jasonyp
- 3
- 0
can anyone tell me how to find the pressure head and residual head?
the Q is depend on which?
the Q is depend on which?
The discussion focuses on optimizing the design of a water supply system for a development of 82 single-storey houses. Key calculations include determining the pressure head, residual head, and flow rate, with a suggested average water demand of 330 gallons per day per household being deemed insufficient. Participants emphasize the importance of using gallons per minute (gpm) for pipe sizing rather than gallons per day (gpd), with a more realistic estimate for peak demand being around 400 gpm. Additionally, the necessity of involving a registered professional engineer in the design process is highlighted due to legal and safety implications.
PREREQUISITESEngineers, architects, developers, and anyone involved in the design and implementation of water supply systems, particularly in residential developments.
Mech_Engineer said:330 gallons per day seems very low for 82 houses (that's an average of 4 gallons per day per house)
Bob S said:Typical suburban indoor water use in the U.S. is 65 gpcd (gallons per capita per day) so a typical house indoor usage for 3 people would be 200 gpd (gallons per day). Including outdoor for garden would easily be 300 gpd. Static head pressure at homes is probably 50 psi (pounds per square inch) minimum to 75 psi maximum. You should check these numbers with local utility. Is this water gravity fed from a water tank, or is this a pressurized system with a pneumatic ballast tank?
russ_watters said:No, I'm pretty sure you mistook gal/min for gal/day... 330 gpd is .22 gpm,
The second task is then to size the pipe. You need the flow rate you just calculated (perhaps you already have it if you just got the units wrong - 330 gpm sounds about right),
You are right. If a worst case scenario was a simultaneous 5 gpm per house, then the total demand would be over 400 gpm for the 82 houses.russ_watters said:It is easy to envision real-world scenarios where an 82 house development could exceed 100 or 200 gpm. There are specific times during the day when usage is much higher than other times. From 5:30-7:30 am, for example(and peaking from 6-7), a very high fraction of the houses will have multiple people taking showers at a flow rate of 2.5 gpm per shower for the length of the shower. In addition, there will be several toilet flushes per house at 2.5 gal/flush and faucets running for a few minutes at a time at 1gpm.