The calculated section modulus for a wooden beam does not align with standard wood design tables due to incorrect consideration of the tributary area. The beam spans 24 feet with a tributary area of 10.5 feet, leading to a total load of 210 psf. The moment calculation yields 158,760 lb-ft, and the section modulus is computed as S = M/Fb = (158,760 lb-ft * 12 inches) / 1775 psi. The highest standard value from the wood beam sizing chart is 874 in³, indicating a discrepancy that arises from the misinterpretation of tributary area versus tributary width.

PREREQUISITES
  • Understanding of beam loading and support conditions
  • Knowledge of section modulus calculations
  • Familiarity with wood design tables and properties
  • Basic principles of structural engineering mechanics
NEXT STEPS
  • Review the calculation of tributary area versus tributary width in beam design
  • Study the use of wood design tables for different beam sizes and loads
  • Learn about the implications of dead load and live load on beam sizing
  • Explore advanced structural analysis techniques for moment and section modulus calculations
USEFUL FOR

Structural engineers, architects, and construction professionals involved in wood framing and beam sizing will benefit from this discussion.

erinrcollins
Messages
1
Reaction score
0
The Section modulus of a beam that I compute does not match wood design tables to determine the correct size of the wood framing member. Can anyone offer some insight?

I have to size a wooden beam. The span is 24 feet with a tributary area of 10.5 feet. The dead load value is 85psf, the live load value is 125 psf, for a total value of 210psf. I was given an Fb value of 1775. It is a simple beam equally supported on both ends.

First I calculated the weight for the total load: (10.5 ft)(210) = 2205 lbs/sf

I calculated the Moment for the total load -- wL^2 / 8 = ((2205lb/ft )(24^2))/8 = 158,760 psf
Then I calculated the section modulus S=M/Fb = (158,760 lbft (12 inches)) / 1775

I am looking at a chart of wood beam sizing entitled Section Properties of Standard Dressed Sawn Lumber but the S value on the chart highest value is 874 in^3.

Am I correct in assuming you have to take into account the tributary area to determine the Moment? If I leave the tributary area out and just use the deal/live load of 210, I calculate a 4x14 beam. But I can't imagine that that is correct.

Thanks!
 
Physics news on Phys.org
In the first place, how would you know if your answer was about right, or not? What would be the argument for leaving out the tributary area (or width, as I would prefer you called it?). In other words, are you thinking? I am confused by your sloppy presentation. Tributary "area" should be presumably tributary "width" with the units you have given it. You should always state your units, including for Fb. Your units for moment perhaps should be those of force x distance.
 

Similar threads

Replies
33
Views
6K
  • · Replies 1 ·
Replies
1
Views
2K
Replies
3
Views
4K
Replies
48
Views
19K
  • · Replies 10 ·
Replies
10
Views
61K
  • · Replies 3 ·
Replies
3
Views
7K
  • · Replies 12 ·
Replies
12
Views
41K
  • · Replies 7 ·
Replies
7
Views
6K
Replies
1
Views
8K
Replies
6
Views
5K