How to estimate enthalpy change across a compressor in simple vapor compression cycle

AI Thread Summary
To estimate the enthalpy change across a compressor in a vapor compression cycle using R134a, one can analyze the conditions before and after the compressor, specifically from point H1 to H2. The outlet enthalpy (H2) can be estimated using the compressor's displacement and RPM to calculate the mass flow rate, alongside the power input for enthalpy increase. It is important to consider that if the compressor operates adiabatically, the inlet and outlet entropy will remain approximately constant. For obtaining R134a property data, resources such as manufacturer data, thermodynamic tables, and engineering textbooks are recommended. Accurate calculations depend on understanding the system's heat load and the compressor's operational characteristics.
bobkokke
Messages
1
Reaction score
0
TL;DR Summary
Calculate compressor side of a Vapour compression cycle without knowing output of the compressor.
Hi everyone,


I'm fairly new to HVACR systems and currently doing research on building an estimation model of a basic vapor compression cycle.


Right now, I'm trying to calculate the enthalpy change across the compressor — from point H1 (before the compressor) to point H2 (after the compressor). For my test setup, I’m assuming R134a as the refrigerant, with an inlet pressure of 2 bar. (if possible well asume 5K superheating)


As a reference, I’m using a Bitzer 2DC-3.2Y-40S compressor, but I don’t yet have outlet pressure or temperature data.


My questions are:


  • How can I estimate the outlet enthalpy (H2) in this situation?
  • Can I use the compressor's displacement and RPM to estimate the mass flow rate, and then use power input to find enthalpy increase?
  • Are there any tools or databases you recommend for getting R134a property data?

Any help or guidance would be greatly appreciated!
 
Engineering news on Phys.org
The mass flow rate is determined by the heat load of the overall system. Are you saying that you have no idea what the outlet conditions of the compressor are. If the compressor is operating adiabatically (and nearly reversibly), the inlet entropy- and outlet entropy per unit mass will be about the same. So you move on a constant entropy line for the compressor.

You can get thermodynamic data on 134a either from the manufacturer (e.g., DuPont) of probably from tables in Fundamentals of Engineering thermodynamics by Moran et al. There should be table online of 134a thermodynamic data also.
 
Posted June 2024 - 15 years after starting this class. I have learned a whole lot. To get to the short course on making your stock car, late model, hobby stock E-mod handle, look at the index below. Read all posts on Roll Center, Jacking effect and Why does car drive straight to the wall when I gas it? Also read You really have two race cars. This will cover 90% of problems you have. Simply put, the car pushes going in and is loose coming out. You do not have enuff downforce on the right...
Thread 'Physics of Stretch: What pressure does a band apply on a cylinder?'
Scenario 1 (figure 1) A continuous loop of elastic material is stretched around two metal bars. The top bar is attached to a load cell that reads force. The lower bar can be moved downwards to stretch the elastic material. The lower bar is moved downwards until the two bars are 1190mm apart, stretching the elastic material. The bars are 5mm thick, so the total internal loop length is 1200mm (1190mm + 5mm + 5mm). At this level of stretch, the load cell reads 45N tensile force. Key numbers...
I'm trying to decide what size and type of galvanized steel I need for 2 cantilever extensions. The cantilever is 5 ft. The space between the two cantilever arms is a 17 ft Gap the center 7 ft of the 17 ft Gap we'll need to Bear approximately 17,000 lb spread evenly from the front of the cantilever to the back of the cantilever over 5 ft. I will put support beams across these cantilever arms to support the load evenly
Back
Top