The problems about power factor changed in RCL circuit, help~

In summary: But instead you are telling me that I need to find the reactance instead?I have suspicions about your value for the impedance. Since you know the real part R is 100 Ohms, you should be able to find the magnitude of the impedance given the power factor. You should also be able to find the magnitude of the reactive part. But instead you are telling me that I need to find the reactance instead?
  • #1
qpzm77gg
19
0
R = 100Ω, L=0.5H, supply voltage vs(t) = 12sin(377t) in Figure 1a

XL = wL =377(0.5) = 188.5Ω
vrms = 8.485∠0
Z=213.38∠62.05 Ω
I = 8.485∠0/ 213.38∠62.05 = 0.0398∠-62.05 A
VR = 3.98∠-62.05 V
VL = 7.502∠27.95 V
PT = 0.03982(100) = 0.158W
QT = QL = 0.299 VAR
ST = 0.338∠62.05 VA
Fp = 0.467a capacitor is added to the circuit in series in figure 1b, and Fp = 1
S=0.158∠0
Q=0
PT=0.0346W
I=0.0186A
Z=455.7Ω
C=14.1μF

If Fp in figure 1b is equal to 0.8
Q=0.02595VAR(ind)
I=0.0051∠36.87 A
Z=1662.82∠-36.87 Ω

For the capacitance of here, I'm so interrogative.

If I used the method of QT =QL - Qc
Qc = 0.0049-0.02595 = -0.02105VAR
Xc=809.3Ω
But I used the method of Vs=Vc+VR+VL
Vc = 8.485-0.0051(100)-0.0051(188.5)=7.01V
Xc=1374.5Ω

Why the answers are different when I used these two methods, and it's correct all of my above answers? If some are wrong, please feel free to indicated the mistake. The Figure 1a and 1b are uploaded the files.
Thanks
 

Attachments

  • 22.jpg
    22.jpg
    44.8 KB · Views: 463
  • 23.jpg
    23.jpg
    34.3 KB · Views: 471
Physics news on Phys.org
  • #2
Your calculations for the required capacitor in Figure (a) appear to be fine.

For Figure (b), what are the given component values and conditions? Are the voltage source, resistance, and inductance the same as before?
 
  • #3
gneill said:
Your calculations for the required capacitor in Figure (a) appear to be fine.

For Figure (b), what are the given component values and conditions? Are the voltage source, resistance, and inductance the same as before?


Yes, They are same as before, and then step and step add the capacitor in the circuit and change the power factor from 1 to 0.8.
Thanks
 
  • #4
qpzm77gg said:
Yes, They are same as before, and then step and step add the capacitor in the circuit and change the power factor from 1 to 0.8.
Thanks

Just to be clear, the components start out as Vs, R, L, and C from part (a) where the power factor is 1, and you wish to add another capacitor to bring the power factor down to 0.8?
 
  • #5
gneill said:
Just to be clear, the components start out as Vs, R, L, and C from part (a) where the power factor is 1, and you wish to add another capacitor to bring the power factor down to 0.8?

The complete question is uploaded in the file.
Thanks a lot.
 

Attachments

  • 26.jpg
    26.jpg
    24.8 KB · Views: 485
  • #6
Okay. Having the complete question helps.

For part (c)(iv), finding the capacitance, if you know the power factor and the resistance (the real part of the impedance), then you should be able to find the corresponding reactance. After all,
$$ pf = cos(\theta) = \frac{R}{\sqrt{R^2 + X^2}}$$
X will be positive or negative depending upon whether the current is said to be lagging or leading. You can then find XC from X = XL + XC.

I haven't been able to follow how you've approached parts (i) through (iii). I think if it were me I would have been tempted to do the parts in reverse order :smile:
 
  • #7
QT = QL-Qc
Because all I are same in the in series circuit.
XT=XL - Xc
QT/I2=188.5-Xc
Xc = 1186.19Ω

another method,
|Z|=1662.82
|Z|2 = R2+Xc22
1662.822 = 1002+Xc22
Xc2=1659.8Ω
QT=I2(1659.8)
QT=0.0432VAR(cap)
Qc=QL-QT
Qc=0.0049+0.0432=0.0481VAR(cap)
Xc=0.0481/0.00512=1849.3Ω


There are also difference between the answers, why?
 
  • #8
qpzm77gg said:
QT = QL-Qc
Because all I are same in the in series circuit.
XT=XL - Xc
QT/I2=188.5-Xc
Xc = 1186.19Ω
Is Q a positive or negative value if the pf is leading?
another method,
|Z|=1662.82
|Z|2 = R2+Xc22
1662.822 = 1002+Xc22
Xc2=1659.8Ω
QT=I2(1659.8)
QT=0.0432VAR(cap)
Qc=QL-QT
Qc=0.0049+0.0432=0.0481VAR(cap)
Xc=0.0481/0.00512=1849.3Ω


There are also difference between the answers, why?

I have suspicions about your value for the impedance. Since you know the real part R is 100 Ohms, you should be able to find the magnitude of the impedance given the power factor. You should also be able to find the magnitude of the reactive part.
 

1. What is power factor and how does it affect RCL circuits?

Power factor is a measure of how efficiently electrical power is being used in a circuit. In RCL circuits, the power factor is affected by the reactive components (inductors and capacitors) which can cause the current and voltage to be out of phase. This can result in a lower power factor, leading to inefficient use of power and potential problems in the circuit.

2. How does changing the power factor affect the performance of an RCL circuit?

Changing the power factor can have a significant impact on the performance of an RCL circuit. A lower power factor can result in higher energy losses, reduced efficiency, and potential overheating of components. This can lead to decreased reliability and potential damage to the circuit.

3. What are some common methods for correcting power factor in RCL circuits?

There are several methods for correcting power factor in RCL circuits. These include adding power factor correction capacitors, using active power factor correction circuits, and adjusting the phase angle between the voltage and current using a power factor correction controller.

4. How can I calculate the power factor in an RCL circuit?

The power factor in an RCL circuit can be calculated by dividing the real power (measured in watts) by the apparent power (measured in volt-amperes). This will give a value between 0 and 1, with a higher value indicating a more efficient use of power.

5. How can I troubleshoot power factor problems in RCL circuits?

If you are experiencing power factor problems in an RCL circuit, it is important to first identify the root cause. This can be done by measuring the power factor and determining if it is within an acceptable range. If not, further investigation may be needed to identify the specific components or factors causing the power factor issue. Professional help may be needed to properly troubleshoot and correct the problem.

Back
Top