VFD harmonics effects on generator set

Click For Summary

Discussion Overview

The discussion revolves around the use of Variable Frequency Drives (VFDs) in conjunction with generator sets for driving motors ranging from 0.4 kW to 15 kW. Participants explore the implications of harmonics on generator sizing and performance, particularly in relation to starting currents and power factor considerations.

Discussion Character

  • Exploratory
  • Technical explanation
  • Debate/contested

Main Points Raised

  • One participant suggests that using a VFD could reduce the generator footprint while driving a 20 hp motor, but expresses concern about how to account for harmonics in the system.
  • Another participant questions whether the VFD is being used to drive the generator or if the generator is powering the motor, indicating a need for clarification on the setup.
  • Some participants mention the potential for a power factor control circuit on the VFD input, which could influence generator performance.
  • A participant notes that the VFD has a 6 pulse rectifier input circuit, which may affect harmonics and generator sizing.
  • Concerns are raised about the high starting current of the motor and the implications for generator sizing, with one participant advocating for the use of a VFD to mitigate this issue.
  • Another participant suggests that if high starting torque is not required, a soft-starter could be a more cost-effective solution compared to a VFD.

Areas of Agreement / Disagreement

Participants express differing views on the necessity of using a VFD versus a soft-starter, and there is no consensus on the best approach to account for harmonics in the generator sizing process.

Contextual Notes

Participants have not fully resolved the implications of harmonics on generator performance, nor have they reached a definitive conclusion about the optimal configuration for the motor and generator setup.

Tawanda
Messages
5
Reaction score
0
I would like to use VFDs for motor sizes ranging from 0.4kw to 15kw. My idea here is to reduce the generator foot print to the lowest possible value. My thinking is that, theoretically, I could use a 25kva generator set to drive a 20hp motor (80% operating capacity) and since the VFD eliminates the high starting current I should be okay. But my biggest concern is: how do I account for harmonics in this system. What harmonic factor can I use to correctly size the generator. Is there a filter solution for sizes 0.4kw to 15kw used in a similar set up as above.
 
Engineering news on Phys.org
Tawanda said:
I would like to use VFDs for motor sizes ranging from 0.4kw to 15kw. My idea here is to reduce the generator foot print to the lowest possible value. My thinking is that, theoretically, I could use a 25kva generator set to drive a 20hp motor (80% operating capacity) and since the VFD eliminates the high starting current I should be okay. But my biggest concern is: how do I account for harmonics in this system. What harmonic factor can I use to correctly size the generator. Is there a filter solution for sizes 0.4kw to 15kw used in a similar set up as above.
Welcome to PF.

So you are using a VFD to drive a generator? Are you using this as a motor-generator setup to change AC Mains voltages/frequencies? What are the input and output frequencies? And why would the input AC Mains harmonics generated by driving the VFD affect the AC Mains output voltage waveform?
 
berkeman said:
So you are using a VFD to drive a generator?
Or using a generator to drive an electric motor, and think a VFD for soft-start might make it easier for the generator.
That will depend on the VFD input circuit and control.
I expect there will be a power factor control circuit on the VFD input.
 
Baluncore said:
Or using a generator to drive an electric motor, and think a VFD for soft-start might make it easier for the generator.
Hmm, interesing. Yeah, which drives which...? Guess we need the OP to return to give us more information.
 
berkeman said:
Welcome to PF.

So you are using a VFD to drive a generator? Are you using this as a motor-generator setup to change AC Mains voltages/frequencies? What are the input and output frequencies? And why would the input AC Mains harmonics generated by driving the VFD affect the AC Mains output voltage waveform?
I'm using the generator as the power source to run a 20hp motor and I am thinking the VFD could help to suppress the high starting current whilst still giving high starting torque. The idea is to use the smallest generator possible for the 20hp motor whilst leaving a 20% capacity headroom.
 
Baluncore said:
Or using a generator to drive an electric motor, and think a VFD for soft-start might make it easier for the generator.
That will depend on the VFD input circuit and control.
I expect there will be a power factor control circuit on the VFD input.
That's right. The idea is to make the motor starting easier on the generator. But I'm worried about the effects of harmonics on the genset if I were to size the generator to run at 80% of it's full load capacity. The VFD has a 6 pulse rectifier input circuit.
 
Tawanda said:
The VFD has a 6 pulse rectifier input circuit.
Do you know that the 3PH VFD has a simple 6 diode full-wave rectifier to the capacitor bank?
An expensive VFD might have input power factor control circuits.

Is your motor connected as Y or ∇ ?
Maybe a star to delta starter would be sufficient.
 
  • Like
Likes   Reactions: Averagesupernova
Baluncore said:
Do you know that the 3PH VFD has a simple 6 diode full-wave rectifier to the capacitor bank?
An expensive VFD might have input power factor control circuits.

Is your motor connected as Y or ∇ ?
Maybe a star to delta starter would be sufficient.
The motor is delta connected
 
Baluncore said:
Do you know that the 3PH VFD has a simple 6 diode full-wave rectifier to the capacitor bank?
An expensive VFD might have input power factor control circuits.

Is your motor connected as Y or ∇ ?
Maybe a star to delta starter would be sufficient.

Tawanda said:
The motor is delta connected

In fact the motor has all six leads coming out so I can connect in the star or delta configuration. Problem with a starter - delta starter is that that starting current would still be very high still requiring an overly sized genset to allow for starting. That's why I was thinking along the lines of a VFD.
 
Last edited by a moderator:
  • #10
If you really need high starting torque (I don't know anything about your load), a VFD is a good choice. If your load doesn't need high starting torque (many loads don't), a soft-starter is typically a lot cheaper and will provide the same benefit to the generator.
 
  • Like
Likes   Reactions: Tawanda

Similar threads

Replies
7
Views
3K
  • · Replies 4 ·
Replies
4
Views
2K
  • · Replies 1 ·
Replies
1
Views
3K
  • · Replies 7 ·
Replies
7
Views
4K
  • · Replies 74 ·
3
Replies
74
Views
9K
  • · Replies 7 ·
Replies
7
Views
4K
  • · Replies 4 ·
Replies
4
Views
3K
  • · Replies 39 ·
2
Replies
39
Views
4K
Replies
8
Views
2K
  • · Replies 1 ·
Replies
1
Views
3K