Overvoltage Protection

Click For Summary
SUMMARY

The discussion centers on overvoltage protection in a three-phase four-wire system with 380V LL and 220V LN voltages. When the neutral conductor is disconnected, the 230V LN can spike to 380V LL, potentially damaging equipment. An overvoltage protector rated for up to 300V is being installed, but the maximum tolerable voltage before damage remains unclear. Effective protection strategies include using voltage monitoring relays and understanding the implications of TN-C and TN-S systems for neutral break protection.

PREREQUISITES
  • Understanding of three-phase electrical systems
  • Knowledge of TN-C and TN-S grounding systems
  • Familiarity with overvoltage protection devices and their specifications
  • Experience with voltage monitoring relays and circuit breakers
NEXT STEPS
  • Research the specifications and datasheets of overvoltage protection devices
  • Learn about the operation and installation of voltage monitoring relays
  • Investigate the differences between TN-C and TN-S grounding systems
  • Explore the use of surge protection devices and their effectiveness in various scenarios
USEFUL FOR

Electrical engineers, technicians involved in power distribution, and professionals designing electrical installations who need to ensure reliable overvoltage protection and neutral break safety.

Hfuda
Messages
1
Reaction score
0
A three-phase four-wire system has 380V LL, 220V LN voltages. A number of single phase 220V loads are connected between each phase and neutral. If the neural gets accidentally disconnected from the source, the 230V LN jumps to 380V LL. I am installing an overvoltage protector that can protect up to 300V. However, I am not sure what is the maximum voltage that the input terminals can accept without damage to the protector device? The specs do not provide an answer other than the fact that overvoltage setting can range from 270V to 300V. This implies that it can tolerate voltages above that. But to what level? And for how long?
 
Engineering news on Phys.org
Welcome to PF.

What power levels are we talking about here? What are the main breakers rated at for this 3-phase system? Can you post a link to the protection device datasheet?
 
It's likely the energy or power dissipated in the OVP device that causes their failure. Hence @berkeman's question about upstream protective devices. Voltage is only part of the data you need. Think of this as a system, not a single device.
 
I am well aware of this problem. I design such electrical installations. If you use the TN-C system (combined working and protective neutral, that is, PEN), the protection against neutral breakage is performed as follows: 1) reliable re-grounding of the neutral conductor (PEN conductor) is performed at the input to the electrical switch cabinet; 2) a voltage monitoring relay is used, which controls the release of the input circuit breaker. If you use the TN-S system (separated operating and protective neutral, that is, N and PE), neutral break protection is performed only by using a voltage monitoring relay that controls the release of the input circuit breaker. The N wire is not re-grounded, the PE wire is re-grounded. The control circuit with the voltage monitoring relay is designed so that the input circuit breaker is switched off if the relay is defective. This relay protection circuit ensures voltage control in case of any voltage deviations.
 
  • Like
Likes   Reactions: DaveE
The use of surge arresters or surge protection devices to protect against neutral conductor breakage is unknown to me personally. The fact is that such devices are used for large overvoltages, for example, a lightning strike in an electrical line. Such devices practically do not respond to an increase in voltage from 220V to 380V, since they have a nonlinear characteristic of the dependence of resistance on voltage.
 
  • Like
Likes   Reactions: DaveE and berkeman
Ivan Nikiforov said:
The use of surge arresters or surge protection devices to protect against neutral conductor breakage is unknown to me personally. The fact is that such devices are used for large overvoltages, for example, a lightning strike in an electrical line. Such devices practically do not respond to an increase in voltage from 220V to 380V, since they have a nonlinear characteristic of the dependence of resistance on voltage.
Yes, this. Devices that can clamp voltages that accurately tend to be small, like TVS diodes, which can't absorb much energy. You could monitor the voltages and trip upstream circuit breakers, but this is complex and expensive for an unusual failure mode. It may also not be fast enough to save the downstream equipment anyway. Electrical distribution, done right, is usually pretty reliable, mechanically. If a neutral is broken, someone probably did it sort of on purpose. You can't protect against everything.
 
  • Like
Likes   Reactions: Ivan Nikiforov, Averagesupernova and berkeman

Similar threads

  • · Replies 3 ·
Replies
3
Views
1K
Replies
25
Views
3K
  • · Replies 4 ·
Replies
4
Views
2K
Replies
2
Views
2K
Replies
20
Views
3K
Replies
1
Views
3K
  • · Replies 7 ·
Replies
7
Views
5K
  • · Replies 19 ·
Replies
19
Views
5K
  • · Replies 13 ·
Replies
13
Views
5K
  • · Replies 4 ·
Replies
4
Views
6K