Understanding AS2067 Earthing Requirements: A Closer Look at Figure B5 and B4

  • Thread starter Thread starter victorgoh1981
  • Start date Start date
Click For Summary

Discussion Overview

The discussion centers on the earthing requirements specified in AS2067, particularly focusing on the implications of Figures B5 and B4 regarding the connection of Earth cables from a high voltage (HV) substation to a remote transformer. Participants explore the necessity of this connection given the distance between the two locations and the potential risks associated with Earth Potential Rise (EPR) during faults.

Discussion Character

  • Technical explanation
  • Debate/contested

Main Points Raised

  • One participant questions the need for connecting Earth cables between a distant HV substation and a remote transformer, suggesting that the potential equalization may not be necessary due to the distance.
  • Another participant proposes that the assumption about distance being a factor may be incorrect, indicating that earthing may only be required when the substation and transformer are co-located.
  • A participant references the Australian Standard and its basis on IEC 61936, mentioning measures to avoid transferred potential between high and low voltage systems.
  • One participant discusses the effects of grounding the shield of a medium voltage cable at one end versus both ends, suggesting that grounding at both ends could mitigate potential risks.

Areas of Agreement / Disagreement

Participants express differing views on the necessity and implications of earthing connections between the HV substation and the remote transformer. There is no consensus on whether the distance negates the need for such connections or if other factors must be considered.

Contextual Notes

Some participants note limitations in accessing the full text of the Australian Standard due to paywalls, which may affect their ability to fully evaluate the requirements and implications discussed.

victorgoh1981
Messages
1
Reaction score
0
I have a question about the earthing requirement in AS2067. Figure B5 and B4 show that the Earth cables from the HV substation should connect to the Earth bar of the remote transformer. Since the HV substation is far away from the remote transformer, we do not need to equalize the potential. why do we need to connect the Earth between them? The Earth conductor could transfer the EPR (Earth Potential Rise) from the HV substation to the transformer location in the event of an Earth fault. That could create a dangerous situation for the people near to transformer. Could anyone help me to answer this question? Thanks
 
Engineering news on Phys.org
What country are you in? What is your interest in this question? Are you studying to take an advancde electrician certification exam?
 
He's talking about Australian Standard® Substations and high voltage installations exceeding 1 kV a.c. , https://www.saiglobal.com/PDFTemp/Previews/OSH/AS/AS2000/2000/2067-2008.pdf

But the majority of the document is behind a paywall.

1644590974034.png
 
Last edited:
  • Informative
Likes   Reactions: berkeman
victorgoh1981 said:
... Since the HV substation is far away from the remote transformer, ...
Maybe that is a false assumption.
The earthing may be required only when they are co-located.
With the paywall it is difficult to examine the exact text.
 
I have not a copy of this Australian Standard but as it noted in the Preface it is based on IEC 61936 which is included now in EN 50522/2010.

In this standard at item 6 Measure to avoid transferred potential you may know how to proceed to avoid potential transfer from high to low voltage system or to communication.
 
  • Informative
Likes   Reactions: Tom.G
From the attached sketch you can see that if the shield of the medium voltage cable is grounded [earthed] only at one end at the ungrounded end the potential will be A, but if it grounded at both ends the potential will be B. We can do so that B could be less than maximum permissible.
 

Attachments

  • Potential transferred from Substation.jpg
    Potential transferred from Substation.jpg
    38.7 KB · Views: 179

Similar threads

Replies
15
Views
2K
  • · Replies 10 ·
Replies
10
Views
3K
  • · Replies 19 ·
Replies
19
Views
3K
  • · Replies 13 ·
Replies
13
Views
4K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 11 ·
Replies
11
Views
4K
  • · Replies 8 ·
Replies
8
Views
6K
  • · Replies 9 ·
Replies
9
Views
11K
  • · Replies 21 ·
Replies
21
Views
7K
  • · Replies 4 ·
Replies
4
Views
3K