Inserting pulling metal wires in existing empty conduit

Click For Summary

Discussion Overview

The discussion revolves around techniques for inserting metal wires into an existing empty PVC conduit, specifically one that is 1.5748" (40mm) in diameter. Participants explore various methods for wire pulling, the capacity of the conduit for different wire sizes, and considerations regarding the condition of the conduit over time, including potential issues with water ingress.

Discussion Character

  • Exploratory
  • Technical explanation
  • Debate/contested
  • Mathematical reasoning

Main Points Raised

  • One participant suggests using a "fish tape" for pulling wires, noting that aluminum wire may face challenges navigating bends in the conduit.
  • Another participant proposes a method involving a cotton ball and a vacuum cleaner to facilitate pulling a thread through the conduit.
  • Concerns are raised about the maximum number of conductors that can fit in the conduit, with references to various tables and calculations regarding conduit fill.
  • Questions are posed about the implications of water in underground conduits and how it might affect the electrical system.
  • Participants discuss the ampacity of AWG 4 wire and whether using multiple pairs would effectively double the capacity or maintain the original rating.
  • There is mention of discrepancies in wire area calculations from different sources, leading to confusion about the correct values.

Areas of Agreement / Disagreement

Participants express differing opinions on the best methods for wire insertion and the implications of conduit conditions. There is no consensus on the maximum number of conductors or the effects of water in conduits, and the discussion remains unresolved regarding the ampacity of multiple AWG 4 wires.

Contextual Notes

Participants note potential limitations in the accuracy of wire area calculations and the reliability of references used for conduit fill. The discussion also highlights the need for further clarification on the effects of water in conduits and the implications for electrical safety.

Cobul
Messages
100
Reaction score
11
40mm conduit.JPG


metal wire.JPG


Inserting wires in existing empty conduit

There is an empty PVC conduit size 1.5748" (40mm) in the main entrance panel. It was built around 8 years ago. There is metal wire (see picture above) inside the conduit to pull the main electrical wires from the inside or outside. Is there any technique the electrician can successfuly use to insert the metal wire?

And usually what maximum electrical wire size can fit the empty PVC conduit size 1.5748" (40mm). 2 Live plus one ground wire. Will apply full permit. Don't worry. Just want to know if the conduit can still be used. Thanks.
 
Engineering news on Phys.org
"Pulling" is usually done with a "fish tape." This is a ribbon of tempered, springy, Steel that can be pushed thru the conduit. For heavier (or many) wires, as you have, the fish tape is then used to pull a rope thru. The rope is then used to pull the wires.

The photo you show seems to be Aluminium wire. That may work if the conduit is a straight run, but trying to push it around elbows or thru couplings can be a problem, it isn't stiff enough and when it hits an obstacle it stops. Then you try pushing harder and it bends somewhere in the middle and piles up there.

My handy pocket reference says 5 #2 conductors will fit in that conduit, however I have learned not to rely on that reference, it has too many errors. Still, it seems like there is plenty of room. I'm expect the permit folks will flag anything they don't like.

Cheers,
Tom
 
  • Informative
  • Like
Likes   Reactions: berkeman and Keith_McClary
Cobul said:
Inserting wires in existing empty conduit
Make a small soft ball of cotton wool, that will be just less than the size of the conduit. Gently wind a thread around the ball without tension, make sure the cotton ball stays shaped like a sphere. When a sufficient length of thread has been wound onto the ball, cut the thread and tie off the tail at one end of the conduit. Place the ball in the conduit.

Go to the other end and connect a vacuum cleaner to the conduit. The ball will be pulled through, laying the thread in the conduit as the cotton ball rolls along. Use the first thread to pull a string, then a wire, until you can pull the cables.
You might need to pull another wire in the future, so remember to pull a string into the conduit with the cables.

Use the vacuum cleaner when no one is watching, when they ask, tell them you have a pet mouse called Benjy, that you taught to run cables.
 
  • Like
Likes   Reactions: Klystron, anorlunda and Tom.G
Tom.G said:
"Pulling" is usually done with a "fish tape." This is a ribbon of tempered, springy, Steel that can be pushed thru the conduit. For heavier (or many) wires, as you have, the fish tape is then used to pull a rope thru. The rope is then used to pull the wires.

The photo you show seems to be Aluminium wire. That may work if the conduit is a straight run, but trying to push it around elbows or thru couplings can be a problem, it isn't stiff enough and when it hits an obstacle it stops. Then you try pushing harder and it bends somewhere in the middle and piles up there.

My handy pocket reference says 5 #2 conductors will fit in that conduit, however I have learned not to rely on that reference, it has too many errors. Still, it seems like there is plenty of room. I'm expect the permit folks will flag anything they don't like.

Cheers,
Tom

table 4.png


table 5.png


I read that "To calculate conduit fill:

1. Get the 40% area value from the table corresponding to the type of conduit you're using (Table 4).
2. Get the approximate area value for the size conductors you're using (Table 5).
3. Divide the 40% conduit area by the conductor area, to determine the number of conductors allowed.
NOTE: When calculating conduit fill, if the calculation results in a decimal of 0.8 or larger, you can round to the next whole number.

EXAMPLE:
- 1/2" Schedule 40 PVC 40% fill = 0.114 in².
- 12 AWG THHN conductor = 0.0133 in².
0.114 in² / 0.0133 in² = 8"

1. No problem with that. But let's take the case of AWG 4. In this calculator. AWG 4 corresponds to 21.15 mm^2 cross sectional area. AWG to mm/mm2 | Gauge to mm conversion (rapidtables.com)

But in Table 5. AWG 4 corresponds to 53.16mm^2. There are 2 kinds of area? One cross section of the whole cable. The latter in table 5 is area of what?

2. How long can a 1 1/2 (40mm) PVC conduit still work on fish tape? The conduit length from outside to inside is about 100 feet or 30 meters.

3. If the conduit underground has water inside, how do you think it would affect existing system? Recall many buildings have underground pvc conduits and who knows if many are cracked already.

4. Lastly, AWG 4 can carry 75 A for THHN 75C. If you put 2 AWG 4 pairs from main breaker to inside, the Ampere capacity would become twice, or 150A? Or still 75A? Not that I'd do this. But just thinking how the electrons can traffic themselves and move down 50% each path.

Thank you!
 
Cobul said:
1. No problem with that. But let's take the case of AWG 4. In this calculator. AWG 4 corresponds to 21.15 mm^2 cross sectional area. AWG to mm/mm2 | Gauge to mm conversion (rapidtables.com)

But in Table 5. AWG 4 corresponds to 53.16mm^2. There are 2 kinds of area? One cross section of the whole cable. The latter in table 5 is area of what?
That calculator has a problem. It always shows the same area regaardless of the wire size I enter.

Cobul said:
2. How long can a 1 1/2 (40mm) PVC conduit still work on fish tape? The conduit length from outside to inside is about 100 feet or 30 meters.
Don't know, ask the guy that will be installing it.

Cobul said:
3. If the conduit underground has water inside, how do you think it would affect existing system? Recall many buildings have underground pvc conduits and who knows if many are cracked already.
If you expect it to get wet, consider insulation for underground (direct) burial, if I recall correctly it wil be UG style rather than THHN.

Cobul said:
4. Lastly, AWG 4 can carry 75 A for THHN 75C. If you put 2 AWG 4 pairs from main breaker to inside, the Ampere capacity would become twice, or 150A? Or still 75A? Not that I'd do this. But just thinking how the electrons can traffic themselves and move down 50% each path.
I've seen it done when there is not a wire size made for the current, but a single conductor is cheaper if available.
 
Tom.G said:
That calculator has a problem. It always shows the same area regaardless of the wire size I enter.

Maybe you are using incompatible browser? It always works for me. Let's just use existing table then.

wire-gauge-conversion-mm-to-awg-awg-conversion-table-mm2-www-microfinanceindia-org-49-51886.png


table 5.png


Let's take the case of AWG 4. In the first table or standard you can find anywhere. AWG 4 corresponds to 21.1mm^2 cross sectional area. But in Table 5. AWG 4 corresponds to 53.16mm^2. There are 2 kinds of area? One cross section of the whole cable. The latter in table 5 is area of what?
 

Similar threads

Replies
16
Views
5K
Replies
4
Views
3K
  • · Replies 9 ·
Replies
9
Views
3K
  • · Replies 16 ·
Replies
16
Views
6K
  • · Replies 1 ·
Replies
1
Views
5K
  • · Replies 35 ·
2
Replies
35
Views
11K
  • · Replies 19 ·
Replies
19
Views
13K
  • · Replies 42 ·
2
Replies
42
Views
8K
  • · Replies 1 ·
Replies
1
Views
5K
  • · Replies 19 ·
Replies
19
Views
6K