You need more than one data point for the pump. Typically you have a 'pump curve' which shows the head at various flowrates. As the flowrate is decreased towards zero, the head will rise to the 'shutoff head', and as flow is increased the head will drop off. Then you can plot the pump curve along with the system resistance curve (basically bernoulli solved for head loss). Where the two curves cross, that's the operating point.
Above describes the situation for a centrifugal pump. If you have a positive displacement pump, the flowrate is constant; all you need is bernoulli. But I don't think you have a PD pump, because then the 'at 30 meters head' doesn't make sense.