The discussion revolves around calculating the efficiency of a 500W transformer that steps down voltage from 230V to 24V, considering winding resistances and core losses. The participant initially calculates copper losses and total losses, arriving at an efficiency of 99.07%. However, confusion arises regarding the input and output power relationship, as the 500W rating refers to output power, not input. Clarification is provided that the input power must account for losses, leading to a revised calculation of input power as 504.668W. The conversation emphasizes the importance of understanding transformer efficiency in relation to input and output power dynamics.
MathsDude69
Messages
25
Reaction score
0
Hey. I am currently doing a bit of revision for an exam and I am struggling on the following question:

Calculate the efficiency of a 500W transformer, which reduces the 230 AC voltage to 24 V. For the calculations, assume the resistances of the primary and secondary windings as 0.05 Ohm and 0.01 Ohm, respectively. The losses in the transformer core Pc = 70mW.

I understand the whole voltage/current/power/impedance ratio stuff, but can't seem to find any information on calculating efficiencies using the resistances or the transformer core losses. Any Suggestions?
 
Engineering news on Phys.org
Hey. I've found a bit more information regarding copper losses in transformers. It states:

Copper Loss = Ip2Rp + Is2Rs

I would think given the question that the asnwer would be:

P = VI ∴ I = P/V

For the primary:
500/230 = 2.27 Amps

For the secondary:
500/24 = 20.83 Amps

Copper loss for primary:
2.272 x 0.05 = 0.258 W

Copper loss for secondary:
20.832 x 0.01 = 4.34 W

Total Copper Loss:
0.258 + 4.34 = 4.598 W

Total loss including core loss:

4.598 + 0.07 = 4.668 W

Total efficiency =
(500-4.668)/500 = 0.9907 = 99.07% efficient.

The problem with this is if we were only getting an efficiency of 99.07% the secondary wouldn't be developing 20.83 Amps! Does anyone know how to actually solve this question?
 
@ Maths:
I skimmed through this pretty fast but I would say that you should not have 500 watts for both the primary and secondary. With any efficiency of less than 100% you will naturally get you a lower secondary current than 20.83.
 
You are nearly there except for the last bit.

The 500W refers to the output not the input for transformers so

input power = output power + total losses = 500 + 4.668 = 504.668.

efficiency = 1 - losses/input power = 1 - 4.668/504.668 = 99.07% expressed as a percentage.
 
See this is where I am getting confused. If the input power is 504.668W instead of 500W wouldn't that make the current and thus the losses higher on the primary winding??
 
More power is lost, but more is put in too. The percentage of loss should be the same.
 
Thread 'I thought it was only Amazon that sold unsafe junk'
I grabbed an under cabinet LED light today at a big box store. Nothing special. 18 inches in length and made to plug several lights together. Here is a pic of the power cord: The drawing on the box led me to believe that it would accept a standard IEC cord which surprised me. But it's a variation of it. I didn't try it, but I would assume you could plug a standard IEC cord into this and have a double male cord AKA suicide cord. And to boot, it's likely going to reverse the hot and...

Similar threads

  • · Replies 8 ·
Replies
8
Views
3K
  • · Replies 9 ·
Replies
9
Views
3K
Replies
10
Views
3K
Replies
2
Views
2K
Replies
8
Views
2K
  • · Replies 8 ·
Replies
8
Views
2K
  • · Replies 14 ·
Replies
14
Views
3K
  • · Replies 4 ·
Replies
4
Views
3K
  • · Replies 5 ·
Replies
5
Views
3K
  • · Replies 4 ·
Replies
4
Views
3K