What are the effects of boiling in a heat exchanger?

Click For Summary
SUMMARY

The discussion centers on the implications of boiling in a heat exchanger using water as a coolant, particularly at high temperatures around 900°F. The participants highlight that boiling will lead to steam formation, which can result in sudden pressure increases and potential loss of coolant if backpressure is not managed. The system is identified as an open system, where the coolant is discarded, and the need for increased coolant flow rate is emphasized to prevent boiling and maintain effective cooling. The conversation also touches on the future use of combustible gas as a coolant, indicating a shift in operational strategy.

PREREQUISITES
  • Understanding of heat exchanger design principles
  • Knowledge of fluid dynamics, particularly in open systems
  • Familiarity with boiling point dynamics and phase changes in fluids
  • Experience with pressure management in thermal systems
NEXT STEPS
  • Research the Leidenfrost effect and its implications in heat transfer systems
  • Learn about managing backpressure in heat exchangers
  • Explore alternative coolants and their thermal properties
  • Investigate the design considerations for using combustible gases in heat exchangers
USEFUL FOR

Engineers and designers involved in thermal system design, particularly those working with heat exchangers and coolant management in high-temperature applications.

TheHypnotoad
Messages
2
Reaction score
0
I'm working on a heat exchanger design, with water as the coolant. I'm running an analysis on this thing, and it looks like it's going to get hot. Like, 900F hot. So, of course this is going to be steam by the time it reaches the outlet. I'm really not a fluids kind of girl, but it's on me to tell the experimental engineer whether this test is going to end in tears, and if it's going to be a problem, I want to try to talk him into using a different coolant.

So, my question for forum! What happens to a heat exchanger when boiling occurs in the coolant flow? Should I be expecting sudden pressure increases? Losses in the maximum mass flow rate? Exploding heat exchangers?

Some more information:
-Fluid enters at around 200psi
-Coolant is not immediately vented at the outlet, but enters a manifold and is piped a few feet off to be vented

Thanks for your input!
 
Engineering news on Phys.org
Welcome to PF

Sounds like you are saying this is an open system - the coolant gets discarded? The pressure in the system will be very low since it is open, and any backpressure will be due to dynamic effects (the steam rushing out at probably supersonic speed) unless there are valves or other devices to create backpressure.

What you're describing is a boiler - turning water into steam is the main function. But whether you want steam or not depends on what the coolant is meant to do after it leaves the boiler. If you don't want steam, you'll need to increase the coolant flow rate until it can remove the heat without boiling.

Seems like an odd way to run a heat exchanger, but without knowing more details it is tough to know why you are doing this.
 
russ_watters said:
Welcome to PF

Sounds like you are saying this is an open system - the coolant gets discarded? The pressure in the system will be very low since it is open, and any backpressure will be due to dynamic effects (the steam rushing out at probably supersonic speed) unless there are valves or other devices to create backpressure.

What you're describing is a boiler - turning water into steam is the main function. But whether you want steam or not depends on what the coolant is meant to do after it leaves the boiler. If you don't want steam, you'll need to increase the coolant flow rate until it can remove the heat without boiling.

Seems like an odd way to run a heat exchanger, but without knowing more details it is tough to know why you are doing this.

Thanks for the response, Russ! You're right, it's an odd way to run a real heat exchanger . . . in reality, it's going to be an active cooling system. Eventually, they'll run the system with a combustible gas as the coolant, and they'll burn the gas to heat the panel. But for an initial test, they wanted to run something less combustible, like water. So yes, it's a bit of an odd setup to start out.

So it sounds like all that will happen here is as the water boils, the steam will rush out and I will be left with no coolant, unless a back pressure is applied, right? You asked if this was a boiler, but really, the point is to keep the thing under a certain temperature, and if I have no coolant, that's not going to fly. Sounds like the test engineer and I have some talking to do. . . .

And thanks for the welcome :) looks like a neat little forum around here :approve:
 
You might have troubles with the Leidenfront effect, take it into consideration.
 

Similar threads

  • · Replies 3 ·
Replies
3
Views
3K
  • · Replies 4 ·
Replies
4
Views
3K
Replies
1
Views
2K
  • · Replies 1 ·
Replies
1
Views
2K
Replies
22
Views
4K
Replies
11
Views
2K
  • · Replies 3 ·
Replies
3
Views
3K
  • · Replies 5 ·
Replies
5
Views
2K
  • · Replies 6 ·
Replies
6
Views
14K
  • · Replies 2 ·
Replies
2
Views
2K