Pressure Testing (furnace installation leak)

Click For Summary

Discussion Overview

The discussion revolves around the pressure testing of a propane furnace installation, focusing on the behavior of pressure readings over time and the potential causes of pressure loss. Participants explore various factors that may influence the pressure readings, including temperature fluctuations and the characteristics of the gas valve.

Discussion Character

  • Exploratory
  • Technical explanation
  • Debate/contested

Main Points Raised

  • One participant reports a pressure loss from 10" WC to 0" WC over 11 hours, suggesting a possible leak in the electric gas valve despite no detectable propane odor.
  • Another participant questions whether ambient air temperature remains constant during the test and if any part of the piping system is affected by external heating or cooling sources.
  • A third participant raises the issue of the directional nature of the electric valve, suggesting that improper installation could lead to leaks.
  • A later reply indicates that fluctuations in ambient temperature and barometric pressure may have contributed to the observed pressure changes, leading to the conclusion that there was no actual leak.
  • The initial poster reflects on the impact of external factors, such as heat from a black pipe and changing weather conditions, on the manometer readings.

Areas of Agreement / Disagreement

Participants generally agree that external factors, such as temperature and barometric pressure, can affect pressure readings. However, there is no consensus on the specific contributions of these factors to the pressure loss observed in the initial testing.

Contextual Notes

Limitations include the dependence on ambient temperature conditions and the potential influence of external heating or cooling sources on the pressure readings. The discussion does not resolve the exact relationship between the gas valve specifications and the observed pressure loss.

CosmicDriftwood
Messages
2
Reaction score
0
Chasing a ghost perhaps but in the process of pressure testing a simple propane furnace installation I installed a water Column pressure gauge. Over a period of 11 hours the pressure gauge reading will go from 10" WC to 0" WC. In the course of trying to understand this I installed a manometer in conjunction with the pressure gauge. I should add that this furnace is new and has never be used beyond an initial checkout.

Extensive testing shows that with an initial test pressure of 11" WC the rate of pressure loss is approximate 0.5" WC/hour. Exhaustive soap bubble testing of the short run of pipe and six fittings between the manual shut off valve and the furnace electric gas valve shows no leaks. So that suggest the the gas valve is leaking either through and/or from the valve body. I will say that there has never been a hint of propane odor.

The phenomenon that I need help with understanding it that after 15 hours or so with the test in progress and having been pressured to 10" - 12" WC the manometer will show a negative pressure of -3" WC -. This is a U-Tube manometer and is open on one side to atmosphere. So If indeed there is a leak through the electric gas valve - since all piping connections are tight, then the -3" WC is the difference between atmospheric pressure and the pressure inside of the piping and electric gas valve. I should add that the outlet side of the electric gas valve is always at atmosphere. It really looks like that there is a 3" vacuum relative to atmosphere right? But how can this be since the system will go to zero pressure, because of this "ghost" leak and then start to show negative (vacuum)? Nature abhors a vacuum so if there is a leak then the manometer should go to zero and stay there right?

The ANSI standard for electric gas valves allows for 235 cc/hour leakage passing through the valve and 200 cc/hour out of the valve for a total of 435 cc/hours. Relatively speaking I can't get a handle on what that means in terms of pressure loss. With a base pressure of 11" WC at an ambient temperature of 60 F; I'm trying to figure out of this valve is within spec.

Any help and/or advice will be appreciated. Thanks...
 
Engineering news on Phys.org
The first questions that come to mind is whether or not the ambient air temperature is constant at the beginning and the end of the test and if any part of the piping system, including attached piping and equipment exposed to radiant or conductive heating or cooling during any period of the test from the sun or another source such as a nearby furnace?
 
  • Like
Likes   Reactions: CosmicDriftwood and CWatters
+1 on the temperature issue.

Is the electric valve directional? Some valves will appear to work but leak if installed the wrong way around.
 
JBA said:
The first questions that come to mind is whether or not the ambient air temperature is constant at the beginning and the end of the test and if any part of the piping system, including attached piping and equipment exposed to radiant or conductive heating or cooling during any period of the test from the sun or another source such as a nearby furnace?

Thanks JBA for you your reply. Your comment was right on track as it turned out. Wish that I had gotten back to checking for replies to my post sooner than I did because I concluded that I have indeed been chasing a ghost and that ghost had a lot to do with the "attached piping and equipment exposed to radiant or conductive heating or cooling during any period of the test from the sun or another source" as you indicated in your reply. The ambient temperature in the immediate area was fluctuating to some degree but the real variable was the heat sink effect from the through the wall 3/4" black pipe coming from the outside of the building. That effect in conjunction with the barometric pressure fluctuation due to a couple of storm fronts and was impacting my manometer by as much as 3" WC. So sometime on Friday I concluded that those two effects were creating my "ghost".

My test port for the manometer connection and the WC gauge was in line after a 1/2" valve that when closed would isolate both of them from the rest of the piping. So this morning the outside ambient temperature was 28 F and the ambient temp inside the building was 48 F, and the 1/2" valve had been closed off for 48 hours. The manometer read a negative 9" WC (that's a -9"). So you nailed it and for me this ghost said "boo". There's no leak.
 

Similar threads

  • · Replies 3 ·
Replies
3
Views
1K
  • · Replies 1 ·
Replies
1
Views
3K
  • · Replies 20 ·
Replies
20
Views
11K
  • · Replies 8 ·
Replies
8
Views
8K
  • · Replies 6 ·
Replies
6
Views
3K
  • · Replies 19 ·
Replies
19
Views
6K
Replies
3
Views
4K
  • · Replies 11 ·
Replies
11
Views
4K
  • · Replies 4 ·
Replies
4
Views
9K
Replies
2
Views
4K