.
 
bonbon22 said:
ok. I think i understand it a bit better, when doing the calculation for resistance i got a value of 21.78ohms what does this value represent the answer was 0.01 percent of this value.
You'll have to show your work so that we can see what you've calculated.
 
gneill said:
You'll have to show your work so that we can see what you've calculated.
132kV ^2/ 800mw
gneill said:
You'll have to show your work so that we can see what you've calculated.


(132*10^3)^2/80010^6 = 21.78
 
bonbon22 said:
(132*10^3)^2/80010^6 = 21.78
Once again you're taking the voltage drop on the transmission line to be the entire voltage delivered to the load. That is incorrect. Only a small fraction of the voltage produced by the generating station is "lost" traveling the transmission line.
 
  • Like
Likes   Reactions: bonbon22
The power lost via P = I^2*R heating is just 1% of the total power. Now, if you only knew the current ...
 
  • Like
Likes   Reactions: bonbon22
sojsail said:
The power lost via P = I^2*R heating is just 1% of the total power. Now, if you only knew the current ...
0.01 of (800 * 10^6) = 8*10^6
(132*10^3)^2/ 8*10^6 = 2178
gneill said:
Once again you're taking the voltage drop on the transmission line to be the entire voltage delivered to the load. That is incorrect. Only a small fraction of the voltage produced by the generating station is "lost" traveling the transmission line.
so i take 1 percent of both power and voltage , i got the right answer now cheers.
 
  • #10
I was trying to steer you to a method of solving that I thought would demonstrate a more clear way to look at it:

You could calculate the current using P = V*I.
And then find the resistance, using as data the above current and the power that is lost to heat (P_lost=1% of P) while that current flows thru the R.
This formula, P_lost = I^2*R, rearranged as R = P_lost / I^2, would then have given you the same result.
 
  • Like
Likes   Reactions: bonbon22
  • #11
sojsail said:
I was trying to steer you to a method of solving that I thought would demonstrate a more clear way to look at it:

You could calculate the current using P = V*I.
And then find the resistance, using as data the above current and the power that is lost to heat (P_lost=1% of P) while that current flows thru the R.
This formula, P_lost = I^2*R, rearranged as R = P_lost / I^2, would then have given you the same result.
sojsail i appreciate your help, slightly confused are you saying that only taking the power at 1 percent but not the voltage would give me the same result ? is it bad practice to use V^2 /R so its better to use I ^2 * R?
thanks again.
 
  • #12
Consider the phrasing of the original problem statement:
A particular transmission line delivers 800 MW of power at
132 kV to the user. It loses 1% of the transmitted power as heat.
800 MW at 132 kV is delivered to the user. That's what ends up across the eventual load. If 1% of the generated power is being lost in transmission, the generating station must actually be generating 808 MW at its end of the line.

You know what the user is receiving. From that information you can determine the current in the load and hence the transmission line since they are in series.

243259


The transmission line is dissipating ΔP = 8 MW of power. So ##\Delta P = I^2 R_T## and solve for ##R_T##.
 
  • Like
Likes   Reactions: sojsail and bonbon22
  • #13
gneill said:
Consider the phrasing of the original problem statement:

800 MW at 132 kV is delivered to the user. That's what ends up across the eventual load. If 1% of the generated power is being lost in transmission, the generating station must actually be generating 808 MW at its end of the line.

You know what the user is receiving. From that information you can determine the current in the load and hence the transmission line since they are in series.

View attachment 243259

The transmission line is dissipating ΔP = 8 MW of power. So ##\Delta P = I^2 R_T## and solve for ##R_T##.
ahhh gotcha makes perfect sense now , cheers m8
 

Similar threads

  • · Replies 2 ·
Replies
2
Views
2K
  • · Replies 9 ·
Replies
9
Views
2K
Replies
6
Views
1K
  • · Replies 20 ·
Replies
20
Views
11K
  • · Replies 14 ·
Replies
14
Views
3K
  • · Replies 4 ·
Replies
4
Views
4K
  • · Replies 3 ·
Replies
3
Views
4K
  • · Replies 7 ·
Replies
7
Views
4K
Replies
8
Views
2K
  • · Replies 4 ·
Replies
4
Views
2K