Is My Understanding of Grounding Transformers Correct?

Click For Summary
SUMMARY

The discussion confirms that the understanding of grounding transformers, specifically wye-delta configurations, is accurate. During normal operation, only a small magnetizing current flows on the wye side due to balanced conditions. In the event of a single-phase to ground fault, zero sequence currents require a return path through the wye-delta grounding transformer, allowing for balanced amp-turns and enabling current flow. Without the delta secondary connection, the grounding transformer would only draw magnetizing current without providing any functional benefits.

PREREQUISITES
  • Understanding of grounding transformers and their configurations
  • Knowledge of zero sequence currents and their implications
  • Familiarity with amp-turn balance in electrical systems
  • Basic principles of Kirchhoff's Voltage Law (KVL)
NEXT STEPS
  • Research the operational principles of grounding transformers in electrical systems
  • Study the effects of single-phase to ground faults on power systems
  • Learn about zero sequence current analysis in grounding systems
  • Explore the design and applications of wye-delta transformer connections
USEFUL FOR

Electrical engineers, power system designers, and professionals involved in grounding system analysis and fault management will benefit from this discussion.

KraakeCrest
Messages
18
Reaction score
2
Hi

Got some questions regarding grounding transformers (wye-delta), or maybe I should write, I need someone to tell me if my understanding is correct.

First, under no fault operation:
Only a small current will flow in the wye side of the grounding transformer, aka magnetizing current. Because, if the system is balanced, no other current will flow in the wye side, because amp-turns must be balanced (except magnetizing current), and since using KVL around the delta loop yields 0 there are no place for any currents in wye to be "amp-turn balanced". Conclusion: Only a small current is flowing in the wye primary side of the grounding transformer during balanced non-fault operation.During single phase to ground fault:
Because of the single phase to ground fault, zero sequence currents arise. For them to flow they require a return path via neutral or ground back to the source, which is provided by the wye-delta grounding transformer. So for zero sequence current to flow as shown in the picture below, the amp-turns on the wye side of the grounding transformer must be balanced by something. And this something is the delta secondary connection, using KVL around the loop with zero sequence induced voltages, yields something different from zero, and hence currents can flow in the closed loop and amp-turns are balanced.

Without this delta secondary and only a wye primary the grounding transformer would not add anything useful and only draw useless magnetizing current, right?

WYE-DELTA
upload_2017-10-3_16-28-21.png
 
Engineering news on Phys.org
Your understanding is correct.
 
Most likely this can only be answered by an "old timer". I am making measurements on an uA709 op amp (metal can). I would like to calculate the frequency rolloff curves (I can measure them). I assume the compensation is via the miller effect. To do the calculations I would need to know the gain of the transistors and the effective resistance seen at the compensation terminals, not including the values I put there. Anyone know those values?

Similar threads

  • · Replies 22 ·
Replies
22
Views
8K
Replies
6
Views
4K
  • · Replies 2 ·
Replies
2
Views
2K
  • · Replies 8 ·
Replies
8
Views
3K
  • · Replies 11 ·
Replies
11
Views
6K
  • · Replies 1 ·
Replies
1
Views
4K
  • · Replies 16 ·
Replies
16
Views
4K
  • · Replies 32 ·
2
Replies
32
Views
4K
Replies
4
Views
3K
Replies
9
Views
2K