220V Split Phase Generator for International Use

Click For Summary

Discussion Overview

The discussion centers around converting a 240/120V 60Hz generator for use in China, which operates on a 50Hz system. Participants explore the implications of adjusting the generator's frequency and voltage, particularly regarding safety and compatibility with devices designed for line-to-neutral power systems.

Discussion Character

  • Technical explanation
  • Debate/contested
  • Experimental/applied

Main Points Raised

  • One participant suggests that slowing down the engine and adjusting the voltage regulator can achieve the necessary 50Hz and 220V output for use in China.
  • Another participant expresses concern about the safety implications of using a generator where both lines are hot, particularly if the neutral is tied to the chassis.
  • A third participant raises the issue of devices that may have their neutral tied to ground, questioning how this would interact with the generator's output and whether it would trip breakers.
  • One participant inquires about the application of the power, specifically for diesel burning heaters, and mentions the need for compatibility with shore power.
  • There is a mention of contacting the manufacturer for guidance, but responses have been limited and unhelpful.

Areas of Agreement / Disagreement

Participants generally agree on the potential safety issues related to the generator's configuration and the implications for devices designed for line-to-neutral power. However, there is no consensus on the best approach to ensure safety and compatibility.

Contextual Notes

Participants note the uncertainty regarding the commonality of devices with neutral tied to ground and the implications for electric codes. There is also a lack of clarity on the manufacturer's knowledge of international power systems.

Who May Find This Useful

This discussion may be useful for individuals involved in generator modifications for international use, particularly those concerned with safety and compatibility of electrical systems across different regions.

jdoyle3
Messages
3
Reaction score
0
I am trying to convert a 240/120V 60Hz genset for international use, specifically for China at the moment. I need 50 Hz, which I can achieve by slowing the engine down and making the necessary changes to the voltage regulator in the generator. I can also adjust my Line-to-Line voltage to the necessary 220V. I am under the impression that I can neglect the neutral terminal in the generator and only use the two lines to get my 220V.

From what I understand, the power they would typically use in China (or Europe, etc.) is 220V (or 230V) measured line to neutral. Even though I am using line-to-line, is there a difference to devices being powered? I know that voltage is a measure of the potential difference across two wires which is why I can achieve the correct voltage, but I now need double-pole breakers and I don't have a true neutral in the system. And I'm not sure if I need to bond the neutral terminal within the generator to ground, or leave it floating.

How will this affect devices that are used to the line-to-neutral power? And is what I am trying to do acceptable and safe? Any help would be greatly appreciated.
 
Engineering news on Phys.org
As far as frequency is concerned it will not be an issue for some things like incandescent lights, resistive heating elements and universal motors such as portable drills and some power tools with brushes. However, I have a concern with the fact that the generator may have it's neutral tied to the chassis. So both sides of the 240 volt line are hot and I assume equipment in this country is typically not set up for this. Be very careful here. I see this as a safety issue.
 
I agree, I am very concerned about a potential safety issue. I believe the issue would be if a load internally had its neutral tied to ground. I don't know how common that is, or if that is against any and all electric codes. But then again, if that created a short, my double pole breakers would open the circuit to protect it.

I suppose that would mean it was safe, but the generator would not be able to power that load because it would trip the breaker every time.
 
jdoyle3 said:
I am trying to convert a 240/120V 60Hz genset for international use, specifically for China at the moment.
Welcome to the PF.

What will be the application for this power? Can you consult the manufacturer of the motor/generator to see if they are familiar with China's power system and regulations?
 
The power is for diesel burning heaters that we provide with the genset. But one of our selling features is that they can power the heaters with shore power instead of the genset. Otherwise we could leave the genset at 60 Hz. We are trying to set it up to run the same type of power that would normally be available.

I have contacted the manufacturer and sales rep, but so far they are about as knowledgeable as I am. We are trying to find a solution, but it is moving slow so far.
 

Similar threads

  • · Replies 5 ·
Replies
5
Views
2K
  • · Replies 41 ·
2
Replies
41
Views
19K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 3 ·
Replies
3
Views
1K
Replies
15
Views
2K
Replies
8
Views
3K
  • · Replies 37 ·
2
Replies
37
Views
8K
  • · Replies 5 ·
Replies
5
Views
3K
Replies
61
Views
10K
  • · Replies 5 ·
Replies
5
Views
6K