How to understand the Rating of this transformer

  • Thread starter Thread starter RITESHH KAKKAR
  • Start date Start date
  • Tags Tags
    Rating Transformer
Click For Summary
SUMMARY

The transformer discussed has a rating of 7.5 kVA, with a primary voltage of 460 VAC and a secondary voltage of 230 L-L and 133 L-N. It features a Delta primary and Wye secondary winding structure, with a maximum continuous AC power rating of 7.5 kVA. The transformer can be tapped to provide 105.0%, 100.0%, or 95.0% of the primary nominal voltage, and has a percent impedance of 3.3% at 170°C. Its insulation class is rated at 220°C, indicating the maximum winding temperature in service, and it employs ambient air cooling, primarily used for isolation in electric motor applications.

PREREQUISITES
  • Understanding of transformer ratings and specifications
  • Knowledge of Delta and Wye winding configurations
  • Familiarity with electrical voltage levels and their applications
  • Basic principles of transformer insulation classes and cooling methods
NEXT STEPS
  • Research transformer winding methods, specifically Delta and Wye configurations
  • Learn about transformer insulation classes and their significance in operation
  • Explore the implications of transformer impedance on performance
  • Investigate the cooling methods used in transformers and their effects on efficiency
USEFUL FOR

Electrical engineers, technicians working with transformers, and professionals involved in motor isolation applications will benefit from this discussion.

RITESHH KAKKAR
Messages
16
Reaction score
0
Hello
How to know the rating of this transformer
 

Attachments

  • rtgty.jpg
    rtgty.jpg
    68.3 KB · Views: 409
Engineering news on Phys.org
The name plate says 7.5 KVA. That is the rating.
 
  • Like
Likes   Reactions: Fisherman199
Hello
How the Winding is done in it what is the method
 
RITESHH KAKKAR said:
Hello
How the Winding is done in it what is the method
Delta primary, Wye secondary - It’s all there on the plate...
 
RITESHH KAKKAR said:
Hello
How to know the rating of this transformer

The Maximum continuous AC Power rating: 7.5kVA
Primary Voltage: 460VAC
Secondary Voltage: 230 L-L; 133 L-N
Can be tapped to provide either: 105.0%, 100.0%, or 95.0% of primary nominal voltage.
Winding Structure: Delta/G-Wye
Percent Impedance at 170 C (normal operating temperature): 3.3%
Insulation class: 220 (220 C will be the maximum winding temperature when in service. Hotter than that and something is wrong.)
Cooling Method: AA (Ambient Air)
Most likely usage: Isolation for an electric motor (hence the strange primary voltage and delta primary winding.)
 
Last edited:
  • Like
Likes   Reactions: krater

Similar threads

  • · Replies 8 ·
Replies
8
Views
3K
  • · Replies 10 ·
Replies
10
Views
2K
  • · Replies 8 ·
Replies
8
Views
2K
  • · Replies 12 ·
Replies
12
Views
2K
  • · Replies 4 ·
Replies
4
Views
2K
  • · Replies 9 ·
Replies
9
Views
2K
  • · Replies 3 ·
Replies
3
Views
2K
  • · Replies 9 ·
Replies
9
Views
3K
Replies
2
Views
1K
  • · Replies 2 ·
Replies
2
Views
963