Power Factor Correction for a 230V Single Phase Lighting Installation
13 replies · 4K views · last reply
topcat123
The problem statement
Using the nomogram of FIGURE 10, calculate the size of
capacitor bank to give a final power factor of 0.95 for a single phase,
230 V, 50 Hz lighting installation which has a load current of 17.5 A and
operates at 0.8 pf.
The nonogram gives a value k = 0.44
Relevant equations
Qc = Pk
Xc = 1/2pifC
P = VI
The attempt at a solution
I have come up with two ways but i think the first is wrong as the current though the capasitor (If in parrallel) will not be the same as the load current.
Attempt 1
P = 230 x 17.5 = 4025W
Qc = 4.03 x 0.44 = 1.77 KVAr
P = I^2 x Xc
Xc = P/I^2 = 1.77 x 1000 x 17.5^2 = 5.783Ω
so C would come out at 550μF (as I said I think this is wrong)
Attempt 2
Power still = 4025W and Qc = 1.77 KVAr
but P = V^2/Xc so Xc = V^2/P
Xc = 230^2 x 1.77 x 1000 = 18.38Ω
so C would work out at 173μF
Just a bit of guidance would be appreciated.
Hi topcat123, Welcome to Physics Forums.
While I'm not that familiar with the usual methodologies used in Power Systems (like the nomogram you mention), I can suggest a more generic approach.
Since you are given the current magnitude and the power factor you can write the current phasor (complex or polar form). Knowing the voltage too, you can write the impedance or admittance of the load (Y = 1/Z = I/V).
Recalling that admittances add in parallel, you can find the admittance (of a capacitor) to add in order to bring the pf from 0.8 to 0.95; It's just a matter of reducing the imaginary component of the total admittance to the desired value, and capacitors have negative imaginary admittance...
rude man said:
Ahem ... :smile:
Hah! Well caught. Dunno why that brain cell fired :smile:
So draw a phase diagram for 0.8 pf.
Work out the restive current.
Overlay the new 0.95 pf and work out the change in the reactive component.
from that i con work out the capacitor size.
Doing it this way i get 123μF
before i got 173μF
before i got 173μF
Can you show more of your work?
I think it would be better to work with admittances, since they add in parallel (presumably the capacitor bank will be placed in parallel with the load). I'm seeing a smaller value of capacitance for the result.
Ok
Z=V/I = 230/17.5 = 13.14Ω
cos θ = 0.8 so R = 0.8 x 13.14 = 10.512Ω
Xl = √Z^2 - R^2 = 62.16Ω
New pf = 0.95 = cos θ
θ = 18.19°
R tan 18.19° = Xl-Xc =3.455Ω
There for Xc = 58.71Ω
C=1/2πfXc = 54.22μF
Check your calculation of Xl. 62.16Ω looks too large.
Remember that impedances in parallel don't add algebraically. Admittances (1/Z) add.
yes Xl should be 7.88Ω forgot to √it.
So Xl-Xc = 3.455Ω
(1/3.455)-(1/7.88) = 1/Xc
Xc = 6.152Ω
C=1/2πfXc = 1/(2π x 50 x 6.152) = 0.000517F
Is this better?
So Xl-Xc = 3.455Ω
Xc = 6.152Ω
Is this better?
One problem, while it is true that admittance is the inverse of impedance, Y = 1/Z, it is not true that the imaginary part of the admittance is equal to the inverse of the imaginary part of the impedance. That is, Im(Y) ≠ 1/Im(Z).
Start by finding Y = 1/Z. Then work with its components; you want to reduce its polar angle in the same fashion that you're trying to do for the impedance.
Z = V/I = 230/17.5 = 13.14Ω
Y = 1/Z = 0.076
G = Y cosθ = 0.076 x 0.8 = 0.061
Bl =√z^2 - G^2 = 0.076^2 - 0.061^2 = 0.045
new pf 0.95
cosθ = 0.95 θ = 18.19°
Bl-Bc = G tan 18.19° = 0.020
Bc = 0.025
Xc = 1/Bc = 40Ω
which makes C = 79.5μF
Hope i have it this time...
That looks MUCH better! I think if you hang on to a few more digits of accuracy for intermediate values your final result will be closer to 81.6 μF.
Cheers!
topcat123 said:
Thanks for the help gneill.
No worries, I'm glad to help!