What Set Temperature Achieves 900C Without Controller Offset?

  • Thread starter Thread starter kamran_chemist
  • Start date Start date
  • Tags Tags
    Temperature
Join the discussion
Ask a follow-up here, or get your own question answered by working scientists, mathematicians and engineers — people, not an autocomplete.
Real named experts · corrections over time · the nuance an AI answer skips
3 replies · 1K views
kamran_chemist
Messages
2
Reaction score
0
How to incorporate deviation -9.2C in furnace, while its measured temperature is 909.2C and Display temperature is 900. if there is no option of offset in controller. What will be the set temperature to achieve 900C.
 
Physics news on Phys.org
Welcome to PF.

Can you post datasheets for the oven and controller? Do you have the Owners Manual and Service Manual for both? If so, there is probably some calibration procedure listed.

Also, what other temperature measuring device are you using to sense the "measured temperature"? Are you sure it is accurate?
 
Reply
  • Like
Likes   Reactions: DeBangis21 and Lord Jestocost
Dear berkeman,

Find attachment for reference.
CALIBRATION.jpeg
 
Last edited by a moderator:
kamran_chemist said:
How to incorporate deviation -9.2C in furnace, while its measured temperature is 909.2C and Display temperature is 900. if there is no option of offset in controller. What will be the set temperature to achieve 900C.
This seems too simple, I must not understand something.

You have a thermometer you trust. You can't calibrate your controller. So, why don't you be the controller. Do some experiments and make a lookup table. Ask for the temperature that corresponds with the behavior you want.

PS: If you choose to have a lottery, I've got dibs on 890.8C.
 
Reply
  • Like
  • Haha
Likes   Reactions: Tom.G and russ_watters