Transformer Impedance Discussion

Click For Summary
SUMMARY

The discussion centers on calculating the short circuit current rating of a 120V panel fed from a 7.5 kVA transformer, resulting in a calculated short circuit current of approximately 2083.3 Amps based on a 3% impedance of 0.03. Participants clarify that the impedance can be expressed as R + jX, where R is the resistance and X is the reactance, and that the 3% impedance indicates the maximum allowable voltage drop under full load conditions. The calculations involve using complex impedance and per-unit systems to derive accurate short circuit current values.

PREREQUISITES
  • Understanding of transformer ratings and specifications
  • Knowledge of complex impedance (R + jX) in AC circuits
  • Familiarity with per-unit system calculations
  • Basic electrical engineering principles, including Ohm's Law and power calculations
NEXT STEPS
  • Study transformer impedance calculations and their implications on short circuit ratings
  • Learn about per-unit system analysis in electrical engineering
  • Explore the relationship between voltage drop and transformer efficiency
  • Investigate the effects of reactance in AC circuits and its impact on power delivery
USEFUL FOR

Electrical engineers, power system designers, and technicians involved in transformer applications and short circuit analysis will benefit from this discussion.

psparky
Science Advisor
Gold Member
Messages
884
Reaction score
31
I was working on trying to find the short circuit current rating of a 120 volt panel fed from a 7.5KVA transformer.

Using P=IV you get 7.5KVA=120 * I

I = 62.5 Amps.

Then I believe you divide that current by the impedance of the transformer. .03 is the impedance in this case in the transformer specs. So I do the math and I get about 2,000 amp short circuit rating.

Great. My question is this. If impedance is R + JX, how does .03 relate to that?

Is it possible the R+jx add up to be .03? Or is that nonsense? I believe they even state the .03 as 3% as well.
 
Last edited:
Engineering news on Phys.org
Ok, I am not an expert in electronics but if you have a circuit with impedances then its automatically an alternating current circuit. In this case I am only able to use complex way to calculate. (Z_complex * I_complex = V_complex)
You have apparent power and therefore effective/active power and reactive power.
There has to be a cos(phi) in your calculation of power. active power should be defined as P=V*I*cos(phi)
You can't easily divide P by U for the current.
U is the source voltage, but there is also R, and X (capacity or inductivity)
that means you have dropout voltages on R and X (Vr and Vx)
Also impedances generally have units, it's Ohm
 
Sparky - I believe you are getting to the right answer.

I was taught a simpler method
Your 3% impedance is probably per-unit

so 1 per unit volts / 0.03 per unit impedance = 33.3 per unit amps
and your per-unit amperage is 62.5 .

62.5 amps X 33.3 = 2081 amps into a zero impedance fault, about what you got

(That's why your household 15 amp breakers say something preposterous on the back like 10,000 amps - don't [STRIKE]use[/STRIKE] attempt to use one downstream from a source capable of more fault current than that .)

i've not seen it broken down into R and X for small transformers.

Clearly the impedance of interconnecting wires and of the circuit breaker itself aid in limiting fault current.

old jim
 
Interesting approach Jim.

I'm still looking for the relation of R+ jx to the transformer impedence (.03)

I will hit up my old electronics mentor from college. I have yet to stump him.
 
120V, 7.5kVA; I = 62.5A
R load = V / I = 1.92 ohm

I believe the 3% is the maximum percentage of voltage drop to be lost in the transformer secondary and circuit under full load conditions.
3% of 1.92 ohm = 0.0576 ohm transformer secondary resistance.
Short circuit current will be V / R = 120 / 0.0576 = 2083.3A

If you know the current rating of the panel, you do not need to know the line voltage.
Short circuit current will be 63A * 100% / 3% = 2100.A
 
If we’ll represent the current flowing through transformer in complex:
I=I*[cos(fi)-j*sin(fi)] and [neglecting the magnetic circuit of Xm and Rfe] the transformer impedance will be: Z=R1+R’2+j*(X1+X’2) where R1= primary winding resistance R’2=secondary winding resistance referred to primary and X1=leakage magnetic flux reactance of primary winding X’2=secondary winding leakage reactance referred to primary.
Then we may take R1+R’2=R and X1+X’2=X and Z=R+j*X.
abs(I*Z)[complex]=abs(I*[cos(fi)-j*sin(fi)]*(R+j*X)
I*Z=I*{[R*cos(fi)+X*sin(fi)]+j*[X*cos(fi)-R*sin(fi)]}
abs(I*Z)=I*SQRT{[R*cos(fi)+X*sin(fi)]^2+[X*cos(fi)-R*sin(fi)]^2}=I*SQRT(R^2+X^2)
abs(I*Z)[complex]=abs(I)*abs(Z)=V1-V’2 [Voltage dip-or voltage sag- through transformer.
This voltage dip -if the current will be Irated- it is the short-circuit voltage[vk] and it is represented in p.u.-vk%=vk/Vrated*100.
Z=vk%*Vrated/Irated for single-phase [or two-phase] system and Z=vk%*Vrated/sqrt(3)/Irated.
By multiplying [and dividing] by Vrated Z=vk%*Vrated^2/Srated where S=SQRT(3)*Vrated*Irated [the apparent rated power of the transformer].
 
Correction:
Z=vk%/100*Vrated/Irated for single-phase [or two-phase] system and Z=vk%/100*Vrated/sqrt(3)/Irated for three-phase system.
By multiplying [and dividing] by Vrated Z=vk%/100*Vrated^2/Srated.
Ik1=Vrated/Z or Ik3=Vrated/Z/sqrt(3).By substituting Z=vk%/100*Vrated/Irated
Ik1=Irated*100/vk% or Ik3=Irated*100/vk% as Baluncore already said.
 
I believe the 3% is the maximum percentage of voltage drop to be lost in the transformer secondary and circuit under full load conditions.
3% of 1.92 ohm = 0.0576 ohm transformer secondary resistance.
Short circuit current will be V / R = 120 / 0.0576 = 2083.3A

Secondary? or both windings, ie lumped ?

One per unit load gives voltage drop numerically equal to per unit Z, without having to worry about turns ratios .
Handy, eh? That's why there's 'per unit' .
 
Of course, if you will consider a Zbase=Vrated^2/Srated then vk=Z/Zbase[p.u.] or vk%=Z/Zbase*100
 
  • #10
Babadag said:
If we’ll represent the current flowing through transformer in complex:
I=I*[cos(fi)-j*sin(fi)] and [neglecting the magnetic circuit of Xm and Rfe] the transformer impedance will be: Z=R1+R’2+j*(X1+X’2) where R1= primary winding resistance R’2=secondary winding resistance referred to primary and X1=leakage magnetic flux reactance of primary winding X’2=secondary winding leakage reactance referred to primary.
Then we may take R1+R’2=R and X1+X’2=X and Z=R+j*X.
abs(I*Z)[complex]=abs(I*[cos(fi)-j*sin(fi)]*(R+j*X)
I*Z=I*{[R*cos(fi)+X*sin(fi)]+j*[X*cos(fi)-R*sin(fi)]}
abs(I*Z)=I*SQRT{[R*cos(fi)+X*sin(fi)]^2+[X*cos(fi)-R*sin(fi)]^2}=I*SQRT(R^2+X^2)
abs(I*Z)[complex]=abs(I)*abs(Z)=V1-V’2 [Voltage dip-or voltage sag- through transformer.
This voltage dip -if the current will be Irated- it is the short-circuit voltage[vk] and it is represented in p.u.-vk%=vk/Vrated*100.
Z=vk%*Vrated/Irated for single-phase [or two-phase] system and Z=vk%*Vrated/sqrt(3)/Irated.
By multiplying [and dividing] by Vrated Z=vk%*Vrated^2/Srated where S=SQRT(3)*Vrated*Irated [the apparent rated power of the transformer].

Interesting stuff. Wish I had the brains to understand it.
 
  • #11
Baluncore said:
120V, 7.5kVA; I = 62.5A
R load = V / I = 1.92 ohm

I believe the 3% is the maximum percentage of voltage drop to be lost in the transformer secondary and circuit under full load conditions.
3% of 1.92 ohm = 0.0576 ohm transformer secondary resistance.
Short circuit current will be V / R = 120 / 0.0576 = 2083.3A

If you know the current rating of the panel, you do not need to know the line voltage.
Short circuit current will be 63A * 100% / 3% = 2100.A

Gotcha, thanks.
 

Similar threads

  • · Replies 8 ·
Replies
8
Views
3K
  • · Replies 8 ·
Replies
8
Views
2K
  • · Replies 3 ·
Replies
3
Views
2K
  • · Replies 21 ·
Replies
21
Views
2K
  • · Replies 14 ·
Replies
14
Views
3K
Replies
6
Views
4K
  • · Replies 5 ·
Replies
5
Views
6K
  • · Replies 8 ·
Replies
8
Views
3K
  • · Replies 15 ·
Replies
15
Views
5K
  • · Replies 23 ·
Replies
23
Views
4K