SanPhysics said:
Is that means I can make toroidal transformer up to 418 VA.
There you go - Well Done !
That's a practical page !
I do a reasonableness check on formulas before i trust them
VA=5.0*J*Bm*f*Ac min*ID²*10-7
VA =Power handling capacity (VA)
J =Current density (A/ mm2)
Bm =Maximum induction ( Tesla)
f =Frequency ( Hz)
ID =Inside diameter (mm)
Ac min =Effective cross sectional area (mm2)
Let's see here
jim hardy said:
Its VA capacity is limited by how much wire you can fit through the window.
J X ID
2 tells how many amps i can get through the window for a given current density, which will define amps X turns
Bm X Acmin tells how much flux i can get through the core , which when multiplied by frequency defines the volts per turn
amps X turns X volts/turn = VA
so the form of the equation passes my sanity check.
They collected their constants in those two numbers, 5.0 & 10
-7
and i didnt check them. This is just a sanity check after all ...
SanPhysics said:
VA= (5.0*3.1*1.5*50*1000*3600)*0.0000001=418.5
I see where you got every number except the 3.1 for J
and i got the same result as you when i multiplied
so yes i think your 418.5 VA is the capacity of that core at 3.1 amps/mm
2
418 VA / 230V = 1.82 amps / 3.1 = 0.59mm2 wire , approximately #19 which seems reasonable
Be aware it might take considerable patience to get enough turns on it when winding by hand instead of using a machine that lays them in neatly
but it's really instructive to wind a core and run a saturation curve on it - plot magnetizing current versus volts per turn.
I'm very much impressed with that Eilor tutorial you found. NIce Job !
Have Fun . We learn 10X better by actually doing things than by just reading about doing them.
Keep us posted ?
old jim