Unbalanced Phase Currents in 3~ Motor

Click For Summary
SUMMARY

The discussion centers on diagnosing unbalanced phase currents in a 3-phase induction motor, where two phases exhibited currents nearly twice the normal value. Prolonged operation may have weakened insulation, leading to shorted windings, rather than increased resistance causing higher currents. Miswiring and incorrect tap connections were also suggested as potential causes. Accurate measurement of stator winding resistance and phase currents is essential for troubleshooting this issue.

PREREQUISITES
  • Understanding of 3-phase induction motor operation
  • Knowledge of electrical resistance measurement techniques
  • Familiarity with motor wiring configurations and tap diagrams
  • Experience with troubleshooting electrical faults in motors
NEXT STEPS
  • Learn how to measure stator winding resistance accurately
  • Research the effects of insulation degradation on motor performance
  • Study the implications of miswiring in 3-phase motors
  • Explore troubleshooting methods for unbalanced phase currents in induction motors
USEFUL FOR

Electrical engineers, motor technicians, and maintenance personnel involved in the operation and troubleshooting of 3-phase induction motors will benefit from this discussion.

QwertyXP
Messages
66
Reaction score
0
A 3-phase induction motor in our factory had unequal phase currents. One of the currents was nearly normal while the other two were about twice the usual value. Somebody said that prolonged running causes increase in resistance of stator winding, and this results in increased current. But this explanation appears wrong at the very outset, because increased resistance should actually decrease the current.

What might the reason be?
 
Engineering news on Phys.org
Was this taken out of service and re-installed at any time?
Was it running ok and then a problem developed?
My first thought was that a winding was connected backwards, but that would only happen if the connections were removed and no markings existed on them.
The explanation you got should affect all 3 currents, not just 2.
You could also have 2 shorted windings, only a very sensitive meter will tell you that, or a very complex troubleshooting routine. Do all your windings have the same resistance (within 5-10%)?
Are any shorted to ground (motor housing)?
 
  • Like
Likes   Reactions: 1 person
A 3-phase induction motor in our factory had unequal phase currents. One of the currents was nearly normal while the other two were about twice the usual value.

I'm guessing from your use of past tense that it burnt up ?

If so, wirennut is probably right.
 
Our electrical workshop received a complaint that the motor's overload relay was tripping (motor didn't burn up though). Upon inspection, the electrician discovered that two of the phases had higher currents. I'm assuming that currents were normal when the motor was installed because electricians are required to measure them after installation. I didn't get the chance to make any measurements myself, but I was just wondering what the cause might be. I guess measuring the stator winding resistance should have given me the clue.

So a possible conclusion is that prolonged running actually decreased the resistance by weakening the insulation and thus shorting the windings. Increase in winding resistance can never increase the current. Does this look like a valid explanation?
 
My personal feeling is that it was mis-wired, as wirenut suggested.

Of course only the electricians who investigated know for sure.
 
  • Like
Likes   Reactions: 1 person
Many 3~ motors have multiple taps and you can actually change the operating voltage (and consequently the current) by connecting the appropriate leads together. I was giving a print with a tap diagram once and was asked to wire a motor for a certain voltage. They gave me the wrong print. Luckily I'm mechanically savvy and I know what a motor should sound like. I ran it for a second and realized that it was wrong. A little research later and I found the right print.

Does your building have one or more wild legs? Some services purposely have a higher voltage in one or more legs. It's a terrible idea but they do it for flourescent lighting. When you use the higher leg for flourescent lights they draw less current and then you can have more lights on one breaker circuit. If your building is fairly new you probably won't see this.
 
  • Like
Likes   Reactions: 1 person
When running in delta configuration, misplaced tap link or a shorted turn in one winding will cause a higher current in the two phases that drive that winding.
 
  • Like
Likes   Reactions: 1 person

Similar threads

Replies
4
Views
3K
Replies
9
Views
2K
  • · Replies 7 ·
Replies
7
Views
2K
Replies
2
Views
4K
  • · Replies 2 ·
Replies
2
Views
1K
Replies
7
Views
3K
  • · Replies 20 ·
Replies
20
Views
3K
  • · Replies 5 ·
Replies
5
Views
2K
  • · Replies 14 ·
Replies
14
Views
4K
  • · Replies 11 ·
Replies
11
Views
3K