Graphical way of sizing a storage tank

Click For Summary
SUMMARY

This discussion focuses on the graphical method for sizing a hot water storage tank based on energy consumption patterns. A total of 55 kWh is utilized over a 24-hour period, with a heat source power of 3.5 kW capable of heating this energy in 10 hours. The placement of tangents along the usage curve is critical for determining the necessary storage capacity, with the distance between tangents representing energy in kWh. Understanding daily hot water needs is essential for optimizing storage tank size and cycle frequency.

PREREQUISITES
  • Understanding of thermal energy calculations
  • Familiarity with graphical analysis techniques
  • Knowledge of hot water heating systems
  • Basic principles of energy consumption and storage
NEXT STEPS
  • Research methods for calculating daily hot water needs
  • Explore graphical techniques for energy consumption analysis
  • Learn about different types of hot water storage tanks
  • Investigate the impact of temperature variations on heating cycles
USEFUL FOR

Engineers, HVAC professionals, and anyone involved in designing or optimizing hot water heating systems will benefit from this discussion.

TSN79
Messages
422
Reaction score
0
The attachment shows an example from a book on how to size a hot water storage tank (for tap water). During the 24h period a total of 55 kWh is used. The red curve shows the variation in usage along the period. The slope of the green lines is determined by the heat source's power, in this case 3,5 kW, which manages to heat up 55 kWh in 10 hours. Tangents are then placed along the curve as shown in the topmost example to determine how much water must be stored.

My question is this; how do I know where exactly to place the tangents? The book shows the topmost placing in this case but I don't see how this is obvious. The bottom example (by me) results in more storage but how do I know that's not the correct choice...?
 

Attachments

  • hotwater.jpg
    hotwater.jpg
    19.7 KB · Views: 662
Engineering news on Phys.org
The tangents are separated by a distance proportional to energy, in kWh. Note that the second plot, shows two lines separated by 2 kWh.

How to place the tangent? You must know your hot water needs. How many kWh per day of hot water heating do you need? Suppose that is 29 kwh, then one 29 kWh cycle per day serves that need. However, if the temperature drops too low between cycles, it might be better to split it into 10, 10 and 9 kWh smaller cycles.
 

Similar threads

  • · Replies 12 ·
Replies
12
Views
2K
Replies
14
Views
3K
  • · Replies 2 ·
Replies
2
Views
4K
  • · Replies 1 ·
Replies
1
Views
3K
Replies
12
Views
3K
  • · Replies 6 ·
Replies
6
Views
11K
  • · Replies 17 ·
Replies
17
Views
4K
Replies
20
Views
9K
  • · Replies 1 ·
Replies
1
Views
4K
  • · Replies 10 ·
Replies
10
Views
6K