The discussion focuses on calculating the torque for a starter generator (СГ-18-1С) rated at 18 kW and operating between 3600 to 6200 RPM. Initial calculations suggest a torque of approximately 48 Nm at 4000 RPM, but further analysis indicates a maximum applied shaft torque of 125 Nm is possible. The calculations confirm that the output power translates to around 24.13 HP, leading to a torque of about 43 Nm at 4000 RPM when considering efficiency losses. The generator is designed for starting diesel engines and supplying electric energy, with a maximum current of 800 amps. Accurate torque calculations are crucial for selecting an appropriate motor for the application.
royalbas001
Messages
1
Reaction score
0
TL;DR Summary
Torque calculation of СГ-18-1С
Hi
I want to design a test rig for starter generator ( СГ-18-1С ). The output of the starter generator is 28V, 18KW @ rpm 3600 - 6200. The output will be regulated through excitation winding current.

I want to choose a motor to run the stater generator. Please tell me, How to calculate the torque of the starter generator.

I calculated as Torque = Power x 60 / 2 x Pi x rpm, results a ~48Nm torque at 4000 rpm. Is it correct or need to consider the excitation winding current? Please suggest. I want to choose the motor using V- belt pully drive with step up.

Thank you
 
Engineering news on Phys.org
1 HP = 746 Watts
18KW / 746

18 000/746 = 24.13 HP

HP x 5252 /rpm = Torque (Ft.Lbs.)
24.13 x 5252 / 4000 = 31.68 FtLbs

1FtLb = 1.356 Nm
31.68 x 1.356≅ 43Nm

That assumes 100% efficiency in the starter and the belts, which of course will not happen.

Cheers,
Tom
 
  • Like
Likes Ivan Nikiforov
Welcome to PF.

The SG-18-1S starter/generator is a Russian built direct current machine of mixed excitation, with air cooling by a built-in fan, designed for starting of diesel engines, supplying electric energy, and recharging batteries.

Specified as 18 kW.
Generator maximum current: 800 amp continuous. ( Vmax of 22.5 volt ).
Maximum applied shaft torque = 125 N∙m.
Maximum speed 7000 RPM.

To generate the maximum output will require an engine rating of 18 kW.
18 kW is equivalent to 24 HP.

4000 RPM * 0.10472 = 418.9 radian/sec.
18 kW / 418.9 = 43.0 N∙m.
My numbers agree with Tom.G

For 18 kW output, shaft torque will be;
@ 3600 RPM, 48. N∙m
@ 4000 RPM, 43. N∙m
@ 4400 RPM, 39. N∙m
@ 5200 RPM, 33. N∙m
@ 6000 RPM, 29. N∙m
 
  • Like
Likes Ivan Nikiforov
How did you find PF?: Via Google search Hi, I have a vessel I 3D printed to investigate single bubble rise. The vessel has a 4 mm gap separated by acrylic panels. This is essentially my viewing chamber where I can record the bubble motion. The vessel is open to atmosphere. The bubble generation mechanism is composed of a syringe pump and glass capillary tube (Internal Diameter of 0.45 mm). I connect a 1/4” air line hose from the syringe to the capillary The bubble is formed at the tip...
Thread 'What type of toilet do I have?'
I was enrolled in an online plumbing course at Stratford University. My plumbing textbook lists four types of residential toilets: 1# upflush toilets 2# pressure assisted toilets 3# gravity-fed, rim jet toilets and 4# gravity-fed, siphon-jet toilets. I know my toilet is not an upflush toilet because my toilet is not below the sewage line, and my toilet does not have a grinder and a pump next to it to propel waste upwards. I am about 99% sure that my toilet is not a pressure assisted...
After over 25 years of engineering, designing and analyzing bolted joints, I just learned this little fact. According to ASME B1.2, Gages and Gaging for Unified Inch Screw Threads: "The no-go gage should not pass over more than three complete turns when inserted into the internal thread of the product. " 3 turns seems like way to much. I have some really critical nuts that are of standard geometry (5/8"-11 UNC 3B) and have about 4.5 threads when you account for the chamfers on either...
Back
Top