Synchronous Generator Synch: Incoming Speed > Connected Generators

Click For Summary
SUMMARY

In the parallel operation of synchronous generators, the incoming generator must have a slightly higher speed than the connected generators to avoid phase differences upon synchronization. If both generators operate at the same speed, a phase difference occurs due to the electrical counter torque not matching the input mechanical torque, leading to reverse current flow and potential activation of the reverse power trip. The connected generator will slow down as it takes on load, while the already loaded generator will speed up, resulting in out-of-synchronization conditions.

PREREQUISITES
  • Synchronous generator operation principles
  • Understanding of electrical counter torque
  • Knowledge of load sharing in parallel generator systems
  • Familiarity with reverse power trip mechanisms
NEXT STEPS
  • Research synchronous generator synchronization techniques
  • Study the effects of load changes on generator performance
  • Learn about electrical counter torque calculations
  • Explore reverse power trip settings and configurations
USEFUL FOR

Electrical engineers, power system operators, and anyone involved in the operation and synchronization of synchronous generators will benefit from this discussion.

smruti
Messages
20
Reaction score
0
in a parallel operation of synchronous generators...while synchronising a new generator to a bus..why the speed of incoming generator should be slightly more than the other generators that are connected to the bus?
 
Engineering news on Phys.org
Because as soon as the generator is connected it will take some load and will try to slow down and the already loaded gen. will try to speed up. If both had the same intial speed this will result in a phase difference after connection. A reverse current will flow into the new gen. and activate the reverse power trip.
 
Rippetherocker said:
Because as soon as the generator is connected it will take some load and will try to slow down and the already loaded gen. will try to speed up. If both had the same intial speed this will result in a phase difference after connection. A reverse current will flow into the new gen. and activate the reverse power trip.
how it will cause phase difference when the speed will be same? can you please elaborate?
 
The speed will not be the same. When the generator is connected it will provide power to the system and the electrical counter torque on the shaft won't match the input mechanical torque. The machine will slow down. The other machine will speed up, since it takes less load now. With them running at different speeds they will be out of synch. That causes the phase difference. I didn't really add anything to the first response but I think he is pretty clear. Does it make sense?
 
  • Like
Likes   Reactions: Rippetherocker
FOIWATER said:
The speed will not be the same. When the generator is connected it will provide power to the system and the electrical counter torque on the shaft won't match the input mechanical torque. The machine will slow down. The other machine will speed up, since it takes less load now. With them running at different speeds they will be out of synch. That causes the phase difference. I didn't really add anything to the first response but I think he is pretty clear. Does it make sense?
thank you..
 

Similar threads

  • · Replies 37 ·
2
Replies
37
Views
7K
Replies
3
Views
2K
Replies
1
Views
3K
Replies
12
Views
2K
Replies
14
Views
3K
  • · Replies 2 ·
Replies
2
Views
4K
  • · Replies 46 ·
2
Replies
46
Views
6K
  • · Replies 4 ·
Replies
4
Views
3K
  • · Replies 5 ·
Replies
5
Views
2K
  • · Replies 10 ·
Replies
10
Views
2K