Electrical Consumption of Machine

Click For Summary

Discussion Overview

The discussion revolves around calculating the electrical consumption of an industrial parts washer, focusing on the machine's power usage in kilowatts (kW). Participants explore the necessary parameters, including voltage, current, and power factor, while addressing the complexities of measuring or estimating power factor in a three-phase system.

Discussion Character

  • Technical explanation
  • Mathematical reasoning
  • Debate/contested
  • Experimental/applied

Main Points Raised

  • One participant seeks to calculate the machine's power consumption using the formula kW = (Volts x Amps x Power Factor x Sqrt 3) / 1,000, but is uncertain about how to determine the power factor.
  • Another participant suggests estimating the power factor based on the load condition of the motor, indicating that if it is a 1/4 loaded motor, a power factor of 60% could be used.
  • Questions arise about how to measure the power factor with the available voltage and current readings, with suggestions to use a power meter or specific types of meters like a cos(φ)-meter.
  • Some participants discuss the implications of the machine's configuration, including whether it has variable frequency drives (VFDs) and the nature of the load (pumps, conveyor, electric heat).
  • There is a mention of the limitations of the tools available to the original poster, specifically that they cannot measure power factor directly with their multimeter and clamp meter.
  • Participants discuss the potential complexity of calculations given multiple motors and heating elements in the parts washer, suggesting that the original poster may need to measure amperage directly for more accurate results.
  • Suggestions are made for alternative methods to estimate power consumption, including monitoring the power meter over a period while running the machine.
  • One participant notes that if the parts washer has multiple motors, the calculations may become more complex, and they express a desire to find an industrial wattmeter for accurate measurement.

Areas of Agreement / Disagreement

Participants generally agree that measuring or estimating the power factor is crucial for accurate calculations, but there is no consensus on how to proceed without additional measurements or information about the machine's load characteristics. Multiple competing views on how to estimate or measure power factor remain unresolved.

Contextual Notes

Participants highlight the need for specific information about the machine's load and configuration to make accurate calculations. There are unresolved questions regarding the exact nature of the loads (resistive vs. inductive) and the potential impact of VFDs on power readings.

Who May Find This Useful

This discussion may be useful for electrical engineers, technicians, or anyone involved in industrial machinery operation and maintenance, particularly those interested in power consumption calculations and measurement techniques.

Berk
Messages
9
Reaction score
0
I need to know how much electricity a machine uses in kW please.

On the machine information plate it states: 460 volts, 60 Hz, 161 amps, and it is a 3 phase.

I took the readings for the volts and amps:
Phase 1- 271 volts & 37.68 Amps
Phase 2- 271 volts & 37.62 Amps
Phase 3- 273 volts & 38 Amps

I cannot figure out the Power Factor to apply to the formula I am using:
kW= (Volts x Amps x Power Factor x Sqrt 3) / 1,000

I know Power Factor = Real Power/ Apparent Power, however I cannot figure out the real power. I believe the apparent power is (460 x 161 x Sqrt 3) / 1,000 = 128.27 kVA?

Could I just average the voltage readings and then average the amperage readings for the 3 phases and then do (Avg volt x Avg amp x Sqrt 3) / 1,000 to get the true/real power without using the Power Factor?

Are my assumptions correct? Can someone please help me calculate the electrical consumption please! Thank you
 
Engineering news on Phys.org
Welcome to PF!

You're pretty close: you don't have a measurement of power factor, so the best you can do is estimate. If you describe the application, we can help with that. If this is a 1/4 loaded motor, I'd use 60%. Otherwise, your calculation is fine.
 
The machine in question is an industrial parts washer. How would I find out if it is a 1/4 loaded motor? When you say my calculation is fine, are you referring to using the nameplate amps x volts or the avg amps x avg volts readings that I got with the device?
 
Berk said:
Can someone please help me calculate the electrical consumption please! Thank you
I'm afraid not. You need to know or measure power factor.
 
How would I measure the power factor with the given information? Or do I need additional information? I have the voltage and amps for each phase and the kVA.
 
The readings you took are the actual load and they were about 1/4 of the nameplate. So that's the second calculation.

Also, when you say a parts washer, that makes the load pumps and a conveyor? Or is there electric heat as wel? And do any of the motors have VFDs?
 
Berk said:
How would I measure the power factor with the given information? Or do I need additional information? I have the voltage and amps for each phase and the kVA.
Measuring power factor is done with a power meter.
 
Berk said:
How would I measure the power factor with the given information? Or do I need additional information? I have the voltage and amps for each phase and the kVA.
You can measure/determine it with cos(φ)-meter or clamp on-power meter or any kind of wattmeter . To calculate/estimate it you should now what motor exactly you have. So, nothing about cos φn on the nameplate?
 
zoki85 said:
I'm afraid not. You need to know or measure power factor.
For most purposes you can estimate it close enough for a useful answer, though it does depend on the required precision.
 
  • #10
I do not know if the motor has VFDs, and the parts washer is basically a big conveyor belt system. I believe there is electric heat as well, not sure though.I cannot attach the manual because it is larger than 3 MB. I have 2 tools at my disposal, a Fluke 115 True RMS Multimeter & a Fluke 325 True RMS Clamp Meter. If you could please guide me through the steps needed to calculate the most accurate kW (true power) with the resources at my disposal, I will be eternally grateful. Thank you!
 
  • #11
russ_watters said:
For most purposes you can estimate it close enough for a useful answer, though it does depend on the required precision.
cos φ estimations get more shaky more you're off the nominal power of machines.
 
  • #12
Berk said:
I do not know if the motor has VFDs, and the parts washer is basically a big conveyor belt system. I believe there is electric heat as well, not sure though.I cannot attach the manual because it is larger than 3 MB. I have 2 tools at my disposal, a Fluke 115 True RMS Multimeter & a Fluke 325 True RMS Clamp Meter. If you could please guide me through the steps needed to calculate the most accurate kW (true power) with the resources at my disposal, I will be eternally grateful. Thank you!
With your equipment you can't measure or calculate power factor. You need a power meter and unfortunately, they aren't cheap:
http://www.fluke.com/fluke/m3en/solutions/pq/

To estimate the power factor, you need to know how much of the load is resistive (from the heaters) and how much is inductive (from the motors). You'll need amperage readings for each motor feed and the nameplate amperage of each motor.

If the pumps or motors change speed, they are probably on VFDs, but if they were, you'd probably also get true power readings from the VFDs, so I'm guessing they are not.
 
  • #13
zoki85 said:
cos φ estimations get more shaky more you're off the nominal power of machines.
Yes, but if he has a name brand motor with performance curves, he can get very close. If not...
[edit] oops...looks like it was worse than I remembered. Below 50% load, it starts getting pretty bad:

motor%20powerf_doe-med.jpg
 
  • #14
What is the cheapest Wattmeter I can buy that can be used on a 460 volt, 161 amp machine?
 
  • #16
Baldor JMM3713T 15HP 3450RPM 3PH 60HZ 215JM 3744M TEFC

https://www.mrosupply.com/motors/ac-motors/pump-motors/24080_jmm3713t_baldor-electric-motors/?gclid=CLyZpJuyrcICFVJhfgodTiYApw

This is the motor on the parts washer. What is the next step to figure out the kW (True Power)?
 
  • #17
Berk said:
Baldor JMM3713T 15HP 3450RPM 3PH 60HZ 215JM 3744M TEFC

https://www.mrosupply.com/motors/ac-motors/pump-motors/24080_jmm3713t_baldor-electric-motors/?gclid=CLyZpJuyrcICFVJhfgodTiYApw

This is the motor on the parts washer. What is the next step to figure out the kW (True Power)?
Performance graph (p6).
Line current drawn at 460 V (266V phase to neutral) → Power factor (cos φ).
This should give you a good estimate of a true electrical power of the motor since Pel= 460⋅I⋅√3 ⋅cos φ
 
  • #18
Berk said:
What is the cheapest Wattmeter I can buy that can be used on a 460 volt, 161 amp machine?
If you were able to switch off all but low-power machinery (and restrict the lighting) in the shop, and just run that motor alone at the intended loading, you might be able to see how much your workshop's power meter advances in 15 minutes of running, then x4 for the figure of actual power drawn. Depends on the meter―some of these electronic ones I think only the utility company can read.

It might be more practiceable to switch off everything else on just one of the phases, at least, to devote one phase's watthour meter to this motor exclusively, for 15 mins to do the test? (Monitor the 3 currents to confirm loading is balanced.)
 
Last edited:
  • #19
Berk said:
Baldor JMM3713T 15HP 3450RPM 3PH 60HZ 215JM 3744M TEFC

https://www.mrosupply.com/motors/ac-motors/pump-motors/24080_jmm3713t_baldor-electric-motors/?gclid=CLyZpJuyrcICFVJhfgodTiYApw

This is the motor on the parts washer. What is the next step to figure out the kW (True Power)?
Is that the only motor in the washer? Doesn't it have a water pump and a conveyor?

If it is the only motor, that motor is so small compared to your nameplate electrical capacity that you could probably ignore it and assume all of your electrical usage is the electric heat at a 100% power factor. I'd probably still measure its amperage directly though.
 
  • #20
Well there are 2 of those motors actually as well as a few heating elements (pads). I'm figuring that the calculations are going to be fairly complex, so I am trying to find someone who will lend me an industrial wattmeter.
 
  • #21
Depending on where you live, you may be able to "rent" a recorder from a local electrician. I work for an electrical contractor, and we have come in and set up a 3 phase recorder for 2 to 14 days and then downloaded the file and sent it to the customer. If you find someone locally that has one you may have to pay them for its use (do you have an electrician who takes care or your place?). With the file you can look at voltage per phase to neutral (min, max, avg, and inst), current per phase (min, max, avg and inst), power factor, and voltage phase to phase.
BTW the files can become very large. Once we left a recorder on a service for 14 days, and took a reading every second, and the file would have been >700 pages if printed out. Thank goodness for computers to analyze the info.

Bottom line - see if you can beg, borrow or rent one from a larger electrician locally.
 
Last edited:
  • #22
wirenut said:
Depending on where you live, you may be able to "rent" a recorder from a local electrician. I work for an electrical contractor, and we have come in and set up a 3 phase recorder for 2 to 14 days and then downloaded the file and sent it to the customer. If you find someone locally that has one you may have to pay them for its use (do you have an electrician who takes care or your place?). With the file you can look at voltage per phase to neutral (min, max, avg, and inst), current per phase (min, max, avg and inst), power factor, and voltage phase to phase.
BTW the files can become very large. Once we left a recorder on a service for 14 days, and took a reading every second, and the file would have been >700 pages if printed out. Thank goodness for computers to analyze the info.

Bottom line - see if you can beg, borrow or rent one from a larger electrician locally.
 
  • #23
Haha thanks for the information
 

Similar threads

  • · Replies 21 ·
Replies
21
Views
5K
  • · Replies 11 ·
Replies
11
Views
4K
  • · Replies 25 ·
Replies
25
Views
6K
  • · Replies 9 ·
Replies
9
Views
4K
  • · Replies 2 ·
Replies
2
Views
5K
  • · Replies 7 ·
Replies
7
Views
2K
  • · Replies 19 ·
Replies
19
Views
4K
  • · Replies 16 ·
Replies
16
Views
4K
Replies
9
Views
3K
Replies
0
Views
2K