VFD harmonics effects on generator set

Click For Summary
SUMMARY

The discussion focuses on the use of Variable Frequency Drives (VFDs) to manage motor sizes ranging from 0.4 kW to 15 kW while minimizing generator footprint. The user proposes using a 25 kVA generator to drive a 20 hp motor at 80% capacity, leveraging the VFD to mitigate high starting currents. Key concerns include accounting for harmonics in the system and the appropriate harmonic factor for generator sizing. The conversation highlights the importance of understanding the VFD's input circuit and power factor control to optimize performance.

PREREQUISITES
  • Understanding of Variable Frequency Drives (VFDs) and their operation
  • Knowledge of generator sizing and capacity management
  • Familiarity with harmonic distortion and its effects on electrical systems
  • Basic electrical engineering concepts, including motor configurations (Y and Δ)
NEXT STEPS
  • Research harmonic distortion mitigation techniques for VFD applications
  • Learn about generator sizing principles for variable load applications
  • Explore the differences between VFDs and soft starters for motor control
  • Investigate power factor correction methods for VFD systems
USEFUL FOR

Electrical engineers, power system designers, and technicians involved in motor control and generator sizing, particularly those working with VFD applications in industrial settings.

Tawanda
Messages
5
Reaction score
0
I would like to use VFDs for motor sizes ranging from 0.4kw to 15kw. My idea here is to reduce the generator foot print to the lowest possible value. My thinking is that, theoretically, I could use a 25kva generator set to drive a 20hp motor (80% operating capacity) and since the VFD eliminates the high starting current I should be okay. But my biggest concern is: how do I account for harmonics in this system. What harmonic factor can I use to correctly size the generator. Is there a filter solution for sizes 0.4kw to 15kw used in a similar set up as above.
 
Engineering news on Phys.org
Tawanda said:
I would like to use VFDs for motor sizes ranging from 0.4kw to 15kw. My idea here is to reduce the generator foot print to the lowest possible value. My thinking is that, theoretically, I could use a 25kva generator set to drive a 20hp motor (80% operating capacity) and since the VFD eliminates the high starting current I should be okay. But my biggest concern is: how do I account for harmonics in this system. What harmonic factor can I use to correctly size the generator. Is there a filter solution for sizes 0.4kw to 15kw used in a similar set up as above.
Welcome to PF.

So you are using a VFD to drive a generator? Are you using this as a motor-generator setup to change AC Mains voltages/frequencies? What are the input and output frequencies? And why would the input AC Mains harmonics generated by driving the VFD affect the AC Mains output voltage waveform?
 
berkeman said:
So you are using a VFD to drive a generator?
Or using a generator to drive an electric motor, and think a VFD for soft-start might make it easier for the generator.
That will depend on the VFD input circuit and control.
I expect there will be a power factor control circuit on the VFD input.
 
Baluncore said:
Or using a generator to drive an electric motor, and think a VFD for soft-start might make it easier for the generator.
Hmm, interesing. Yeah, which drives which...? Guess we need the OP to return to give us more information.
 
berkeman said:
Welcome to PF.

So you are using a VFD to drive a generator? Are you using this as a motor-generator setup to change AC Mains voltages/frequencies? What are the input and output frequencies? And why would the input AC Mains harmonics generated by driving the VFD affect the AC Mains output voltage waveform?
I'm using the generator as the power source to run a 20hp motor and I am thinking the VFD could help to suppress the high starting current whilst still giving high starting torque. The idea is to use the smallest generator possible for the 20hp motor whilst leaving a 20% capacity headroom.
 
Baluncore said:
Or using a generator to drive an electric motor, and think a VFD for soft-start might make it easier for the generator.
That will depend on the VFD input circuit and control.
I expect there will be a power factor control circuit on the VFD input.
That's right. The idea is to make the motor starting easier on the generator. But I'm worried about the effects of harmonics on the genset if I were to size the generator to run at 80% of it's full load capacity. The VFD has a 6 pulse rectifier input circuit.
 
Tawanda said:
The VFD has a 6 pulse rectifier input circuit.
Do you know that the 3PH VFD has a simple 6 diode full-wave rectifier to the capacitor bank?
An expensive VFD might have input power factor control circuits.

Is your motor connected as Y or ∇ ?
Maybe a star to delta starter would be sufficient.
 
  • Like
Likes   Reactions: Averagesupernova
Baluncore said:
Do you know that the 3PH VFD has a simple 6 diode full-wave rectifier to the capacitor bank?
An expensive VFD might have input power factor control circuits.

Is your motor connected as Y or ∇ ?
Maybe a star to delta starter would be sufficient.
The motor is delta connected
 
Baluncore said:
Do you know that the 3PH VFD has a simple 6 diode full-wave rectifier to the capacitor bank?
An expensive VFD might have input power factor control circuits.

Is your motor connected as Y or ∇ ?
Maybe a star to delta starter would be sufficient.

Tawanda said:
The motor is delta connected

In fact the motor has all six leads coming out so I can connect in the star or delta configuration. Problem with a starter - delta starter is that that starting current would still be very high still requiring an overly sized genset to allow for starting. That's why I was thinking along the lines of a VFD.
 
Last edited by a moderator:
  • #10
If you really need high starting torque (I don't know anything about your load), a VFD is a good choice. If your load doesn't need high starting torque (many loads don't), a soft-starter is typically a lot cheaper and will provide the same benefit to the generator.
 
  • Like
Likes   Reactions: Tawanda

Similar threads

Replies
7
Views
3K
  • · Replies 4 ·
Replies
4
Views
2K
  • · Replies 1 ·
Replies
1
Views
3K
  • · Replies 7 ·
Replies
7
Views
4K
  • · Replies 74 ·
3
Replies
74
Views
9K
  • · Replies 7 ·
Replies
7
Views
4K
  • · Replies 4 ·
Replies
4
Views
3K
  • · Replies 39 ·
2
Replies
39
Views
4K
Replies
8
Views
2K
  • · Replies 1 ·
Replies
1
Views
3K