Hi all

I'd like to heat up a mile of buried copper cable to roughly 100 deg C.

The centre core is 80mm dia solid copper with impregnated paper insulation.

Maximum spot temp is 150 deg C.

I can expose the core at each end and clamp on a heating element.

I've got plenty of time = weeks if required

Achievable??????
 

Answers and Replies

  • #2
FredGarvin
Science Advisor
5,067
10
You'll have to account for the heat transfer between the cable and the ground it is burried in. Obviously, if you had large enough heating elements/power supplies, then you could do it. You would probably have an easier time heating the cable up if you ran a current through it and let its internal resistance take care of the rest.
 
  • #3
3
0
I'm working on the decommissioning of the circuit at the moment.
Energising the cable in any way would not get approval, plenty of 415kv floating around!
 
  • #4
berkeman
Mentor
60,912
11,295
Hi all

I'd like to heat up a mile of buried copper cable to roughly 100 deg C.

The centre core is 80mm dia solid copper with impregnated paper insulation.

Maximum spot temp is 150 deg C.

I can expose the core at each end and clamp on a heating element.

I've got plenty of time = weeks if required

Achievable??????

Doesn't sound achievable to me. Simple enough to test. Do you have a shorter length of the cable? Even 25 meters should be enough. Bury, clamp and heat, and measure the temperture at the other end. Even after a long time, I'm guessing there will be a couple of degrees of temperature drop.

Before dismissing using a current to do the heating, have you calculated what the current and voltage would need to be?
 
  • #5
Mech_Engineer
Science Advisor
Gold Member
2,575
172
Hi all

I'd like to heat up a mile of buried copper cable to roughly 100 deg C.

The centre core is 80mm dia solid copper with impregnated paper insulation.

Maximum spot temp is 150 deg C.

I can expose the core at each end and clamp on a heating element.

I've got plenty of time = weeks if required

Achievable??????

It's not possible by heating the cable from each end, you would basically have to have a perfect thermal insulator surrounding it. To get a uniform 100C accross the entire length of the cable, you will need to pass a large amount of power (in the form of electrical current) through it and rely on resistive heating in the copper itself. It will take a very significant amount of power to heat a cable that long to 100C.

Clamping a heater on the cable every 10-20 feet or so might do it, but you'd need on the order of 250 heaters!
 
  • #6
4,662
6
Do you want to uniformly heat up the entire mile of underground cable? In this case, short one end and run enough current through the other end (either ac or dc) to produce about 10 watts per meter power loss. 80 mm is a large diameter. What is this, a 14.4 KV power transmission line? What is its amp rating (buried cable)?
Bob S.
 
  • #7
berkeman
Mentor
60,912
11,295
Hi all

I'd like to heat up a mile of buried copper cable to roughly 100 deg C.

The centre core is 80mm dia solid copper with impregnated paper insulation.

Maximum spot temp is 150 deg C.

I can expose the core at each end and clamp on a heating element.

I've got plenty of time = weeks if required

Achievable??????

I guess we should have asked this at the start, but why do you want to run this experiment? What is the overall goal?
 
  • #8
berkeman
Mentor
60,912
11,295
(just realized that an EIR is probably required for this experiment. How many years do you have before you need results?)
 
  • #9
mgb_phys
Science Advisor
Homework Helper
7,819
14
It's a common way of finding an intermittent fault in a buried power cable if resistance/reflectivity measurements don't work.
We had one on site - they shorted the cable at the distribution board, brought in a huge generator truck and put large voltages onto it until there was a blast of steam from the ground.
 
  • #10
berkeman
Mentor
60,912
11,295
It's a common way of finding an intermittent fault in a buried power cable if resistance/reflectivity measurements don't work.
We had one on site - they shorted the cable at the distribution board, brought in a huge generator truck and put large voltages onto it until there was a blast of steam from the ground.

Oh crap, Occam's razor. If you just need to detect a fault, there are MUCH lower power and safer ways to do that. Say Cable Tester. Lordy.
 
  • #11
3
0
We are doing some R&D, looking at the removal of the oil remaining entrained within the paper insulation following flushing.

I'm looking at a hybrid of thermal desorbtion and air stripping, hence the heat requirement.

The heat would also aid the flushing process but then would only need 60-70 deg C.
 
  • #12
mgb_phys
Science Advisor
Homework Helper
7,819
14
Oh crap, Occam's razor. If you just need to detect a fault, there are MUCH lower power and safer ways to do that. Say Cable Tester. Lordy.

That's what I would have thought, I'm guessing the fault had enough conductance to not show on a resistivity test and the cable was old and damaged enough that a reflectivity test showed breaks everywhere.
 

Related Threads on Thermal Conductivity in a Copper Cable

  • Last Post
Replies
5
Views
8K
  • Last Post
Replies
4
Views
563
  • Last Post
Replies
3
Views
5K
  • Last Post
Replies
12
Views
1K
Replies
3
Views
1K
Replies
1
Views
3K
Replies
1
Views
563
Replies
3
Views
3K
  • Last Post
Replies
2
Views
4K
Top