Discussion Overview
The discussion revolves around the integration of a Current Transformer (CT) with a PLC analog input card and an analog meter. Participants explore the feasibility of connecting both measuring devices to the CT's secondary output without removing the existing analog meter. The conversation includes technical considerations regarding wiring, calibration, and the implications of using different types of shunt resistors.
Discussion Character
- Technical explanation
- Debate/contested
- Mathematical reasoning
Main Points Raised
- One participant inquires about connecting both the analog meter and the PLC input card to the same point on the CT secondary.
- Another suggests using a millivolt input Action Pak and utilizing the existing meter as a shunt, noting potential voltage levels.
- It is emphasized that the new shunt resistance of 0.1 ohm should be wired in series with the old analog meter and the CT secondary to ensure the same current flows through both systems.
- Concerns are raised about operating a CT with an open circuit output, stressing the need for careful disconnection of the new meter without removing the shunt.
- Participants express a need for a connection diagram to clarify the series resistance connection with the analog meter.
- Different approaches are presented, including connecting a high impedance millivolt transducer in parallel with the existing meter or using a 0.1 ohm AC current transducer in series.
- One participant shares insights about potential issues with using a moving iron meter as a shunt, highlighting temperature effects on resistance and suggesting the new shunt be wired in series instead.
- There is a call for more information about the existing meter to ensure proper integration and avoid design errors.
Areas of Agreement / Disagreement
Participants present multiple competing views on the best approach to integrate the measuring devices, and there is no consensus on a single method. The discussion remains unresolved regarding the optimal configuration and potential issues.
Contextual Notes
Participants note the importance of calibration after modifications and the potential impact of temperature variations on resistance in the context of using different types of meters and shunts.