Understanding Reactive Power Flow in Power Factor Correction

AI Thread Summary
Connecting a capacitor across an inductive load facilitates reactive power (Q) flow between the capacitor and inductor, reducing the generator's need to supply Q. The capacitor does not supply Q to the generator when an inductive load is present because the reactive power primarily circulates between the capacitor and inductor. The generator provides leading reactive power to the capacitor and lagging reactive power to the inductive load, resulting in a cancellation effect. Consequently, the generator supplies less reactive power than it would if only the inductive load were connected. This interaction highlights the importance of power factor correction in electrical systems.
QwertyXP
Messages
66
Reaction score
0
When you connect a capacitor across an inductive load, reactive power (Q) flows back and forth between capacitor and inductor, so (ideally) the generator doesn't need to supply Q to the load.

My question is, why doesn't the capacitor supply Q to the generator as well? If only a capacitor were connected across a generator, Q would flow from capacitor->generator and vice versa. But when an inductive load is also connected in parallel, Q flows only b/w cap. and ind. and does not go towards the generator. Why is this so?
 
Engineering news on Phys.org
The generator supplies the capacitor with reactive power (leading), and it supplies the inductive load with lagging reactive power. There is some cancelling of the leading with the lagging, so the generator ends up supplying less reactive power than when supplying the inductive load alone.
 
  • Like
Likes 1 person
Got it, thank you.
 
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...