jim hardy said:That's an interesting feature of governors. Let me talk for a minute about the steam turbine i knew.
How the governor actually works is on the measured difference between measured speed and a reference speed.
The device that tells the valves how far open they should be is called "Speed Changer".
It has that name because it's used to roll the turbine from standstill to synchronous speed.
My turbine's synchronous speed was 1800 RPM.
To start it you might send it a reference speed of ten or twenty RPM. The steam valves would open slightly and it'd accelerate.
You'd send higher and higher reference speeds until it reached 1800 RPM.
Because there's no load on the generator it takes very little steam to roll the turbine and the valves are very nearly closed.
Next you synchronize the generator and connect it to the grid.
Now speed can no longer change because of the "infinite bus" concept.
So if you send it a reference speed of 1801 RPM the steam valves will open slightly .
But speed can't change so the extra thermal energy being carried in by steam goes out as electrical energy.
That's what turbine- generators do -
Mr Turbine turns thermal energy into mechanical energy
and
Mr Generator turns mechanical energy into electrical energy..
Recall the valves are positioned by difference between measured and reference speed.
So if you send it a higher reference speed it'll see more difference and open the valves further causing more kilowatts to flow out of Mr generator.
And that's how the "Speed Changer" becomes a "Load Changer". One device, two names.
What is the relation between speed error and valve position ?
Ours was 100% valve travel for 3% speed error.
So once you've synchronized and connected the generator to the grid , you send increasing reference speed and the valves open.
When reference speed reaches 103% of 1800 RPM, which is 1854 RPM, the valves will be fully open and you're making full power.
If grid should speed up , the speed error will get smaller and valves will close proportionally reaching full closed at 1854 RPM = 61.8 hz.
Now to your question
If a local speed measuring device is off by 1 RPM, it'll indicate 1799 or 1801 when the generator is at synchronous speed ready to synchronize.
>>>No matter, that's the reference speed you'd have to send it to achieve synchronous speed <<<< So it'll position the valves relative to synchronous speed.
Same applies to frequency.
But that's transparent because "Reference Speed" was an analog signal representing speed.
The analog signals for Reference and Measured speeds were hydraulic oil pressures internal to the speed/load changer, not electronic, and were displayed on pressure gauges indicating PSI.
There was an electronic RPM meter for the operators to watch while rolling the turbine up to speed ..
The "Speed Changer" knob doesn't mention RPM it just says "Raise" one way and "Lower" the other. You bump it and watch the RPM meter.
Final speed adjustments you made by watching the synchronizing lights.
After synchronizing you bump the same knob and watch the megawatt meter .
It's that simple.
Of course the governor is more complex than a simple proportional speed/load changer. It has rate of change pf speed compensation, automatic runbacks, and settable limits on valve opening.
I hope that plants the basic idea of a speed/load changer. Nowadays it'll be an electronic computer programmed to do pretty much the same thing.
I hope this isn't clutter. Should be more mathematical in a physics forum, but your question was "How does it work?"
Once you understand how the pieces work individually you can begin to work them connected in your thought experiments.
old jim
Thats cool, so basically absolute speed error is not a problem because you let the infinite bus guide the machine once its connected, then your load controller is just applying tor... ahem, power, by fluttering some valves to deliver more electric power.
I assume once the turbine is turning at the right speed, you bring up the field so you can see your AC output to synch, I'm assuming just set the field current to give you the right voltage before connecting?
So what is the control strategy for the field once connected? Is it essentially just compensating out resistance effects with load or is it more complicated?