Pump pressure and static height in central heating

Click For Summary
SUMMARY

In central heating systems, the pressure on the suction side of the circulation pump must be managed to prevent cavitation, which can damage the pump impeller. The common rule of thumb stating that suction pressure should equal the static height of the system is an oversimplification. In practice, hydronic systems typically do not face NPSH issues, except in high-performance industrial applications. Accurate pressure calculations involve assessing the pump curve, line losses, and static pressure to ensure optimal performance.

PREREQUISITES
  • Understanding of centrifugal pump operation and cavitation
  • Knowledge of hydronic heating system design
  • Familiarity with pump curves and pressure calculations
  • Basic principles of fluid dynamics in closed systems
NEXT STEPS
  • Study centrifugal pump cavitation and its effects on performance
  • Learn how to calculate NPSH for various pump models
  • Research methods for calculating head loss in hydronic systems
  • Explore pressure management techniques in high-rise building heating systems
USEFUL FOR

Heating engineers, HVAC technicians, and anyone involved in the design or maintenance of hydronic heating systems will benefit from this discussion.

TSN79
Messages
422
Reaction score
0
I was told recently that in a central heating system, the pressure on the suction side of the circulation pump should be at least equal to the static height of the system. I've never heard this stated before, and I don't intuitively get why this should be the case. If there is actually something to it, maybe someone here can explain it to me?
 
Engineering news on Phys.org
All centrifugal pumps have a minimum NPSH (net positive suction head). If the absolute pressure at the suction is too low, it cavitates. Cavitation is bad, it destroys the impeller.

What the OP was told is an oversimplified rule of thumb that avoids the need to find / calculate the pressure at the pump suction, the (worst case) vapor pressure at the pump suction, and the minimum NPSH for that pump.
 
  • Like
Likes   Reactions: Asymptotic
Doesnt this mean that in a vented system the pump must be at the lowest point? In my vented heating system I have circulating pumps on both floors. The pressure at the input to the top floor pump is therefore about half the max static height.
 
With positive static pressure at the pump suction (suction is below the vent), water temperature below boiling, reasonably low line losses between the pump suction and the vent, and a typical hydronic circulating pump, you should be good.

Most hydronic systems do not have NPSH problems. It's the high performance industrial applications that need to be checked, especially systems with high line losses in the pump suction line.
 
TSN79 said:
I was told recently that in a central heating system, the pressure on the suction side of the circulation pump should be at least equal to the static height of the system.
That doesn't make any sense. The only way it can even be true (for a basement-located system...) is when the pump is off; the pressure on both sides is equal to the stack height. When you turn the pump on, the pressure on the suction side goes down!

I think you must have heard wrong.
 
Thanks for the feedback guys. In addition I have a related question regarding the pump pressure. As mentioned, when the pump starts, the pressure on the suction side decreases, and increases on the pressure side. I can calculate the loss through the entire loop, but is there a way to predict exactly how much it will decrease and increase on the suction and pressure side?
 
The exact calculation is system dependent, but in general the procedure is:
1) Find the pressure difference across the pump from the pump curve and the calculated flow rate.
2) Calculate the line loss between a point of known pressure and the nearest side (suction or discharge) of the pump. Typical points of known pressure are an atmospheric vent or an expansion tank.
3) From (2), find the pressure on one side of the pump.
4) From (3) and (1), find the pressure on the other side of the pump.
5) Compare to the static pressure at the pump (pressure with pump off).
 
  • Like
Likes   Reactions: Asymptotic and russ_watters
I suddenly became unsure of a question I was previously sure about :P

Say a closed system has a height of 10 meters. When the pump is off one can observe a pressure difference of 1 bar between the top and bottom of the system. Will this difference stay constant also when the pump is started? I'm quite sure it does not and that I only need to calculate the pipe's head loss as if it was a horizontal piee of pipe, but for some reason I sudden became unsure of this...
 
Three steps:
1) Calculate head loss while ignoring gravity.
2) Calculate static head at zero flow.
3) Add the two together.

Most hydronic heating systems operate at 10 to 20 PSI, most potable water systems are at 40 to 50 PSI. This makes for challenges in taller buildings.
 

Similar threads

  • · Replies 2 ·
Replies
2
Views
3K
Replies
1
Views
934
  • · Replies 1 ·
Replies
1
Views
3K
  • · Replies 15 ·
Replies
15
Views
4K
  • · Replies 7 ·
Replies
7
Views
5K
  • · Replies 6 ·
Replies
6
Views
24K
Replies
8
Views
2K
  • · Replies 3 ·
Replies
3
Views
2K
  • · Replies 16 ·
Replies
16
Views
3K
  • · Replies 2 ·
Replies
2
Views
2K