Summation of kVA and kVAR with Different Power Factors

  • Thread starter Thread starter traderza
  • Start date Start date
Click For Summary

Discussion Overview

The discussion revolves around the summation of kVA and kVAR readings from two transformers with different power factors. Participants explore how to calculate total kVA and kVAR for a facility based on measurements from smart meters, addressing both theoretical and practical aspects of power measurement in electrical systems.

Discussion Character

  • Technical explanation
  • Conceptual clarification
  • Debate/contested
  • Mathematical reasoning

Main Points Raised

  • One participant notes that total kW can be summed arithmetically, but questions how to sum kVA and kVAR due to differing power factors.
  • Another participant explains that kVA is the vectorial summation of kVAR and kW, emphasizing the importance of phase relationships in the calculations.
  • It is mentioned that to add kVA or kVAR, assumptions must be made regarding the voltages being the same and the phase of the current being identical.
  • A participant expresses uncertainty about the kVA summation process, suggesting it may not be a simple arithmetic addition.
  • Further clarification is provided that kW and kVAR can be summed independently since they are orthogonal, leading to a formula for calculating total kVA.
  • Participants discuss the implications of having different combinations of inductive and resistive loads without knowing the phase difference between the two feeders.

Areas of Agreement / Disagreement

Participants generally agree on the need for certain assumptions when summing kVA and kVAR, but there remains uncertainty regarding the specific conditions under which these sums can be accurately calculated. Multiple viewpoints on the methodology exist without a clear consensus.

Contextual Notes

Limitations include the lack of information on phase differences between the two feeders, which affects the ability to accurately sum kVA and kVAR. The discussion also highlights the dependency on consistent measurements across different parameters.

Who May Find This Useful

This discussion may be useful for electrical engineers, technicians, and students interested in power measurement, electrical systems, and the complexities of calculating apparent and reactive power in facilities with multiple transformers.

traderza
Messages
5
Reaction score
0
TL;DR
I need the formula for each of these summations please
I am measuring the incoming power from 2 transformers using smart meters.

The client wants to know the total kVA and total kVAR of his facility

I know that the total kW is a simple arithmetic sum but I don't know how to summate kVA and kVAR because of the different power factors.

Can anyone help please?
 
Engineering news on Phys.org
Factor (P.F.) is the ratio of Working Power to Apparent Power.
KVAR is reactive power. The power of your transformer uses to produce magnetizing flux.
KVA is apparent power and that is Vectorial Summation of KVAR and KW.
KW is working power. The power that performs useful work.
I like the beer and analogy.
photo_1693218226698.png
 

Attachments

  • Like
Likes   Reactions: CalcNerd, nsaspook and russ_watters
Delta Prime said:
Factor (P.F.) is the ratio of Working Power to Apparent Power.
KVAR is reactive power. The power of your transformer uses to produce magnetizing flux.
KVA is apparent power and that is Vectorial Summation of KVAR and KW.
KW is working power. The power that performs useful work.
I like the beer and analogy.
View attachment 331125
Thanks for the reply and the thirsty analogy! My question is; how do I summate the two kVA readings to provide a composite total kVA for the facility in question?
 
traderza said:
I know that the total kW is a simple arithmetic sum but I don't know how to summate kVA and kVAR because of the different power factors.
kVA is the product of average voltage and in-phase current.
kVAR is the product of average voltage and quadrature current.

If supply 1 and 2 are at the same voltage ...
kW1 + kW2 = kW total.
kVA1 + kVA2 = kVA total.
kVAR1 + kVAR2 = kVAR total.
But that assumes the phase of the current through the two meters is the same.
 
Many thanks for that. I was under the impression that the kVA summation was not a simple arithmetic addition but I was wrong clearly.
 
traderza said:
Many thanks for that. I was under the impression that the kVA summation was not a simple arithmetic addition but I was wrong clearly.
You were not wrong. To add the VA or VAR you must assume that:
1. The voltages are the same, (or you must compute and add the currents).
2. The phase of the current through the two meters is identical.

Imagine two independent meters, both reading 1 kVA. If meter #2, had 180 degree phase current with reference to meter #1, the currents would cancel to zero kVA.
 
  • Like
Likes   Reactions: CalcNerd
Baluncore said:
You were not wrong. To add the VA or VAR you must assume that:
1. The voltages are the same, (or you must compute and add the currents).
2. The phase of the current through the two meters is identical.

Imagine two independent meters, both reading 1 kVA. If meter #2, had 180 degree phase current with reference to meter #1, the currents would cancel to zero kVA.
Thanks for the reply.

The two feeders will be supplying different combinations of inductive and resistive loads but i have no way of knowing the phase difference between the two.

The parameters I can measure for each feeder are:

Volts per phase
Amps per phase
kVA
kVAR
kW
Power Factor

Given these are what I have to work with, how do I calculate the total kVA and kVAR for the facility
 
traderza said:
Given these are what I have to work with, how do I calculate the total kVA and kVAR for the facility
You have a right angle triangle. kW2 + kVAR2 = kVA2;
You can check your data for either metered feeder is consistent.

traderza said:
The two feeders will be supplying different combinations of inductive and resistive loads but i have no way of knowing the phase difference between the two.
That precludes capacitive loads, so it tells you kVAR is positive.

You can independently sum kW and kVAR since they are orthogonal.
kWt = kW1 + kW2;
kVARt = kVAR1 + kVAR2;
From that compute; kVAt = √( kWt2 + kVARt2 );
P.F. = cos(θ) = kWt / kVAt;
 
Baluncore said:
You have a right angle triangle. kW2 + kVAR2 = kVA2;
You can check your data for either metered feeder is consistent.That precludes capacitive loads, so it tells you kVAR is positive.

You can independently sum kW and kVAR since they are orthogonal.
kWt = kW1 + kW2;
kVARt = kVAR1 + kVAR2;
From that compute; kVAt = √( kWt2 + kVARt2 );
P.F. = cos(θ) = kWt / kVAt;
That's what I'm looking for! Many thanks!!
 

Similar threads

Replies
2
Views
1K
  • · Replies 17 ·
Replies
17
Views
6K
  • · Replies 8 ·
Replies
8
Views
2K
  • · Replies 35 ·
2
Replies
35
Views
9K
  • · Replies 5 ·
Replies
5
Views
2K
Replies
4
Views
3K
  • · Replies 22 ·
Replies
22
Views
10K
Replies
1
Views
2K
  • · Replies 22 ·
Replies
22
Views
3K
Replies
8
Views
2K