Power Factor Questions in AC Circuits

  • Thread starter Thread starter daredevil
  • Start date Start date
  • Tags Tags
    Power Power factor
Click For Summary
SUMMARY

In AC circuits, energy is not consumed by capacitors and inductors, yet they affect the power factor, which is crucial for efficient power delivery. Power companies charge for low power factors because generator and wire capacities are based on amperage rather than wattage. While real power correlates with fuel consumption in power plants, apparent power is necessary to maintain system stability. Correcting phase shifts typically involves adding capacitors, and distributed generation can help manage power factor by operating out of phase.

PREREQUISITES
  • Understanding of AC circuit fundamentals
  • Knowledge of power factor and its implications
  • Familiarity with real power vs. apparent power
  • Basic concepts of distributed generation and VARs
NEXT STEPS
  • Research power factor correction techniques using capacitors
  • Learn about distributed generation and its impact on power factor
  • Explore the relationship between amperage and wire sizing in electrical systems
  • Study the role of VARs in power systems and how they are sold to power companies
USEFUL FOR

Electrical engineers, power system analysts, and anyone involved in optimizing AC circuit performance and power factor management.

daredevil
Messages
12
Reaction score
0
In AC circuits, it seems that there is no energy used for capacitors and inductors.

I was wondering how is the energy used causing it to increase and decrease the power factor?. And also, why does the power provider have to supply power(apparent power) for something that is ultimately not even used

Thanks..
 
Engineering news on Phys.org
Apparent power is not supplied as real power by the generator. The reason the power company gets annoyed at (and charges you for) low power factor is that the capacity of generators and wires is based on amperage, not wattage.
 
Thankss..

So, aren't there are generators made based on wattage??.. or can we ignore the apparent power and use a generator to supply for the real power only?

And also when the current returns to distribution point.. different cables with be with different power factors.. so will there be any problem caused by that
 
Pwr comes to us in three phases, each 120 degrees out of phase with the next. We derive pwr by flowing current between the phases. If the phases change from their ideal 120 degrees, you still have full pwr flowing thru each phase, which is what we get charged for. But we now have slightly less voltage between the phases at each instant in time, so we get less usable pwr between the phases.

Correcting this phase shift normally means adding capacitors. But with expanded use of distributed generation; we can run the DG generators out of phase in the opposite direction to help correct the PF on the grid. This is how generator owners sell VARS to the power company.
 
Last edited:
daredevil said:
Thankss..

So, aren't there are generators made based on wattage??.. or can we ignore the apparent power and use a generator to supply for the real power only?
The real power is "real" in the sense that it directly relates to how much fuel the power plant burns. That's why it is the main component of a commercial bill. But how hot a wire or generator gets is a function of amperage, so the worse the power factor the higher the amperage so the larger the wires and generator need to be or the higher the losses will be.
 

Similar threads

  • · Replies 8 ·
Replies
8
Views
2K
  • · Replies 2 ·
Replies
2
Views
1K
Replies
12
Views
3K
Replies
8
Views
2K
  • · Replies 14 ·
Replies
14
Views
2K
  • · Replies 3 ·
Replies
3
Views
3K
Replies
11
Views
2K
Replies
6
Views
4K
  • · Replies 3 ·
Replies
3
Views
2K
  • · Replies 8 ·
Replies
8
Views
3K