Rate of energy dissipated by a power transmission line

Click For Summary
The discussion focuses on calculating the energy dissipated by a power transmission line carrying 400A at 765 kV with a resistance of 29 μΩ/m over 800 km. The correct power dissipation is determined to be 3.7 MW using the formula P = IV. Participants clarify that the equation P = V^2 / R cannot be used without knowing the specific voltage drop across the line. The calculations confirm that the answer is option D, 3.7 MW, highlighting the importance of using the correct parameters for power loss calculations. Understanding the relationship between current, resistance, and power is essential in this context.
hidemi
Messages
206
Reaction score
36
Homework Statement
A power transmission line carries 400A of current at a voltage of 765 kV. If the line has a resistance of 29 μΩ/m, what is the rate at which energy is being dissipated in 800 km of line?

a.) 0 W
b.) 3.7 kW
c.) 310 kW
d.) 3.7 MW
e.) 310 MW

The answer is D.
Relevant Equations
Power = V^2/R = I^2*R
VR = IR
= 400 [ 29*10^-6 * 800 * 10^3 ]
= 9280

P = IV
= 400*9280
= 3.7 MW

I was able to calculate the correct answer from the above, but why can't I use the equation P= V^2 / R?
 
Physics news on Phys.org
hidemi said:
VR = IR

I was able to calculate the correct answer from the above, but why can't I use the equation P= V^2 / R?
You mean V=IR.

What voltage did you use in V^2/R? If 765kV, what two points is that the voltage difference for?
 
hidemi said:
Homework Statement:: A power transmission line carries 400A of current at a voltage of 765 kV. If the line has a resistance of 29 μΩ/m, what is the rate at which energy is being dissipated in 800 km of line?

a.) 0 W
b.) 3.7 kW
c.) 310 kW
d.) 3.7 MW
e.) 310 MW

The answer is D.
Relevant Equations:: Power = V^2/R = I^2*R

I was able to calculate the correct answer from the above, but why can't I use the equation P= V^2 / R?
Because you weren't given the voltage drop along the wires. You were given the current I and the resistance -- that is enough to calculate the power loss along the wire.
 
Thank you all.
 
If have close pipe system with water inside pressurized at P1= 200 000Pa absolute, density 1000kg/m3, wider pipe diameter=2cm, contraction pipe diameter=1.49cm, that is contraction area ratio A1/A2=1.8 a) If water is stationary(pump OFF) and if I drill a hole anywhere at pipe, water will leak out, because pressure(200kPa) inside is higher than atmospheric pressure (101 325Pa). b)If I turn on pump and water start flowing with with v1=10m/s in A1 wider section, from Bernoulli equation I...

Similar threads

  • · Replies 9 ·
Replies
9
Views
2K
  • · Replies 2 ·
Replies
2
Views
2K
  • · Replies 2 ·
Replies
2
Views
922
  • · Replies 12 ·
Replies
12
Views
3K
Replies
6
Views
1K
  • · Replies 20 ·
Replies
20
Views
11K
Replies
6
Views
2K
  • · Replies 4 ·
Replies
4
Views
2K
  • · Replies 14 ·
Replies
14
Views
3K
  • · Replies 8 ·
Replies
8
Views
2K