Heat transfer between water tank and pipe system

AI Thread Summary
The discussion focuses on calculating the water circulation rate and the duration that an ice melting pool can support an air-conditioning system using fan coil units. The user seeks to determine the optimal flow rate to ensure effective heat transfer without compromising the cooling capacity of the office. Calculations suggest a flow rate of approximately 1.2 m³/h per coil, with the ice melting pool potentially supporting the system for about 20 hours under ideal conditions. Concerns are raised about the measured water temperature of 3-5°C, which may indicate mixing with hot water, and the need for a sufficient volume of ice to maintain cooling. The overall consensus emphasizes the importance of a larger ice storage capacity for effective HVAC performance.
Leo Lee
Messages
4
Reaction score
0
Hello All,
I have a question for heat exchange calculation and hope someone can help. I would like to recover the "cooling energy" from a ice melting pool for air-conditioning for a small office. I plan to install three fan coil units with 800CFM for the office with closed loop water pipe to circulate water from fan coil units to the cooling coil immersed in the ice melting water tank and then back to fan coil units. Hence, heat from the office will transfer to the ice melting water.
Ice melting tank effective size : 4m x 2.2m x 1m(H)
Ice melting water temperature : 3 ~ 5*C as measured
Cooling coil : OD : 9.52mm OD; Length : 32.4m ; Material : copper
Fan coil unit : each cooling capacity 7.92kW (assume water in at 7*C and leave at 12.5*C)
What is the water circulating flow rate for the above system ?
How long will the ice water support for the system (as the water temperature will rise up) ? Ice will be refilled for every 2 to 3 hours and cannot support air-conditioning at 7*C.
Any assumption can be made. I only need rough estimation for reference. I have a normal air-conditioning system for the office as backup. This project is for environmental education purpose. Thanks !
 
Anyone can help ?
 
Hello Leo, :welcome:

It is a bit unclear how we can help here. Are you asking simple things, like
Leo Lee said:
What is the water circulating flow rate for the above system ?
with as a naive answer$$ {dQ\over dt} = \rho \,c_p \, \Delta T\, F_v \quad \Rightarrow \quad F_v = { 7.92\; kJ/s \over 1000 \; kg/m^3 \ 4.2 \;kJ/(kg\cdot \mathstrut^\circ\! C) \ 5.5 ^\circ \!C} \ \ ? $$So some 1.2 m3/h per coil.

Similarly for the melting rate of ice:
Leo Lee said:
How long will the ice water support the system
$$

{dM\over dt} = {dQ\over dt} \Delta H_f \quad \Rightarrow \quad T = \rho \ V \ \Delta H_f {dQ\over dt} = {593\; kg/m^3 \ 8.8 \;m^3 \ 334\; kJ/kg \over 7.92\; kJ/s}$$or some 20 hours if all three are at full capacity (and the ice tank is perfectly isolated :rolleyes: (*) )

(## \; 593\; kg/m^3\ ## is the density of dry crushed ice)But there are some things in your account I can't follow: ice in contact with water should yield a temperature of ##0 \; ^\circ \!C\ ##, so how come you measure 3 - 5 ? And use 7 degrees for the coil input ?

How did you determine the length of your cooling coil ? Isn't it a design parameter to be established ? You have ##\displaystyle {dQ\over dt} = U\; A\; \Delta T## with ##A## the contact area and ##U## the over-all heat transfer coefficient (which you probably don't know yet).
 
BvU said:
Hello Leo, :welcome:

It is a bit unclear how we can help here. Are you asking simple things, like
with as a naive answer$$ {dQ\over dt} = \rho \,c_p \, \Delta T\, F_v \quad \Rightarrow \quad F_v = { 7.92\; kJ/s \over 1000 \; kg/m^3 \ 4.2 \;kJ/(kg\cdot \mathstrut^\circ\! C) \ 5.5 ^\circ \!C} \ \ ? $$So some 1.2 m3/h per coil.

Similarly for the melting rate of ice:
$$

{dM\over dt} = {dQ\over dt} \Delta H_f \quad \Rightarrow \quad T = \rho \ V \ \Delta H_f {dQ\over dt} = {593\; kg/m^3 \ 8.8 \;m^3 \ 334\; kJ/kg \over 7.92\; kJ/s}$$or some 20 hours if all three are at full capacity (and the ice tank is perfectly isolated :rolleyes: (*) )

(## \; 593\; kg/m^3\ ## is the density of dry crushed ice)But there are some things in your account I can't follow: ice in contact with water should yield a temperature of ##0 \; ^\circ \!C\ ##, so how come you measure 3 - 5 ? And use 7 degrees for the coil input ?

How did you determine the length of your cooling coil ? Isn't it a design parameter to be established ? You have ##\displaystyle {dQ\over dt} = U\; A\; \Delta T## with ##A## the contact area and ##U## the over-all heat transfer coefficient (which you probably don't know yet).

Thanks for your reply. Sorry for confusion in my question. I would like to determine the water circulation rate inside the pipe system. That is critical to determine the water temperature entering and leaving the ice melting pool, as well as entering and leaving fan coil units. If water circulation rate is too fast, there will be no sufficient time for heat transfer to the ice melting pool. If it is too slow, the fan coil unit will not have sufficient water flow to remove heat from the office. How can I determine a suitable water circulation rate ?

I measured the water temperature at the ice melting pool by infrared temperature measurement sensor and the reading is 3~5 degree. Is it not suitable for the measurement? On the other hand, the pool has hot water supply for ice melting. I am not sure any hot water mixed in the pool before my measurement.

Regarding the cooling coil length, I will use an abandoned 1600 CFM fan coil unit's coil and the measured length is 32.4m.

I don't know the U-value of the cooling coil in the ice melting pool, any ball-part figure can be used ?

Thank you very much.

Best Regards

Leo
 
Hello, anyone can help ? Thanks.
 
Leo Lee said:
Thanks for your reply. Sorry for confusion in my question. I would like to determine the water circulation rate inside the pipe system. That is critical to determine the water temperature entering and leaving the ice melting pool, as well as entering and leaving fan coil units. If water circulation rate is too fast, there will be no sufficient time for heat transfer to the ice melting pool. If it is too slow, the fan coil unit will not have sufficient water flow to remove heat from the office. How can I determine a suitable water circulation rate ?
Since you specified an inlet and outlet temperature and power, that leads directly to only one possible water circulation rate, as calculated by @BvU
I measured the water temperature at the ice melting pool by infrared temperature measurement sensor and the reading is 3~5 degree. Is it not suitable for the measurement?
It is a bit surprising, but I suppose it is possible in a dynamic situation.
Regarding the cooling coil length, I will use an abandoned 1600 CFM fan coil unit's coil and the measured length is 32.4m.

I don't know the U-value of the cooling coil in the ice melting pool, any ball-part figure can be used ?
Since this is real-world, that makes life easier. You can calculate it based on the actual testing you've done, but I don't think I would bother. With a 3-5C melting pool temperature and 7C supply to the FCU, I'd say your main problem is too small of a tank and/or not enough ice. Ice storage can be a useful solution to some HVAC problems, but as you are finding out, you need a lot of ice. In the USA, we have a unit of refrigeration called a "ton", which refers to the melting of a US ton (900 kg) of ice in 24 hours. Each of your FCUs has a capacity of 2 tons.
 
  • Like
Likes Vedward
How did you find PF?: Via Google search Hi, I have a vessel I 3D printed to investigate single bubble rise. The vessel has a 4 mm gap separated by acrylic panels. This is essentially my viewing chamber where I can record the bubble motion. The vessel is open to atmosphere. The bubble generation mechanism is composed of a syringe pump and glass capillary tube (Internal Diameter of 0.45 mm). I connect a 1/4” air line hose from the syringe to the capillary The bubble is formed at the tip...
Thread 'What type of toilet do I have?'
I was enrolled in an online plumbing course at Stratford University. My plumbing textbook lists four types of residential toilets: 1# upflush toilets 2# pressure assisted toilets 3# gravity-fed, rim jet toilets and 4# gravity-fed, siphon-jet toilets. I know my toilet is not an upflush toilet because my toilet is not below the sewage line, and my toilet does not have a grinder and a pump next to it to propel waste upwards. I am about 99% sure that my toilet is not a pressure assisted...
After over 25 years of engineering, designing and analyzing bolted joints, I just learned this little fact. According to ASME B1.2, Gages and Gaging for Unified Inch Screw Threads: "The no-go gage should not pass over more than three complete turns when inserted into the internal thread of the product. " 3 turns seems like way to much. I have some really critical nuts that are of standard geometry (5/8"-11 UNC 3B) and have about 4.5 threads when you account for the chamfers on either...