Halving 220V Output Voltage: Investigating the Problem

  • Thread starter Thread starter sbsapre
  • Start date Start date
  • Tags Tags
    Output Voltage
Click For Summary
SUMMARY

The discussion centers on a 20 KVA UPS system that outputs 220 Volts single-phase from an isolation transformer, while measurements indicate 110 Volts when referenced to ground. This discrepancy suggests the use of a center-tap transformer, where the center tap is grounded, effectively halving the voltage when measured to ground. Additionally, the UPS fails when connected to a load typically powered by another 20 KVA UPS with a three-phase, 440 Volts output, indicating potential compatibility issues between the systems.

PREREQUISITES
  • Understanding of three-phase power systems
  • Knowledge of isolation transformers and their configurations
  • Familiarity with voltage measurement techniques
  • Basic principles of UPS operation and load compatibility
NEXT STEPS
  • Research center-tap transformer configurations and their applications
  • Learn about UPS load compatibility and connection methods
  • Investigate voltage measurement techniques in electrical systems
  • Explore troubleshooting methods for UPS failures under load
USEFUL FOR

Electrical engineers, UPS system designers, and technicians involved in power distribution and troubleshooting electrical systems.

sbsapre
Messages
1
Reaction score
0
Dear All,

In our plant , we have an 20 KVA UPS with three phase , 440 Volts , 50 HZ input . The output is single phase 220 Volts outputted from Isolation transformer.
I find it strange though output voltage between two terminal of isolation transformer is 220 Volts , when measured with respect to ground , it is 110 Volts.
I want to understand how the output voltage is halved when measured with respect to ground.
Another problem whenever output voltage is connected to load which is normally fed by another 20 KVA UPS having 3 phase , 4 wire , 440 volts output , the single phase UPS fails.
We have taken precaution of connecting two terminals of 220 KVA single phase UPS to one phase and ground of the load terminals which are normally fed by UPS having three phase output.
I shall appreciate valuable inputs from members.
Regards,

S.B. SAPRE
 
Engineering news on Phys.org
sbsapre said:
Dear All,

I find it strange though output voltage between two terminal of isolation transformer is 220 Volts , when measured with respect to ground , it is 110 Volts.
I want to understand how the output voltage is halved when measured with respect to ground.
Most likely it is a center tap transformer. With the tap connected to ground.
 

Similar threads

  • · Replies 5 ·
Replies
5
Views
2K
Replies
9
Views
2K
  • · Replies 25 ·
Replies
25
Views
5K
  • · Replies 4 ·
Replies
4
Views
3K
Replies
19
Views
3K
  • · Replies 14 ·
Replies
14
Views
5K
Replies
12
Views
3K
Replies
6
Views
3K
  • · Replies 9 ·
Replies
9
Views
4K
Replies
4
Views
2K