Insolation, efficiency, and area

Click For Summary
SUMMARY

The discussion centers on calculating the required size of a flat plate collector (FPC) to meet a family's domestic hot water needs in Denver, CO, during March. The calculations indicate that 80 gallons of water must be heated from 45°F to 130°F, resulting in a heat requirement of 56,440 Btu/d. Using the provided insolation value of 2060 Btu/ft²/d and an efficiency of 40%, the calculated collector area is 69 ft². However, the professor marked the answer as incorrect, suggesting a possible miscalculation involving efficiency.

PREREQUISITES
  • Understanding of thermal energy calculations (Q=mcΔT)
  • Knowledge of solar insolation values for specific locations
  • Familiarity with flat plate collector efficiency metrics
  • Basic principles of heat transfer and temperature conversion
NEXT STEPS
  • Research the impact of collector tilt angle on solar energy absorption
  • Learn about variations in insolation values across different months and locations
  • Investigate the effects of collector efficiency on system performance
  • Explore common errors in thermal energy calculations in solar heating systems
USEFUL FOR

Students studying renewable energy systems, engineers designing solar heating solutions, and professionals involved in energy efficiency assessments.

EnergyKitty
Messages
7
Reaction score
0

Homework Statement


What size FPC is needed to supply a family's domestic hot water needs in March in Denver, CO? Assume 80 gallons per day are needed (1gal=8.3 lb.) for the water and that the collector-heat exchanger system has an average efficiency of 40%. The collector tilt angle is equal to latitude.

Homework Equations


Example given in chapter:
Calculate the size collector needed to heat 80 gallons of water per day from 50 deg to 130 deg F in March in Los Angeles. Assume the insolation is 1700 Btu/d/ft^2, and the FPC efficiency is 50%.
Q=mc(change of Temp)
Q= 80gal x 8.3 lb/gal x 1 Btu/lb/deg F x (130-50)deg F = 53,100 Btu/d
The heat available from the FPC will be Q = insolation x area x efficiency
53,100 Btu/d = 1700 Btu/d/ft^2 x area x 0.5
Therefore, the collector area = 62 ft^2

The Attempt at a Solution


Following the example I did:
Insolation in March for Denver, CO is 2060 Btu/ft^2/d (provided in the textbook index)
80 gallons x 8.3 lbs/gal = 664 lbs
mean temp in March in Denver, CO = 45 deg F (provided in index of text)
efficiency = 40%
664 lbs x 1 Btu/lb/deg F x (130 - 45) deg F = 56,440 Btu/d
56,440 Btu/d = 2060 Btu/ft^2/d x area x 0.4 = 69 ft^2

My professor marked it wrong and said it's 56 ft^2, where did I go wrong?
 
Physics news on Phys.org
EnergyKitty said:

Homework Statement


What size FPC is needed to supply a family's domestic hot water needs in March in Denver, CO? Assume 80 gallons per day are needed (1gal=8.3 lb.) for the water and that the collector-heat exchanger system has an average efficiency of 40%. The collector tilt angle is equal to latitude.

Homework Equations


Example given in chapter:
Calculate the size collector needed to heat 80 gallons of water per day from 50 deg to 130 deg F in March in Los Angeles. Assume the insolation is 1700 Btu/d/ft^2, and the FPC efficiency is 50%.
Q=mc(change of Temp)
Q= 80gal x 8.3 lb/gal x 1 Btu/lb/deg F x (130-50)deg F = 53,100 Btu/d
The heat available from the FPC will be Q = insolation x area x efficiency
53,100 Btu/d = 1700 Btu/d/ft^2 x area x 0.5
Therefore, the collector area = 62 ft^2

The Attempt at a Solution


Following the example I did:
Insolation in March for Denver, CO is 2060 Btu/ft^2/d (provided in the textbook index)
80 gallons x 8.3 lbs/gal = 664 lbs
mean temp in March in Denver, CO = 45 deg F (provided in index of text)
efficiency = 40%
664 lbs x 1 Btu/lb/deg F x (130 - 45) deg F = 56,440 Btu/d
56,440 Btu/d = 2060 Btu/ft^2/d x area x 0.4 = 69 ft^2

My professor marked it wrong and said it's 56 ft^2, where did I go wrong?
I see nothing wrong with your calculation. Are you sure the target temperature is still 130F? But my guess is the prof used 50% efficiency by mistake.
 

Similar threads

Replies
3
Views
2K
Replies
2
Views
2K
  • · Replies 21 ·
Replies
21
Views
5K
  • · Replies 3 ·
Replies
3
Views
3K
  • · Replies 1 ·
Replies
1
Views
2K
Replies
1
Views
2K
  • · Replies 1 ·
Replies
1
Views
3K
  • · Replies 5 ·
Replies
5
Views
3K
  • · Replies 5 ·
Replies
5
Views
3K