gferr
Messages
1
Reaction score
0
I have been using etap 7.5 demo and have been trying to model an HVDC link connected to 2 buses and conduct a load flow analysis (there is also a generator in swing mode attached to one bus and a normal transmission line connecting the two buses to satisfy the simulation requirements), but it comes up with a pop up error saying calculation error "Calcluation aborted due to HVDC rectifier output or Inverter input kV not matching rated kV".

I am unsure of what settings to use for the ratings page for the HVDC link. The busbars I am connecting to are set to 400 kV.

Does anyone have an example of settings for the HVDC link ratings page that would allow this to operate ?

Thanks
 
Engineering news on Phys.org
maybe your value 400kv out of range?
use specified rated value or lower value