What is the Recommended Ventilation Rate for a Brewery?

  • Thread starter Thread starter newyorkdesign
  • Start date Start date
  • Tags Tags
    Rate Ventilation
Click For Summary

Discussion Overview

The discussion revolves around determining the recommended ventilation rate for a brewery, particularly focusing on managing carbon dioxide levels during the fermentation process. Participants explore various methods for calculating air changes and the implications of CO2 exposure for workers in the brewery environment.

Discussion Character

  • Exploratory
  • Technical explanation
  • Debate/contested
  • Mathematical reasoning

Main Points Raised

  • One participant seeks advice on the recommended air changes needed to manage CO2 levels during fermentation, expressing concern for worker safety.
  • Another participant references exposure limits for CO2, suggesting that ventilation should keep levels below 5000 ppm for safety and ideally below 1000 ppm for comfort.
  • ASHRAE standards are mentioned, indicating a target of 1000 ppm for indoor spaces, prompting questions about how to achieve this in exhaust design.
  • A participant proposes a mathematical model to calculate CO2 levels based on yeast production and air exchange rates, emphasizing the need to keep CO2 levels below 1000 ppm.
  • One participant provides a specific figure of 456.3587 pounds of CO2 released per day, asking for help in determining the necessary air changes per hour.
  • Another participant questions the logic of releasing CO2 into the brewery atmosphere and suggests that direct venting from fermentation vats might be more efficient.
  • A later reply supports the idea of direct venting, arguing that it would reduce the need for extensive ventilation systems and prevent CO2 accumulation.
  • Concerns are raised about the precision of the CO2 release figure and its implications for ventilation calculations.

Areas of Agreement / Disagreement

Participants express differing views on the best approach to managing CO2 levels, with some advocating for direct venting from fermentation vats while others focus on calculating air changes based on CO2 production. There is no consensus on a single recommended ventilation rate or method.

Contextual Notes

Participants reference various standards and calculations, but the discussion includes assumptions about CO2 production rates, air density, and the effectiveness of different ventilation strategies, which remain unresolved.

newyorkdesign
Messages
3
Reaction score
0
Hi All, I'm designing an exhaust system in brewery. Does anyone know the recommended air changes (ventilation rate)? My concern is the elevated level of carbon dioxide during the fermentation process. I'm planing on exhausting the air thru sidewall propeller fans and make-up the air thru roof mounted gas heated make up air fan. Please Advice.
Thanks
 
Engineering news on Phys.org
Hi
For the US
http://www.lni.wa.gov/WISHA/Rules/AirborneContam/default.htm
and clicking on Scope and then in table 3 for carbon cioxide
one obtains 5000ppm exposure limit

Also same site but another page
http://www.lni.wa.gov/Safety/Topics/AtoZ/Ventilation/default.asp

So you have to ventilate to keep the CO2 level below that number if employees are in the area.
 
Last edited by a moderator:
ASHRAE has a standard of 1,000 ppm CO2 for indoor spaces. how do i keep it down in my exhaust design
 
Well yes. Anything above 5000ppm and a person can suffer oxygen deprivation or other toxic effects with extended exposure. Below 1000ppm is the comfort zone so that headache, nausea, drowsiness do not occur for most people. That is the difference.

If you have people in the workspace continiously then use the Ashrae figure.
 
I am not a brewery guy nor an air ppm concentration guy but here goes as to what I think.

First thing you should do is determine the rate of CO2 production by the the yeast is the vat, say cubic meters per hour.
Let that rate be Xyeast.

You are exiting nXout; where Xout is the amount of CO2 in the room air per cubic meter, and n is the number of cubic meters per hour exiting.
Input air is similar nXin; here Xin is the amount of CO2 in the incoming air per cubic meter, and n is the amount of air entering in cubic meters per hour.
The room has Xroom amount of CO2 per cubic meter.

You want to keep Xroom below that related to the 1000ppm.
And at steady state, Xroom = Xout.

Xroom = Xroom - nXout + nXin + Xyeast

That gives you a general idea of what is going on with the ventillation.
( Of course , the voume of incoming air is less than the outgoing air due to the gas production by the yeast, so in reality nin < nout )

If you fiddle around with that and tidy it up somewhat making sure I did not forget or misrepresent any items, then you can relate that to the desired ppm. Perhaps through some iterations you can obtain an air change. One would think though there should be a standarized method to obtain air changes if one knows the rate of production of a gas source which the fermentation process is.
 
456.3587 Total pounds of CO2 released per day at full capacity. please help how many Air changer per hour required to be exhausted.
 
newyorkdesign said:
456.3587 Total pounds of CO2 released per day at full capacity. please help how many Air changer per hour required to be exhausted.

A a very high precision you have with 456.3587 pounds of CO2. Let's just round that up to say an easier figure like 460 pounds or 220 kgs. How you came to a value is pounds would be interesting to know.

So, calculate the volume of air at 1000ppm CO2 content contains 220kg or 360pounds of carbon dioxide. Ventilating that much air would be a suitable figure to work with to size your fan(s).
 
A dumb question: why would you want to release 200 kg of CO2 per day into the atmosphere of the brewery, and then remove it by changing the air?

Wouldn't it be better to vent the CO2 from the fermentation vat directly outside the building? Or is this an "artisan" type of microbrewery that is using open fermentation vats (with the disadvantages of contamination from airborne material, though some people prefer them for top-fermenting yeasts) rather than closed vats?
 
AlephZero said:
A dumb question: why would you want to release 200 kg of CO2 per day into the atmosphere of the brewery, and then remove it by changing the air?

Wouldn't it be better to vent the CO2 from the fermentation vat directly outside the building? Or is this an "artisan" type of microbrewery that is using open fermentation vats (with the disadvantages of contamination from airborne material, though some people prefer them for top-fermenting yeasts) rather than closed vats?

Not a dumb question.
The brewery is most likely operating with venting from the vat directly to the atmosphere. That would be the most sensible way to do it. Venting into the inner space would require a larger ventillation system, and pockets of CO2 could be trapped in certain areas unless adequate air circulation was guaranteed, and also temperature control of the vat and inner space would be problematic.

My thought process was to calculate the maximum ventillation required IF the CO2 was vented into the building and then scale that back to perhaps 1% to 2% ( assuming anything more than that and his system is not well contained, though the operator would have to use a percentage value better to his liking and experience ). Comparing that value to the size of building and the volume of air within, the brewery operator could obtain a reasonable air exchange value.

With 220kg of CO2 released per day from the vat, a 1% seepage would mean a 2.2kg of C02 collection into the inner area. With a nominal air density of 1kg/cubic meter, outside air containing 400ppm C02, a thorough mixing with (approximate) 4400 cubic meters of outside air per day should suffice to obtain the desired 1000ppm of C02 within the inner space.

Though I do hesitate(d) for the brewery operator to to actually use that figure as being totally reliable, since first hand site observation from a professional in his area should provide a better assurance that other extraneous factors are taken into account.
 
  • #10
256bits said:
A a very high precision you have with 456.3587 pounds of CO2. Let's just round that up to say an easier figure like 460 pounds or 220 kgs. How you came to a value is pounds would be interesting to know.

So, calculate the volume of air at 1000ppm CO2 content contains 220kg or 360pounds of carbon dioxide. Ventilating that much air would be a suitable figure to work with to size your fan(s).
that should have read:
Ventilating that much air would be a suitable figure to work with to size your fan(s) if you consider a seepage value into the inner work space.
which still does not make sense.
 

Similar threads

  • · Replies 15 ·
Replies
15
Views
4K
  • · Replies 7 ·
Replies
7
Views
2K
  • · Replies 10 ·
Replies
10
Views
2K
  • · Replies 3 ·
Replies
3
Views
4K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 10 ·
Replies
10
Views
3K
Replies
4
Views
6K
  • · Replies 19 ·
Replies
19
Views
10K
  • · Replies 3 ·
Replies
3
Views
3K
  • · Replies 7 ·
Replies
7
Views
2K