Parallel fans in same ducting system

  • Thread starter Thread starter KingMan
  • Start date Start date
  • Tags Tags
    Parallel System
Join the discussion
Ask a follow-up here, or get your own question answered by working scientists, mathematicians and engineers — people, not an autocomplete.
Real named experts · corrections over time · the nuance an AI answer skips
4 replies · 3K views
KingMan
Messages
2
Reaction score
0
Currently, I have a mv fan ducted system with two fans in parallel, one duty and standby (each with 7000cmh).
If I were to run both fans at the same time, do I get 14000cmh in total?
 
Physics news on Phys.org
Welcome to PF.
KingMan said:
If I were to run both fans at the same time, do I get 14000cmh in total?
No. You must study the flow versus pressure relationship first.
The two fans will only double the flow if there is no increase in pressure when the two fans are operated together.
 
Reply
  • Like
Likes   Reactions: russ_watters
...if there is an increase in pressure due to having a fixed/the same ducting system the flow increase may be somewhere near 1.4x. I say "may be somewhere near" because fan performance follows a characteristic curve that is different for every fan, and may stray from the ideal.