Flow rate through large air duct

Click For Summary
SUMMARY

The discussion focuses on calculating the flow rate in a large duct (4'x3') connected to a fan with varying duct sizes. It emphasizes that static pressure readings alone are insufficient for accurate flow rate estimation. Instead, utilizing a fan curve to plot static pressure or employing a pitot tube to measure velocity is recommended for precise calculations. The impact of dynamic pressure head variation on flow rate estimation is also highlighted as significant.

PREREQUISITES
  • Understanding of duct sizing and airflow principles
  • Familiarity with fan curves and their application
  • Knowledge of static and dynamic pressure measurements
  • Experience with pitot tube usage for velocity measurement
NEXT STEPS
  • Research how to interpret fan curves for flow rate calculations
  • Learn about static pressure and dynamic pressure measurement techniques
  • Study the application of pitot tubes in HVAC systems
  • Explore the effects of duct geometry on airflow and pressure loss
USEFUL FOR

HVAC engineers, mechanical engineers, and anyone involved in airflow measurement and duct design will benefit from this discussion.

mattibo
Messages
7
Reaction score
1
I am trying to find the flow rate in a duct that is quite large (around 4'x3') but is very short. This duct leads to a fan which leads to a separate unit through another short duct section. Both these duct sections have different sizes (the fan outlet is much bigger than its inlet). I will take static pressure readings before and after the fan to calculate the flow rate. How will the change in duct sizing effect my flow rate estimation? I guess that the dynamic pressure head variation will have a significnt effect.

Thank you for reading.
 
  • Like
Likes   Reactions: DaleLEspinal456
Engineering news on Phys.org
ping @russ_watters . Can you help with this spring cleaning thread?
 
  • Like
Likes   Reactions: russ_watters
mattibo said:
I am trying to find the flow rate in a duct that is quite large (around 4'x3') but is very short. This duct leads to a fan which leads to a separate unit through another short duct section. Both these duct sections have different sizes (the fan outlet is much bigger than its inlet). I will take static pressure readings before and after the fan to calculate the flow rate. How will the change in duct sizing effect my flow rate estimation? I guess that the dynamic pressure head variation will have a significnt effect.
You can't calculate the flow rate from a static (or differential) pressure measurement across the fan alone. But if you have the fan curve, you can plot the static pressure on it and find the flow. Either way, if you have the equipment to measure the pressure it would be better to use a pito-tube and measure the velocity -- then calculate the flow rate with the duct area.
 
  • Like
Likes   Reactions: anorlunda

Similar threads

  • · Replies 4 ·
Replies
4
Views
3K
Replies
1
Views
1K
  • · Replies 7 ·
Replies
7
Views
2K
  • · Replies 3 ·
Replies
3
Views
3K
  • · Replies 3 ·
Replies
3
Views
2K
  • · Replies 38 ·
2
Replies
38
Views
4K
  • · Replies 3 ·
Replies
3
Views
3K
  • · Replies 4 ·
Replies
4
Views
2K
  • · Replies 20 ·
Replies
20
Views
5K
  • · Replies 15 ·
Replies
15
Views
7K