Heat exchanger capacity (condenser and evaporator)

Click For Summary
SUMMARY

The discussion focuses on calculating heat exchanger capacity in window-type air conditioning units, specifically addressing the refrigerant and air interactions. The correct method for determining heat absorbed involves using the mass flow rate of the refrigerant and the change in enthalpy, as the refrigerant typically operates in a two-phase state. The equations involving air mass flow and specific heat are valid only under specific conditions, such as dry air. The conversation also touches on the use of a psychrometric chart for experiments involving air pressure changes due to fan operation.

PREREQUISITES
  • Understanding of vapor-compression refrigeration cycles
  • Knowledge of thermodynamic properties, including specific heat and enthalpy
  • Familiarity with heat exchanger principles
  • Experience with psychrometric charts and air properties
NEXT STEPS
  • Research the application of enthalpy in heat exchanger calculations
  • Learn about two-phase flow dynamics in refrigeration systems
  • Study the impact of humidity on specific heat calculations
  • Explore the use of psychrometric charts in HVAC applications
USEFUL FOR

This discussion is beneficial for HVAC engineers, thermodynamics students, and professionals involved in the design and analysis of heat exchangers in air conditioning systems.

plucker_08
Messages
54
Reaction score
0
Window-type Aircon

how to get this in an actual experiment?

is it just (mass flow rate of the refrigerant X specific heat X Change in temp of the refrigerant)

or (mass flow rate of the air passing thru the heat exchanger X specific heat X Change in temp of the air)

or (mass flow rate of the refrigerant X change in enthalpy (outlet and inlet state of the refrigerant)

or (mass flow rate of the air X Change in enthalpy of the air)
 
Engineering news on Phys.org
First, think about what control volume you are doing the analysis on. Are you measuring the air or the refrigerant? Under ideal situations, the heat absorbed by the refrigerant is the same as the heat rejected in the room. But practically, you are much more likely to get good data measuring changes in the refrigerant.

This eliminates your second and fourth equations.

Your first equation assumes that the refrigerant is a perfect gas but because in a traditional vapor-compression refrigeration cycle the flow through a heat exchanger is typically two-phase this is a bad assumption, hence this equation does not apply.

Your third equation will allow you to properly calculate the amount of heat absorbed.
 
The first response is fine, but just a quick fyi - if the air is dry, you can use the specific heat times delta-T times mass flow for the air, but if it is moist, you'll need to add the specific heat and mass flow of condensed water. But just using enthalpy instead covers that.

Btw, there is a recent thread about a window heat pump unit where I do this exact experiment. I'm trying to get a paper published.
 
can i use the pyschrometric chart for 100KPa, even if the air is blown thru fan?

the air pressure increases when blown by fan, right?
 
Yes, air pressure increases when blown through a fan, but not by much. A powerful air conditioning fan might give you 1kPa of pressure rise.
 

Similar threads

  • · Replies 3 ·
Replies
3
Views
3K
Replies
1
Views
824
  • · Replies 3 ·
Replies
3
Views
2K
Replies
7
Views
2K
  • · Replies 3 ·
Replies
3
Views
2K
  • · Replies 3 ·
Replies
3
Views
3K
  • · Replies 4 ·
Replies
4
Views
3K
  • · Replies 9 ·
Replies
9
Views
2K
Replies
11
Views
15K
  • · Replies 8 ·
Replies
8
Views
5K